I bid a service swap recently for upgrading from two 100 A services to two 200 A services on 4 duplex units. The customer didn't want to use a meter pack, for some reason. Anyway, I figured the service like a 400 A, and used the smallest service entrance conductors allowable by the NEC, 400 kcmil copper, with 2/0 copper to each meter socket from a trough overhead.

I got the job, built one service and had it inspected. Today the POCO guy comes out and sweats and wrestles and curses the "Big Ol' Wire" we had coming from the riser. I said "sorry buddy, that's the smallest wire we could get away with." He asked why that was, and I said the NEC says so.

He told me that they (the POCO) allow that kind of service to be fed with 4/0 copper. Of course, that would save me a bundle on the other three services, but the NEC says I have to use 400 kcmil minimum. So what would you guys do, use the POCO spec, or the NEC?

InPhase277 is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 03-17-2011, 06:21 PM   #2
BBQ
Senior Member
 
BBQ's Avatar
 
Join Date: Nov 2010
Location: New England
Posts: 23,838
Default

Quote:
Originally Posted by InPhase277 View Post
He told me that they (the POCO) allow that kind of service to be fed with 4/0 copper. Of course, that would save me a bundle on the other three services, but the NEC says I have to use 400 kcmil minimum. So what would you guys do, use the POCO spec, or the NEC?
If the conductors are on the customer side of the service point you must follow the NEC.

That said it sounds like these conductors supply more than one service disconnecting means if that is the case the NEC only requires the conductors to be rated as high as the calculated load not the total of the service disconnects.

Quote:
230.90(A)Exception No. 3: Two to six circuit breakers or sets of fuses
shall be permitted as the overcurrent device to provide the
overload protection. The sum of the ratings of the circuit
breakers or fuses shall be permitted to exceed the ampacity
of the service conductors, provided the calculated load
does not exceed the ampacity of the service conductors.

BBQ is online now   Reply With Quote
Old 03-18-2011, 09:37 AM   #3
Registered Member
 
Join Date: Feb 2008
Location: Atlanta, Ga/Hamilton, Al
Posts: 4,868
Default

The thing is there was no service calc. The reason being the customer simply wanted to upgrade the outside without upgrading the inside. In other words, the old 100 A panel was left in place and fed from a 100 A breaker in the diso outside. They wanted to capacity to put 200 A panels in in the future.

I figured the safest way to go would be with 400 A service SEC's, since we can't calculate a "future load". Since I bid and won the job using 400 CU, I feel that I should just keep using it, but the POCO douche had me wondering if I should just drop to 4/0 since they allow it. What would you do?
InPhase277 is offline   Reply With Quote
Old 03-18-2011, 09:46 AM   #4
Chief Electron Relocator
 
480sparky's Avatar
 
Join Date: Sep 2007
Location: Cornpatch USA
Posts: 31,280
Default

POCOs aren't bound by the NEC. That's how they 'get away' with feeding a 200a service with #2.
__________________
In winter, why do we try to keep the house as warm as it was in summer when we complained about the heat?
480sparky is offline   Reply With Quote
Old 04-04-2011, 10:53 AM   #5
Head Grunt
 
Join Date: Sep 2009
Location: Lower Adirondacks, NY
Posts: 336
Default

Hmmm, an older post but around here when we have something like this in question i just contact a planner from the POCO to see what their opinion is and then call my inspector to see if he will accept the planners opinion. Most of the time the inspector will follow what the POCO recommends.
__________________
No free man shall ever be debarred the use of arms.-Thomas Jefferson
woodchuck2 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What would Poco do? RIVETER General Electrical Discussion 1 07-19-2010 04:36 AM
new (POCO) meter features BryanMD General Electrical Discussion 8 07-15-2009 07:44 PM
Become your own PoCo Minuteman General Electrical Discussion 14 06-08-2009 08:43 AM
How to PO a POCO John Code Violation Discussion 3 12-23-2008 11:44 PM
Odd old service done by the POCO MDShunk Services and Service Equipment 2 09-29-2007 05:39 PM