Thhn Insulation Melting - Electrician Talk - Professional Electrical Contractors Forum
Like Tree45Likes
Old 12-09-2019, 09:03 PM   #1
dronai's Avatar
Rewards Points: 439
Default Thhn Insulation Melting
How many amps would cause the insulation on #8 thhn to melt ? I figured it would make it to about 70A.
A 40HP 480V motor shorted, and we thought the motor was fried, we meggered and it, and was good. But we found the wire from the control panel was #8 had melted !
This is on a Grinding machine, that the operator can increase the resistance by adding more pressure on the Metal when grinding.
The Ol's were sized properly, but didn't trip ??? wth ?
Old 12-09-2019, 09:17 PM   #2
Cow
Rewards Points: 5,232
52 amp x 125%=65 amps. #6 minimum if no derates.
dronai and glen1971 like this.
Old 12-09-2019, 09:29 PM   #3
Southeast Power's Avatar
Rewards Points: 9,264
Motors are interesting, I tend to up size motors that are designed to be loaded on the heavy side of their capacity.
We have a project with some RTUs that require 108 MCA, I’m going to use #1 copper for them.
In a previous like, I would have used #2 aluminum.
dronai and Kevin_Essiambre like this.
Old 12-09-2019, 09:44 PM   #4
dronai's Avatar
Rewards Points: 439
I think it said 46 Amps on the nameplate
Old 12-09-2019, 09:46 PM   #5
dronai's Avatar
Rewards Points: 439
Yeah, I'm definitley going to upsize anything that's questionable.
Southeast Power likes this.
Old 12-09-2019, 09:52 PM   #6
Bird dog's Avatar
Rewards Points: 594
Did you test the OL ckt?
Old 12-09-2019, 10:00 PM   #7
dronai's Avatar
Rewards Points: 439
No, it's an old Nema starter, and I did check the numbers on the heaters. How do you test that ?
Old 12-09-2019, 10:03 PM   #8
Bird dog's Avatar
Rewards Points: 594
IDK. Try undersizing the the heaters just to see them drop the coil out.
edit...Was the breaker sized properly? How old is it? (will it trip?)
millelec likes this.
The Following 2 Users Say Thank You to Bird dog For This Useful Post:
dronai (12-09-2019), millelec (04-15-2020)
Old 12-09-2019, 10:19 PM   #9
dronai's Avatar
Rewards Points: 439
This control panel has fuses, and yes the fuses went out. The wire was defintely undersized, but I just thought the insulation would handle at least 60A before melting. I think the OL's should have tripped at about 52-56
SQ D 87.7 I think they were
The Following User Says Thank You to dronai For This Useful Post:
Bird dog (12-09-2019)
Old 12-09-2019, 10:24 PM   #10
Guest
Rewards Points: 92
I Have been told several times from wire manufactures that the ampacity of these wires are over engineered and that the table has to be followed but the wire typically can hold a lot more than was is required, I will say how ever when you placed your meg ohmeter on the motor what was the reading you received? is there maybe any weird conditions the wire has been subject to? is there perhaps any thing else on the circuit or is it in an hot environment? any other wires in the conduit?
anthonysolino is offline   Reply With Quote
Old 12-09-2019, 10:25 PM   #11
Bird dog's Avatar
Rewards Points: 594
How was the wire melted? Maybe a failing termination?
Maybe a fluke? (no pun intended)
Old 12-09-2019, 10:30 PM   #12
dronai's Avatar
Rewards Points: 439
Motor megged fine. No, and No
Together in places, like a lot of heat. No terminations were good. Insulated taps in the pecker head
Old 12-09-2019, 10:31 PM   #13
Guest
Rewards Points: 92
ideally you should get a reading on a 480v motor of .3 megohms on your meter for a passed test,
Old 12-09-2019, 10:32 PM   #14
dronai's Avatar
Rewards Points: 439
Motor megged fine. I figuered the same. No, and No
Old 12-09-2019, 10:37 PM   #15
Bird dog's Avatar
Rewards Points: 594
Strange...anything out of the ordinary happen like lightning or could something else fault through the motor...any welding?
Old 12-09-2019, 10:40 PM   #16
dronai's Avatar
Rewards Points: 439
Don't think. like I said, I think the operator could have applied too much pressure driving the amperage up, but he does have an amp gauge to watch for this.
Old 12-09-2019, 10:46 PM   #17
Bird dog's Avatar
Rewards Points: 594
Could it be possible the operator runs the machine in such a manner that it heats up the wire without the heaters tripping? Oversize the wire &/or undersize the heaters.
In other words, the wire cools slower than the heaters.
Old 12-09-2019, 10:49 PM   #18
dronai's Avatar
Rewards Points: 439
Rewired with #6, done
John Valdes and CoolWill like this.
Old 12-09-2019, 11:02 PM   #19
Guest
Rewards Points: 92
if that doesn't work you can try to wire it up with TFE conductors I wire my street lighting up down here with it, it helps for high heat type situations,
Kevin_Essiambre likes this.
Old 12-09-2019, 11:06 PM   #20
dronai's Avatar
Rewards Points: 439
TFE never tried it