Old 09-11-2009, 08:03 PM   #1
Default Voltage loss problem.
I am trying to figure out why I lose 110v to a line when I turn the breaker on.
It is a 220v underground feed for a barn. One phase is used for lighting, the other phase is used for receptacles. When you turn the switch on for the lights, the 110v drops off. When the lights are turned back off, the 110v returns. It is not a problem with the lighting, I switched the phases to double check. It works the same way if I were to plug in a drill and turn it on.
What would cause 110v to disappear like this? No breakers trip, I simply lose the voltage. When I test each phase, I am getting 122.8 on the good line, but only 108.5 on the phase I am having problems with. As soon as I try to utilize the problem line, my meter will read no voltage at all.
winright007 is offline   Reply With Quote
Old 09-11-2009, 08:17 PM   #2
Measuring line to where? Ground,neutral, line to line?
leland is online now   Reply With Quote
Old 09-11-2009, 08:21 PM   #3
Line to neutral.
Old 09-11-2009, 08:22 PM   #4
Sure sounds like you have a marginal hot that's going open under load. Pretty common occurance on farms.
Old 09-11-2009, 08:22 PM   #5
drsparky's Avatar
Bad connection, get out the meger.
Old 09-11-2009, 08:26 PM   #6
3rd that
Old 09-11-2009, 08:31 PM   #7
I just talked to the owner after posting this. He told me the line was dug into and repaired. He said it was a long time ago when this happened. He also said they heat shrinked the wires.
So if they did not moisture protect the wires enough, I assume this is my problem. I guess my best bet will be to run a whole new line. There is now an addition on the house, and sits on top of where the wires were ran. It would be almost impossible for me to find the damaged area.
Old 09-11-2009, 09:47 PM   #8
That pretty well clears it up then, doesn't it?
Either that old repair failed or a new break developed. Add that to the list of reasons to do all your underground in pipe. Running direct burial under an addition is industrial-strength stupid.
Old 09-11-2009, 09:51 PM   #9
Seen your member
Is the line a direct-buried cable?
They do make locators that will find the fault in pretty short order.
Old 09-12-2009, 04:40 PM   #10
They ran it in PVC, but hit it with an auger.
Old 09-12-2009, 04:55 PM   #11
Seen your member
I guess you don't need a locator, then.
Old 09-12-2009, 05:06 PM   #12
This was done years ago. I am just going to replace the line.
Old 09-12-2009, 11:37 PM   #13
Stiff Member
idontknow's Avatar
Next time you troubleshoot it, try this.
Utilize the problem line
Check voltage on opposite phase to neutral
If 240, you may have a lost neutral.
idontknow is online now   Reply With Quote
Voltage imbalance problem electricguy483 Commercial Electrical Forum 1 06-22-2009 09:39 PM
Leg loss service call wirenut1110 General Electrical Discussion 13 06-07-2009 07:43 PM
Exfo Multifunction Loss Tester FOT-930 Max TesterII kliffwalker Tools, Equipment and New Products 2 05-31-2009 08:31 AM
need help calculating power loss john salyards General Electrical Discussion 16 03-12-2008 09:30 PM
calculating power loss john salyards NEC Code Forum 1 02-16-2008 07:40 AM