foothillselectrical 03-14-2019 08:19 PM
Hoping someone can help with this problem.
I got called to a customer site today. One building with two tenant spaces. Space 1 is supplied by a pole mounted transformer, 208V Y, 200A. The primary connected loads are bandsaws, lathes, drill presses, milling machines, etc. Nearly all are 3Ph loads, and everything in the building runs perfectly.
Space 2 is fed with a 480V delta, 800A service, pole mounted utility transformer fed from the same primary as the 208V. I can see the primary conductors jumping from transformer to transformer. When the tenant left yesterday everything was running properly, when he returned this morning his 3Ph motors (air compressor, HVAC, and dust collector) were reversed rotation. I have checked voltage and rotation from the main lugs on the switch gear through every bucket and transformer I could find, and everything is phased properly.
They do have a 208V, 200A panel supplied by a 75kva transformer. When the secondary conductors hit the main breaker, B and C phases are reversed. This, to me, indicates that the original system was reverse rotation, and when the sub panel was installed they reversed rotation to correct it. The air compressor and HVAC system are fed from the 208V system, and the dust collector is fed from the 480V system.
Any idea what can cause this?
*Additional note, there is another building on the property and another one down the street who are also customers of mine, and who are fed by the same utility branch circuit. I checked the line side power on those buildings and they are both correct.
glen1971 03-14-2019 09:08 PM
Did the utility do any work on site overnight? Maintenance crew doing work overnight? Can't say that I've ever seen rotation change overnight with no other intervention..
MikeFL 03-14-2019 09:12 PM
Something changed. If it wasn't on site, it has to be POCO.
foothillselectrical 03-14-2019 09:13 PM
Not that we can determine. We had the utility out today and he said they had no work orders in that area for struck poles or anything else that would have required replacing lines. I am the only electrician that works on the facility, and the only work I have done there is replace a metal halide wallpack with an LED, but that was on the 208V side that is still working. AND, I did that yesterday, so if someone else had been there working I would have seen them.
Thank you for your input.
foothillselectrical 03-14-2019 09:15 PM
I agree. But if it was POCO then I would have expected both units to have changed. Am I looking at something wrong?
glen1971 03-14-2019 11:02 PM
What do you mean? Is the equipment actually running backwards? Or is it wrong on a phase rotation meter? If it is actually running backwards, someone switched 2 wires.. If it is on one panel, they did it in that panel. If it is the site or one service, the POCO must have been involved.
HertzHound 03-14-2019 11:40 PM
If I take a rotation meter and hook up all three leeds, it will show one direction. If I remove a leed, it shows the opposite direction.
Is it possible you lost a phase? What happens on a Delta, does it go from a closed delta to an open delta and everything still runs, but backwards?
Since the power company was there, are all their cut outs closed?
How many transformers do you have on the delta bank?
joebanana 03-14-2019 11:54 PM
What did you do to correct the situation? Was it just those 3 machines running backwards? When the compressor runs backwards does it become a vacuum pump?
HertzHound 03-14-2019 11:56 PM
Did you take your readings with the main off so that your not reading through the loads. What was the voltage reading between all the combination of phases and phase to ground?
foothillselectrical 03-15-2019 06:48 AM
1. The equipment is actually running backwards.
2. In the 120/208V panel is phased BLK, BLU,RED (around here FWD is BLK, RED, BLU) IMO, I think this is because the original POCO phasing was reversed.
3. No one has done any electrical work in the building.
4. Two tenant spaces in the same building are supplied by the same POCO primary, as well as 2 other buildings known to be on the same POCO primary. POCO says they have done no work in the area.
foothillselectrical 03-15-2019 06:57 AM
I have 487V A-B, B-C, A-C. There are no open fuses. On my phase rotation meter if I lose a phase it won't rotate. POCO checked their transformer and said it was good. I have a single pole mounted transformer. I can physically see the jumpers from the 208 transformer of to the 480v transformer.
foothillselectrical 03-15-2019 06:58 AM
I have not corrected it yet. We left power off to the 3 phase equipment and are calling the POCO engineer today.
3DDesign 03-15-2019 07:03 AM
Is it possible that a panel feeding the reversed motors lost a phase and were back fed by one of the phases causing it to reverse?
Do the panels have Phase Loss Alarms?
JRaef 03-15-2019 03:56 PM
Phase rotation can't just randomly reverse. I have seen one case where the PoCo lost a transmission line and the crew, working in a storm, reconnected it wrong, causing an entire lumber mill to run backward for a few minutes, damaging a lot of equipment. Other times this happens when people plug in portable generators that are not phased correctly. But temporary changes in rotation are just not possible without someone having physically done it. So someone knows something and is keeping their mouth shut because they don't want to pay for any damage that was caused.
As to the lost phase theory, 3 phase motors will not start with single phase applied, they just vibrate back and forth. If they are ALREADY spinning, they may KEEP spinning with single phase. So with things like fans, as in the HVAC and Dust Collector that might be back-spinning because of air flow, that can happen. But an air compressor, I don't think so, unless MAYBE there is no check valve on the compressor and the tank pressure made it kick back when the phase was lost, so it then kept running backward. That's a stretch though. Could it be though that they just THOUGHT the compressor was running backward?
glen1971 03-15-2019 05:46 PM
Depending if the air compressor is a screw compressor, I've seen them REALLY not like going backwards.. Like destroyed itself by running backwards when the screw tried running through the case..
JRaef 03-15-2019 08:31 PM
Right, which is why a screw compressor always has a check valve.
frenchelectrican 03-15-2019 09:19 PM
I have see even pistion compressor go bad too when they ran backward due the oil pump only work on one direction so run it reverse can burn up the bearing if not getting any lube oil.
to OP did you are aware of momentary power dropped and kicked back on real quick if so it may cause to lock in reverse rotation even a phase conductor get brownout while other two still good it may cause this issue.
foothillselectrical 03-16-2019 07:14 PM
I agree with every theory posed here, including that "random Phase reversals cannot just happen." But, I am the only one who does work in these facilities and, other than the light fixture replacement previously mentioned, I haven't done any work in these two particular buildings in months. And the only two men who can authorize work to be done, haven't had anything done.
I am truly stumped on this one. The POCO is sending out a couple of engineers Monday to see if they can determine if something has changed on their side, but, as stated earlier, I can physically see the primary jumpers from the 208V transformer to the 480V transformer. And the 208V side is running correctly. I have checked rotation on several motors in facilities fed from the same utility line, including a different building yesterday a half mile away, and all is well in those facilities. I do not believe that the utility has done any work on the lines.
As far as the air compressor running backwards, it is a 2 stage piston compressor. I do not believe there is a check valve leaking by as it has held pressure for the several days this issue has been going on. And, I don't think it could cause the motor to start backward if it was leaking because it should only compress the piston to the bottom of it's stroke.
Thank you to everyone who has provided input on this.
varmit 03-16-2019 08:54 PM
If one of the transformer delta secondaries has failed, you could still measure the correct voltage on all three phases. The failed winding could cause a phase shift that would cause reverse rotation.
varmit 03-16-2019 09:00 PM
Motor current would probably be higher also.