i have a 200 amp service wondering what size wire i need for a 100 amp subpanel 220' away from the main service? also what size equip. ground. i got with a 5% vd 1/0 cu and 3/0 at 3% drop. i also got 3/0 al at 5% and 300 at 3
%. this seems a little high. i was figuring to use the 5% drop and do a 3/0 al with a number 2al ground. does this sound right??
zss42002 is offline   Reply With Quote
Old 06-21-2010, 10:30 PM   #2
Rewards Points: 416
The sub panel is 100 amp but what is the calculated load. If you are looking for the wire size for 100 amps at 240 then 2/0 alum. would work. For copper you need #1.
For the EGC then look at T. 250.122
Old 06-21-2010, 10:43 PM   #3
william1978's Avatar
Rewards Points: 2,000
^^^^What Dennis said.
Old 06-21-2010, 10:47 PM   #4
Rewards Points: 416
Remember there is no NEC requirement to wire for VD. It is a good idea and good design but not required.
BTW, I believe the same wire sizes are good for 208, 3 phase also.
Old 06-21-2010, 10:57 PM   #5
Its for a garage at my friends house there is no calc. Load as of yet but there will prob be 15-20 lights a compressor, mayb a 220v motor for a lift. And acouple outlets for grinding wheel and stuff like that but nothing major. So 2/0 would be plenty for this?
As for the egc do I have to take into acount the length and bump it up a couple sizes like the feeders?? Or just go with the 100 amp size??
Old 06-21-2010, 11:05 PM   #6
I own stock in FotoMat!
Rewards Points: 6,520
If you increase the wire size, you must increase the ground size. 250.122(B).
Old 06-21-2010, 11:07 PM   #7
Rewards Points: 416
Good point
Old 06-21-2010, 11:10 PM   #8
Rewards Points: 416
Ken will calculate the egc for you for a few bucks.
Old 06-21-2010, 11:14 PM   #9
Rewards Points: 416
I think you would need a #4 copper EGC-- send Ken $10
Old 06-21-2010, 11:17 PM   #10
Man.... what a scheme.... get everyone on the forum to send me a ten-spot! I'm rich!
Old 06-22-2010, 02:20 AM   #11
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,144
just as long as dinner is at your house!
~Matt
Old 06-23-2010, 08:45 PM   #12
Florida resident
ampman's Avatar
Location: Florida , if your not here you're somewhere else
Rewards Points: 1,604
one million mcm
for lunch I had three cans of alphabet soup then afterwards I had a huge vowel movement
ampman is offline   Reply With Quote
Old 06-23-2010, 09:10 PM   #13
~Matt
Hey, if all 13,329 members sent me a 10-spot, I'd definitely have a shindig at my place.
Old 06-23-2010, 09:50 PM   #14
Rewards Points: 250
lets have a raffle
everyone who wants to put up ten bucks
pick one winner
oldschool is offline   Reply With Quote
Old 06-24-2010, 09:52 AM   #15
The more load, the more the voltage drop. Mike Holt has a calculator you can download.
http://www.mikeholt.com/technical.ph...calvoltagedrop
#3 THHN\THWN copper is good for 100 amps at 75 degrees.
With a load of 50amps at 240volts at 200' with #3 copper Mike Holts voltage drop tool says you have 2.1% voltage drop.
What size wire do i need? myles Residential Electrical Forum 16 05-17-2010 04:19 PM
Wire Size tjvaughan NEC Code Forum 13 03-10-2010 07:22 PM
calulating the main and subpanel LNJSFASHION General Electrical Discussion 26 06-03-2009 07:48 PM
Amp/Distance Wire Size Robby General Electrical Discussion 3 06-03-2008 04:55 PM
Wire size? RCG General Electrical Discussion 18 04-05-2007 09:21 PM