Hermetically sealed or class I div 2 fuse required - Electrician Talk - Professional Electrical Contractors Forum
Old 04-18-2019, 02:25 PM   #1
Rewards Points: 14
Default Hermetically sealed or class I div 2 fuse required
All,
Good afternoon. I'm designing a 24vdc distribution jct. box using a Hoffman type 4X, fiberglass enclosure in a class I div. 2 area. I have 20, fused terminals, 1 amp (+) and 20 terminals (-). The plant told me that I could not the Cooper 5X20 fuse because fuses do not meet the area class. Does anybody know where I can find a hermetically sealed or class I div. 2 rated fuse? I sure would appreciate it. Currently designed with Weidmuller type "WSI 4/LD 60-150V AC/DC" terminal with Weidmuller type "G 20/1.00A/F" fuse.
Thank you,
David
notredave is offline   Reply With Quote
Old 04-18-2019, 05:08 PM   #2
Rewards Points: 416
Are the terminals rated for class1 div2?
https://www.phoenixcontact.com/asset.../3465_en_A.pdf
mitch65 is offline   Reply With Quote
Old 04-18-2019, 05:30 PM   #3
Rewards Points: 12,577
You need to find something sand filled. The plant should tell you what to buy not what not to buy.
Old 04-18-2019, 06:02 PM   #4
Rewards Points: 326
If they are installed in an enclosure rated for the area classification, you can use a regular fuse. But that will be a really expensive can.
According to the article below from Bussman, with a regular enclosure, you can use non-indicating, filled, current-limiting fuses.
From http://www.cooperindustries.com/cont...iv-2-fuses.pdf
Fuses for the protection of motors, appliances, and lamps installed in general
purpose enclosures must also meet one of the following:
a) They are non-indicating, filled and current-limiting type. Bussmann offers
many fuses that meet the criteria for non-indicating, filled, current-limiting
type (See Note 1 and Note 2)
b) They are the type in which the element is immersed in oil or other approved
liquid. Bussmann does not offer this type of product.
c) The element is hermetically sealed against gases and vapors. Bussmann
does not offer hermetically sealed fuses for this type of
application.
File Type: pdf bus-ele-an-3186-class-1-div-2-fuses.pdf (232.4 KB, 39 views)
Old 04-18-2019, 09:12 PM   #5
Rewards Points: 3,876
I gotta disagree.. Speaking from the land of the CEC, a gasketed Junction Box is approved for Zone 2. A glass filled fuse is not approved in that area.. We'd have to use sand filled or ceramic fuses..
Old 04-18-2019, 09:15 PM   #6
Originally Posted by notredave View Post
All,
Thank you,
David
I'd steer clear of the LED indicating ones.. They SUCK! They often let enough leakage current through mess with some electronics. I don't believe they are approved in a classified area..
As for fuses, use sand filled or ceramic. In addition to the ones that Splatz posted, here are some more..
http://www.cooperindustries.com/cont...onicfuses.html
0-10v led dimming te12co2w Lighting Design 34 09-22-2018 01:59 AM
Class 2 Hazardous Locations Donnelly Canadian Electrical Forum 2 06-08-2017 10:13 PM
Two Questions from Apprentice maverick323 General Electrical Discussion 50 06-06-2017 07:26 AM
how do we know what kind of class for the transfomer fuse or switch gear DS fuse ? mike883 General Electrical Discussion 1 04-30-2016 04:44 PM
Harmonic Filter Fuse glen1971 PLCs, VFDs, Motors and Controls 2 04-06-2016 08:14 PM