transformer reverse wiring - Electrician Talk - Professional Electrical Contractors Forum
Old 10-09-2007, 09:48 PM   #1
Default transformer reverse wiring
This concerns delta corner grounding
I have a 480 - 120/208 transformer.
I want to derive 480 volts.
I will feed a 30 kva with a 90 amp breaker and feed the L 123 lugs
I then will take H 123 for my load.
My question is do I corner ground one of the 3 H legs to produce stable voltage readings?
challenge electric is offline   Reply With Quote
Old 10-10-2007, 06:48 PM   #2
Rewards Points: 1,008
[quote]I will feed a 30 kva with a 90 amp breaker and feed the L 123 lugs
I then will take H 123 for my load. [quote]
I assume you mean X1, X2. X3 are 208 (no neutral/grounded conductor)and H1, H2, H3 480 VAC?
That is up to you the NEC does not require it.
BUT IMO, this is a bad installation. I speak from a multitude of experience, where contractors call my shop to check out WIERD voltages at a facility we get there, and we find this connection. In addition some transformer manufactures do not list their transformer for reverse feeding. Lastly there is a higher inrush on the 208 VAC side then there would be on a 208 delta to 480/277 Wye due to winding design They make the right transformer for the application, why not use it? 208 Delta to 480/277 Wye.
Trouble shoot hot ground reverse pmg General Electrical Discussion 6 10-16-2008 09:38 AM
Transformer? preacher General Electrical Discussion 7 10-02-2008 09:23 PM
Transformer wiring boyzrus Services and Service Equipment 6 08-14-2008 12:23 AM
transformer sizing ???? Vr_ecobox Services and Service Equipment 1 12-07-2007 08:49 PM
transformer DBack Elec General Electrical Discussion 2 11-29-2007 10:28 AM