Voltage issues with residential service - Electrician Talk - Professional Electrical Contractors Forum
Like Tree27Likes
  • 1 Post By Drew 64
  • 5 Post By RePhase277
  • 2 Post By PlugsAndLights
  • 3 Post By B-Nabs
  • 1 Post By sbrn33
  • 4 Post By ppsh
  • 1 Post By chicken steve
  • 1 Post By 99cents
  • 4 Post By splatz
  • 3 Post By ~48~
  • 2 Post By McDaniel8402
Old 02-08-2017, 10:04 PM   #1
Rewards Points: 28
Default Voltage issues with residential service
Hello all,
I have a friend of mine who received a shock when cutting a copper pipe going out to a detached living quarters. Dedicated electrical service, water is coming from the main house though. I went over to investigate and read the voltage on one leg of his 120/240V service at 40V, the other at 200V. I searched for a ground rod and found at least 1 under the panel. I couldn't tell if there was a second one, though the wire continued on after the first. After I figured out there was at least that part of the grounding electrode, I disconnected the bond wire to the water coming in from the main house. Voltage was then 0V on one leg, 240V on the other. I read the voltage in the main house and it was 120V to ground for each leg, so I don't think there's a problem with the utility side. I took a reading at the spot in the water supply he redid and it was 80V from the house main house side to the coupled piece he used to patch the pipe.
Is this just an example of why a detached living quarters needs to have a dedicated water supply as well, or anyone know what I'm dealing with here? All load side connections appeared tight at meter box and breaker panel.
Any help or advice is appreciated. I'm stumped.
~48~ is offline   Reply With Quote
Old 02-08-2017, 10:14 PM   #2
Rewards Points: 46
I think you've lost your noodle............
electricguy likes this.
Drew 64 is offline   Reply With Quote
The Following User Says Thank You to Drew 64 For This Useful Post:
~48~ (02-08-2017)
Old 02-08-2017, 10:14 PM   #3
RePhase277's Avatar
Rewards Points: 4,020
The neutral in the feeder between the house and suite is open. This is not a grounding issue. It has nothing to do with ground rods. The neutral is the issue.
The Following User Says Thank You to RePhase277 For This Useful Post:
~48~ (02-08-2017)
Old 02-08-2017, 10:15 PM   #4
Safety Pin Member
PlugsAndLights's Avatar
Rewards Points: 2,854
Forget about the grounds. You have a floating neutral.
P&L
~48~ (02-08-2017)
Old 02-08-2017, 10:31 PM   #5
Rewards Points: 28
Dedicated electrical service. No feeders. I thought it was a floating neutral, too, but the connections all looked tight. I couldn't get the Allan to fit into the neutral in the panel (thanks to the last person in) so I had to settle for the jiggle test.
The readings were consistent throughout whole system.
Old 02-08-2017, 10:34 PM   #6
Watt Pusher
B-Nabs's Avatar
Rewards Points: 438
Then it's loose somewhere else. The symptoms all point to an open neutral.
The Following User Says Thank You to B-Nabs For This Useful Post:
~48~ (02-08-2017)
Old 02-08-2017, 10:36 PM   #7
Safety Pin Member
If it's an overhead then it's likely at the mast head. But, it could be
anywhere between where you're measuring and the center tap of
the supply transformer.
P&L
~48~ (02-08-2017)
Old 02-08-2017, 10:42 PM   #8
still in business
sbrn33's Avatar
Rewards Points: 3,226
Eo when do we tell him to call an electrician?
emtnut likes this.
Old 02-08-2017, 10:55 PM   #9
ppsh's Avatar
Rewards Points: 358
If its overhead, I bet the POCO splice at the mast has failed or has a very high resistance connection. Current is going via water bond/ gas bond/ ground etc.. back to a nearby service(s) fed by the same POCO transformer.
Same situation has led to energized metal mesh in plaster walls, people removing water meters getting shocked, current on coax/phone wires.
There was a thread here a few years back about a bunch of house fires in Florida from the same situation.
ppsh is online now   Reply With Quote
Old 02-09-2017, 06:12 AM   #10
motherplucker
chicken steve's Avatar
Rewards Points: 5,740
Hello all,
No you're not , and the others are spot on following up 48, bum noodle.....
