Old 03-29-2012, 10:01 PM   #1
Default Properly grounding / bonding a transformer with building steel
It's been a while and I just want to ground / bond this transformer with building steel, water, etc. I know the neutral and ground should be bonded in the transformer. So then just bond the transformer to building steel before grounding on the secondary side too? (i.e. do you have to hit building steel from the transformer and on the secondary side).
Thanks for any advice or code help
KnipexUser is offline   Reply With Quote
Old 03-30-2012, 12:16 AM   #2
Heavily Armed Member
HARRY304E's Avatar
Welcome to the forum.....
What type of transformer do you have.?
Old 03-30-2012, 01:48 AM   #3
The answer will varies a little depending on what conferation the transfomer you are using.
Merci,
Marc
Old 03-30-2012, 06:11 AM   #4
It's a 480v to 120v transformer. I think it's a 75kva
Old 03-30-2012, 08:21 AM   #5
Electrical Simpleton
Pete m.'s Avatar
Take a look at 250.30
Pete
Confidence is the feeling you have before you understand the situation.
Old 03-30-2012, 10:10 AM   #6
Basicly you're building the GEC system for your SDS. You can bond in the transformer or in the first disconnect. Bonding in the transformer is how you generally see it done. MikeHolt has a picture somewhere on his website I've seen.
I bring the neutral to a double lug on the XO. From there I bond to the case with a lug that has multiple taps on it. Bring my GEC, EGC's and other bonding to that point. No hard fast rule on exactly where you bond in the transformer.
Bonding/Grounding Transformer Delta Cletis General Electrical Discussion 30 07-19-2011 04:29 PM
Bonding a steel building subelect General Electrical Discussion 8 03-23-2011 08:37 AM
Is it building steel or not? Gaffer15 General Electrical Discussion 2 01-20-2011 05:39 PM
steel bonding? calimurray NEC Code Forum 8 05-21-2008 12:42 PM
Grounding and bonding a transformer Jim Workplace Safety 5 08-18-2007 08:08 PM