Boiler overfilling - Electrician Talk - Professional Electrical Contractors Forum
Like Tree12Likes
Old 10-31-2019, 02:27 PM   #1
460 Delta's Avatar
Rewards Points: 1,222
Default Boiler overfilling
The boiler was overfilling at one of our plants and they were having to operate it manually, I wonder why.
Old 10-31-2019, 02:45 PM   #2
MTW
Rewards Points: 9,952
I see.
Old 10-31-2019, 02:59 PM   #3
joe-nwt's Avatar
Rewards Points: 986
Obviously because the ground isn't connected.
dronai likes this.
Old 10-31-2019, 06:43 PM   #4
Rewards Points: 2,834
Stevie Wonder says it's clear to his fingers!
Old 10-31-2019, 06:59 PM   #5
CoolWill's Avatar
Rewards Points: 3,922
So... There had to be a reason to do that in the first place.
Old 10-31-2019, 08:23 PM   #6
Rewards Points: 3,930
Float doesn't work? Bad control design?
Old 10-31-2019, 09:02 PM   #7
MTW
Low IQ comes to mind.
Old 10-31-2019, 09:05 PM   #8
460 Delta's Avatar
Drivers “helping” me out while I was running conduit and pulling wire for a new compressor at a plant. They absolutely destroyed beyond repair the old one that I was going to save and rebuild for a spare. Most of these guys are willing to help, but are absolutely bulls in a china shop leaving a path of destruction like a tornado.
glen1971 and stiffneck like this.
Old 10-31-2019, 09:07 PM   #9
460 Delta's Avatar
I see.
MTW likes this.
Old 11-04-2019, 11:06 AM   #10
Rewards Points: 256
“I landed the wires on separate terminals, but there was no continuity. So I put them on the same terminal and got continuity. Problem solved!”
Old 11-04-2019, 01:00 PM   #11
Band Member
emtnut's Avatar
Rewards Points: 1,848
Obviously it's because the lug is too big for the terminal.
And if you cut them a bit, you don't have to take the screw out
Old 11-04-2019, 07:04 PM   #12
Rewards Points: 1,618
Nice to see the correct color code
Old 11-04-2019, 07:10 PM   #13
Rewards Points: 994
the floats probably stuck you need to flush water out of the float valve everyday or they gummed up.
Old 11-04-2019, 07:51 PM   #14
460 Delta's Avatar
The float was new out of the box, they couldn’t understand the difference between NO and NC contacts and what a common was.
micromind likes this.
Old 11-04-2019, 07:56 PM   #15
460 Delta's Avatar
Color code I’ve got one plant that ALL control wires are brown THHN 16awg. From the manual station and batch control to the MCC, all brown and no numbers.
dronai and MTW like this.
Old 11-04-2019, 10:42 PM   #16
Cow
Rewards Points: 4,842
I had a similar one a few years ago for a bin tipper, the plant maintenance guys had replaced all the wire with white thhn.
I thought that was bad, but that still doesn't come close to what you've described....
Old 11-04-2019, 11:29 PM   #17
Rewards Points: 7,485
So, you're saying you let the "drivers" make up the brand new switch, and they had no idea what they were doing? Is that common practice?
Old 11-05-2019, 06:06 AM   #18
460 Delta's Avatar
It's common practice for drivers to be laborers if they're not on a load. It's also common for them to do something while I'm busy running conduit and pulling wire that they think will be less labor intensive, as in installing a float switch.
By the time I knew what they were doing, they had the old one demolished and were asking me how to connect the wires, they were up on top of a flat roof for access and I was landing wires inside. I was busy and thought I explained it well enough to them, obviously not.
R-mix is a whole different world and culture, loose and wild is the norm and it's so ingrained there's little I can do generally to stop it. Really good guys and a few gals that will do whatever I ask them, but watch out for the hurricane that follows.
Old 11-05-2019, 06:17 AM   #19
460 Delta's Avatar
I'm not sure how they did it, probably rang out the wires to ground and landed them as they went. They original owners had a construction crew with some good electricians in it, but probably got way behind and here you are. Possibly had a couple handy drivers pulling in the wire for them and oops, we forgot to number those, is that a problem?
Old 11-06-2019, 05:33 PM   #20
So, what happens when someone gets hurt, as in electrocuted, or flashed?
I would think make-up would be less laborer, and more specialized.
In the refinery, unit operators weren't even allowed change light bulbs. Do they let you drive their trucks?