Sizing Main Disconnect For Control Panel? - Electrician Talk - Professional Electrical Contractors Forum
Old 03-18-2008, 09:46 AM   #1
Default Sizing Main Disconnect For Control Panel?
I am looking for a quick rule of thumb when sizing the main breaker or fusing in control panels. Do you add up all the supplemental breakers and fusing and add 10% to get the main breaker size? All the components do not operate at the same time so the actual load will be much less than the sum of all the supplementary circuits. My back gound is stronger in control voltage, PLCs and VFDs. Power distribution is not my strongest point yet.
Voltshead is offline   Reply With Quote
Old 03-18-2008, 05:09 PM   #2
Licensed Journeyman
nolabama's Avatar
Rewards Points: 2,014
this may be a dumb question, but what is the control panel controlling? motors, lights, machines?
Old 03-18-2008, 08:56 PM   #3
I guess that would be a good thing to list. I have 8 each 1 HP frequency drives, 1KVA transformer, 480 to 24vdc power supply. The supply voltage is 480 3PH. I like using calculators to make designing move along faster. Do you have any suggestions for sizing breakers?
Old 03-20-2008, 06:16 PM   #4
Licensed Journeyman
nolabama's Avatar
sorry; way, way out of my league. Unfortunately outside of the ability levels of the people i work around so i go to this place.
Old 03-21-2008, 02:18 AM   #5
Rewards Points: 3,338
You size the main to protect the feeder, not the subsequent loads.
Old 03-21-2008, 07:24 PM   #6
DGFVT
John's Avatar
Rewards Points: 168
2.1 amps per motor times 175% = 4 amp and use FRN-R-4 fuses for each motor. This times 8 = 32 amps, so fuse it for a 30 amp duel element time delay fused main panel disconnect. Make sure you ground the 24 VDC secondary.
Carry On!
R.E.D.
Old 01-21-2011, 04:31 AM   #7
I would like to know what size disconnect for a resistive load bank rated for 500KW at 380 volt,3 phase,3 wire, 50hz, and 1.0 power factor. I'm thinking simple knife switch that is unfused.
davdug is offline   Reply With Quote
Old 01-21-2011, 05:58 AM   #8
RIP 1959-2015
HARRY304E's Avatar
Rewards Points: 1,344
IDK if you will get an answer the thread is from 3 years ago
davdug (01-21-2011)
Old 01-21-2011, 06:39 AM   #9
I beleive you're right. I'll try to post again.
wire and fuse sizing to disconnect gojuman General Electrical Discussion 7 08-28-2008 01:43 AM
Locks on Main Service Disconnect. pudge565 NEC Code Forum 2 07-30-2008 12:38 AM
Generator Sizing Mountain Electrician General Electrical Discussion 23 06-03-2008 07:08 AM
concuctor sizing Bkessler General Electrical Discussion 4 03-02-2008 07:41 PM