Delta? wye? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree3Likes
  • 1 Post By brian john
  • 1 Post By Sblk55
Old 02-16-2018, 06:03 PM   #1
Sblk55's Avatar
Default Delta? wye?
Hi all, I have been a maintenance electrician in the same small plant for 25 years. I have never needed to know so never asked, but how do you know if your system is Delta or Wye?
We get 4160 from PoCo and transform it to 480 to feed our buss system. The buss system is three wire, no neutral. It is a grounded system.
Thank you for your help
Steve
Sblk55 is offline   Reply With Quote
Old 02-16-2018, 07:09 PM   #2
Rewards Points: 26,908
4160VAC to 480Y277VAC transformers are very common.
4160VAC to 480VAC delta is uncommon.
The place to look would be right on the transformer body.
Old 02-16-2018, 07:17 PM   #3
Rewards Points: 3,550
Steve
What is the voltage to ground 480 VAC on 2 phases or 277 VAC on all phases?
Or what is grounded.
micromind likes this.
Old 02-16-2018, 07:26 PM   #4
Rewards Points: 8,109
All depends on where it's grounded. Corner, or center.
joebanana is online now   Reply With Quote
Old 02-16-2018, 07:51 PM   #5
Sblk55's Avatar
We run a bit high, phase to phase is 493, phase to ground is 285.
Steve
Old 02-16-2018, 07:56 PM   #6
Sblk55's Avatar
A few years back we had a large project where we had an outside contractor do the work. They wanted to do the lighting on 277 and had to set a small 50KVA transformer to create a neutral.
Steve
Old 02-16-2018, 08:30 PM   #7
Rewards Points: 700
Lol.
Like my dad says;
One word:
Cast Core
NewElect85 is offline   Reply With Quote
Old 02-16-2018, 08:33 PM   #8
In your area.
nolabama likes this.
The Following 2 Users Say Thank You to brian john For This Useful Post:
NewElect85 (02-16-2018), nolabama (02-19-2018)
Old 02-16-2018, 08:35 PM   #9
Steve
I would think based on the above you have a 3 phase 4-wire grounded wye with a 3 phase 3-wire bus.
Old 02-16-2018, 09:18 PM   #10
Sblk55's Avatar
Thanks to you all and I will definitely check the transformers on Tues.
Steve
Old 02-16-2018, 10:11 PM   #11
Rewards Points: 3,422
Steve
Most likely, the original system is a 480 ungrounded ∆. Or possibly a 480 grounded B system.
The transformer is just a basic transformer with a 480∆ primary and a 277/480 Y connected secondary.
Then 4160 transformer is most likely not 277/480 but rather, 480∆.
One nice thing about a closed ∆ is that it tends to balance voltage at the expense of current. Motors like balanced voltages.......
Old 02-16-2018, 10:26 PM   #12
Sblk55's Avatar
Thanks Micromind, you are correct 20 years ago it was ungrounded. when we changed from 500 KVA transformers to 750 KVA they grounded the system. When pulling out one of the feeds to one of the busses they found where one phase had been shorting to the conduit. With no ground it never triped the breaker. They decided it would be safer to have a ground so that would not happen again.
Steve
Fronius Symo 20.0-3 480 (Delta to Wye Transformer), Neutral Wire jay_the_gemini General Electrical Discussion 5 02-13-2018 11:02 PM
Fronius Symo 20.0-3 480 (Delta - Wye Transformer), Neutral Wire jay_the_gemini Commercial Electrical Forum 2 02-13-2018 07:27 AM
4 wire delta & open delta Madmax73 General Electrical Discussion 6 02-01-2017 10:26 AM
Open delta open wye transformer bank Lone Crapshooter Industrial Electrical Forum 15 09-15-2016 01:42 PM
has anyone ever wire a delta to delta transformer? mike883 General Electrical Discussion 13 06-07-2016 07:38 AM