Having any return path to a mutual Xformer can assume the lions share of N load , given conditions described by you
In fact, part of my personal apprentice training is asking why the arc appears when touching a grounding electrode conductor to a municipal (or any other mettalic back to source) h20 pipe.
circuitman1 likes this.
Old 02-09-2017, 06:42 AM   #11
Rewards Points: 9,122
Go to your room.
chicken steve likes this.
Old 02-09-2017, 07:01 AM   #12
Rewards Points: 2,522
True or false:
When you have voltage on the ground electrode system, pipes, etc., it can be a number of things.
When you see voltages that aren't 120, but add up to 240, you have an open neutral.
Old 02-09-2017, 07:10 AM   #13
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 4,716
People call all of the time about voltage problems.
I tell them to call FPL and tell them your electrician said it was on their side.
More than 80% of the time it's a rotten service entrance splice.
Some of them are bad Smart Meters where it turns off only one side.
Old 02-09-2017, 07:15 AM   #14
motherplucker
True or false:
True
splatz (02-10-2017)
Old 02-09-2017, 07:22 PM   #15
Rewards Points: 286
Another vote for a neutral problem. Classic symptoms.
lightman is offline   Reply With Quote
Old 02-09-2017, 07:55 PM   #16
Rewards Points: 28
So I know it's possible, but is it likely that when the water pipe removal incident occurred it created a surge event on the neutral? I'm guessing the event was before the guy got shocked since there was an abnormal amount of voltage going to ground when it occurred.
Old 02-09-2017, 08:16 PM   #17
Band Member
emtnut's Avatar
Rewards Points: 7,902
So you think everything was fine, but you had a massive amount of current flowing on your GEC ?
all wiyht, rho sritched mg kegtops awound
Old 02-09-2017, 10:53 PM   #18
RePhase277's Avatar
The voltage appeared on the copper pipe when it was cut because the pipe was acting as the neutral. As soon as the cut occurred, the circuit was opened. When he touched both sides of the pipe, he got shocked because he completed the circuit through his body.
There was no surge event. If the lugs that you can check are good, then the problem is either in the line coming to the house, or the transformer itself. Call the utility and tell them you have an open neutral on their side. They don't usually drag their feet on this kind of call.
Old 02-09-2017, 11:24 PM   #19
Rewards Points: 28
Utility came out and addressed the issue. The neutral separated in the service drop. Kudos and gratitude to everyone.
circuitman1, telsa and splatz like this.
The Following User Says Thank You to ~48~ For This Useful Post:
splatz (02-10-2017)
Old 02-17-2017, 02:30 PM   #20
Rewards Points: 46
When I moved into the house I live in now, we had issues for about 6-8 months with incandescent lamps poppin' like popcorn. It was getting expensive, and ticking me off. I knew I had a voltage problem, but I was having trouble finding it. I would normally read close to 130V from line to neutral. Every now and then, my wife would call and tell me that power to half of the house had gone out. I suspected a bad transformer connection. About 2AM one morning I woke to the sound of my smoke detectors making all sorts of racket. They weren't alarming, but making a weird buzzing sound. I jumped out of bed (early January, about 30 deg outside) and realized half of the power to the house was out. Grabbed a meter and ran outside, and yanked the cover off of the panel for the house, and found one leg was dead. Called the power company, and a lineman showed up about an hour later. By that time, power had come back on. Lineman was ticked off, but I told him what I'd seen. He drove his bucket truck into my backyard and inspected the pole-mount transformer, and found a mess. When he tried to pull the primary fuse, the fuse, fuse holder, and leads all crumbled to pieces and fell on the ground. The secondary side was no better. Crusty, corroded, green connections on both legs and neutral. He cleaned it all up, reterminated everything, and I never had another lick of trouble out of it.
McDaniel8402 is offline   Reply With Quote
Residential 200amp Electrical service panel 13grind Services and Service Equipment 5 08-08-2016 12:18 AM
Residential Service darren79 Canadian Electrical Code Forum 29 05-26-2016 09:47 PM
400a residential service WMC Residential Electrical Forum 2 05-07-2016 07:35 AM
Residential main feed voltage fluctuation stackvortex General Electrical Discussion 27 03-14-2016 08:53 PM
400 amp residential service water line bonding Anathera NEC Code Forum 17 03-02-2016 09:52 PM