Industrial Help Needed - Page 3 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree16Likes
Old 10-28-2019, 05:42 PM   #41
Rewards Points: 3,414
My method for identifying voltages and connection method in a building - go outside and look at the poco transformer setup. When you're as awesome and talented as I am, it only takes a quick glance to figure it out.
Of course this works with pole-mount transformers but what about pad-mount?
Old 10-28-2019, 05:46 PM   #42
Originally Posted by Weasel View Post
The only way you can get 480/277 on a delta transformer is to purchase a 3 phase 480vac delta primary and a 480/277 wye secondary and bond XO
You can also install 3 relatively small single-phase transformers and connect them zig-zag to create a neutral from an ungrounded 3Ø ∆ system.
Old 10-28-2019, 06:19 PM   #43
MTW
Rewards Points: 12,241
Read the label on it.
I've never seen a paramount for anything but the smallest industrial building around here, and those are always 480 volt wye since delta is no longer offered by our poco here. Those older industrial services are far too large to meet poco specs for paramount. Usually they receive primary voltage and have their own transformers, or the poco has some huge 100 kva or bigger ones sitting on the ground.
micromind likes this.
Old 10-28-2019, 07:38 PM   #44
460 Delta's Avatar
Rewards Points: 1,986
Like myself.
I don’t see.
Overkill Is Underrated
Old 10-28-2019, 09:36 PM   #45
MTW
Originally Posted by 460 Delta View Post
I don’t see.
Old 10-29-2019, 04:45 AM   #46
460 Delta's Avatar
I do see.
Old 10-29-2019, 10:38 PM   #47
Around here, the PUCO pad mounts don't have any labeling on the outside, only the factory nameplate inside the door.
Also, they're trying to get everything underground, they won't do anything overhead in Reno, only the outlying areas. And reluctantly at that.
Idiotic as it may seem the smallest 3Ø pad mount they have these days is 150 KVA.
They'll still hook up a 4 wire high-leg ∆ in the outlying areas but if anything goes bad on an existing ∆ bank in Reno, it gets replaced with a grounded Y.
Old 10-30-2019, 04:36 AM   #48
Rewards Points: 2,836
Originally Posted by JRaef View Post
While EFFECTIVELY this may wring true most of the time, in reality there is NO ground reference on an ungrounded delta system, so what you measure on from phase to ground depends on capacitance to ground, which can vary greatly from site to site, even on the same system. Plus it can often be "fooled" by things like power electronics that have surge protection erroneously left in place that has a "wye" connection with an internal ground reference. So sometimes you WILL measure 277V or some other odd voltage from phase to ground on an ungrounded delta system, so it's just not reliable to do a voltage measurement only.
I was thinking about this. If you tested phase to ground on a delta system with a low-Z meter / solenoid tester, would that eliminate the capacitive ground readings, readings through MOVs, etc.?