Default 208 vs 480 safety
For a long time, our products were designed to operate off of 208V. The engineers are all well trained in LOTO and safe practices for making live voltage measurements. We do not work live but need to make measurements of the voltage for testing purposes.
Now we are moving to 480V and I would like to ask what everyone does that is different for 480.
We will need to make voltage checks on live circuits. Do we need different probes?
Is you LOTO method different for 480 vs 208?
PPE different or the same?
Thanks
Old 05-02-2019, 09:29 PM   #2
Rewards Points: 890
I treat them the exact same.
Cow, bill39, glen1971 and 1 others like this.
Old 05-02-2019, 09:42 PM   #3
Bird dog's Avatar
Rewards Points: 2,072
Check out the difference between level III & level IV meters. The other thing is levels of PPE in case of arc flash for 208 vs 480.
Old 05-02-2019, 09:50 PM   #4
Rewards Points: 7,869
It's between 480, and 4160 is where the difference is. I use gloves for the 4160. 34.5kv. I use the panel meter.
The Following User Says Thank You to joebanana For This Useful Post:
emt1 (07-10-2019)
Old 05-02-2019, 11:31 PM   #5
cwsims84's Avatar
Rewards Points: 189
Thanks
Just use a 40cal suit/gear either way... really, if it goes ****ty and you aren’t wearing the right gear, it suddenly isn’t your problem anymore..
cwsims84 is offline   Reply With Quote
Old 05-02-2019, 11:39 PM   #6
EJPHI's Avatar
Rewards Points: 12
You guys are helping me a lot.
Keep it coming. I am gonna point managers to this thread
Old 05-03-2019, 10:35 AM   #7
Rewards Points: 2,644
480 is a touch voltage (wont jump) so you can treat it the same as 208. If you use 00 gloves like you are suppose to then its all good. (please don't claim that your guys always wear there gloves as we know better).
The biggest difference is you now have 277 trying to escape rather than 110. Where a wet 110v connection will hold a 277v connection will burn up. I prefer working 480 as ive never come across anything that isn't a wye at that voltage.
Make sure all your meters are rated to 600v cat IV especially tracers. Also try to get a idiot meter like a fluke T5 and tell your guys to use that as the primary meter. The other meters should only be used once you have reached the limits of the T5. This will reduce most of the risk of accidentally leaving a meter set to ohms or touching the probe on a wiggy.
Its a good thing that you are worried about the difference. That shows you still respect it. Once you get comfortable and loose respect is when it can all go horribly wrong.
tmessner likes this.
Old 05-03-2019, 12:55 PM   #8
Rewards Points: 20,695
Allow me to stick this thing in here , just to set the mood...........
Nationalize all foreign owned farmland now. Now.
Old 05-03-2019, 01:15 PM   #9
canbug's Avatar
Rewards Points: 2,028
Hey Mac, I always like seeing those videos but how many cycles was that flash? That is the worst case scenario and the best case would be that your fuse would open at a quarter cycle. Either way, PPE is required and good practice followed.
Tim.
Old 05-03-2019, 01:27 PM   #10
Bird dog's Avatar
Tim.
Something has to block the molten copper flying at you.
Old 05-03-2019, 04:53 PM   #11
460 Delta's Avatar
Rewards Points: 1,722
Just saying, but 277 will take out a bigger chunk of your favorite screwdriver than 120 will.
A B grounded 480 will do some real damage, I have several on R-mix plants and they are to be respected.
micromind for moderator- make ET more industrial
Old 05-03-2019, 06:15 PM   #12
EJPHI's Avatar
Rewards Points: 12
I checked with some of the guys today and we will have 480 delta feed in most instances. We also have some 208 corner grounded delta UPS that will have to play well with the 480. This should be fun.
Inside the equipment we use all black wire with L1, L2, L3 labels which may have to be rethought so we can easily know which wires have 480 on them.
Old 05-03-2019, 06:33 PM   #13
Bird dog's Avatar
Always check with a meter. Doesn't all of your equipment have nameplates with voltage etc?
Old 05-03-2019, 06:41 PM   #14
EJPHI's Avatar
Rewards Points: 12
Nope, but may need to do that.
Old 05-05-2019, 05:02 PM   #15
Rewards Points: 748
With all the new electrical safety requirements, your location might have to do an arc flash study. This is expensive and many places skip it when they get the estimate. It is based on NEC 70 E. For most places a Level 2 ( 12 cal.. ) PPE is fine unless you have large distribution panels or feeders. We had 800 amp, 480/277 volt panels that were a Level 1 PPE and 200 amp, 208/120 volt panel that were a Level 2 & 3. It depends more on the available fault current and the OCPD rather than the voltage. By today's standards, you always must wear your PPE and follow the rules of 70E. That means either sit in your office and ignore the voltage readings or be prepared to spend a lot more time with PPE, prep and filling out energized work permits. A Level 4 PPE is expensive and very difficult to work in unless the place is air conditioned down to 60 degrees.
Old 05-05-2019, 05:32 PM   #16
EJPHI's Avatar
Rewards Points: 12
We have very high energy close to where our equipment will be deployed. So yeah there is major concern about this step up in voltage.
Does anyone know of a very reliable indicator that we can connect line to line?
We can do something simple with some resistors and LEDs, but the indicator must always be correct. We can't accept a design where a false reading due to a failed component would indicate no voltage when in fact voltage is present.
Old 05-05-2019, 05:46 PM   #17
Bird dog's Avatar
A properly trained electrician with a meter.
Old 05-05-2019, 11:29 PM   #18
EJPHI's Avatar
Rewards Points: 12
Bull****
Old 05-07-2019, 07:40 AM   #19
Going_Commando's Avatar
Rewards Points: 1,620
Buy fluke meters with fluke connect so you can rig up your voltage testing and whatnot when its locked out, then close everything up, unlock, energize, and view your readings on your tablet while sitting comfortably on a 5 gallon pail out of the way.
I fricken love fluke connect.
Old 05-10-2019, 07:37 PM   #20
Rewards Points: 504
Do you mean something that you permanently install on the equipment to indicate that live voltage is present?
Grace Voltage Vision
Panduit Verisafe
Safety Hazard - Recall of Eaton Heavy Duty 30A and 60A Safety Switches Bird dog General Electrical Discussion 19 03-16-2019 12:04 PM
Phones and Safety splatz Workplace Safety 17 12-09-2018 11:31 PM
Punitive safety culture MDShunk Workplace Safety 48 05-30-2018 08:35 PM