I'm not sure of the part # since it's been a long time since I've installed one but these were bolt-on 125 and 150 amp breakers that would fit in a basic NQOD panel. They took 6 spaces and it was really important that they be installed in a 3Ř panel, not a single phase one.
Are they still manufactured or is there a better way to install a 125 or 150 amp breaker in a NQOD panel?
Thanks,
Rob.
micromind is offline
Old 11-22-2016, 09:43 PM   #2
backstay's Avatar
Rewards Points: 296
Thanks,
Rob.
QOB3150VH $1844.90 from Grainger
$650 from this place. Ships in 3 days.
http://www.southlandelectrical.com/i...6grBoCEurw_wcB
micromind likes this.
backstay is offline
Old 11-22-2016, 10:07 PM   #3
Rewards Points: 21,882
QOB3125VH and QOB3150VH is not super common item but ya can get it but be aware some lead time on that.
I dont have the price list with me but it will be close what Backstay qouteing on that unless you get one of the breaker supply wholesale place then you may get lucky on price break.
frenchelectrican is online now
Square D_Sarah (11-29-2016)
Old 11-24-2016, 12:56 PM   #4
Thanks, you guys. I'm pretty sure this be less $$$ than any other option.
frenchelectrican likes this.
Old 11-29-2016, 02:17 PM   #5
Manufacturer
Square D_Sarah's Avatar
Rewards Points: 38
To confirm what the others have commented on . . . the part numbers that you are looking for are QOB3125VH & QOB3150VH.
These are bolt on breakers and will go into the 3 phase NQOD panel. They take up 6 pole spaces. There is a max amperage of 20A for the breakers mounted opposite the QOB3125VH and QOB3150VH
Life Is On | Square D by Schneider Electric
Square D_Sarah is offline
Old 11-29-2016, 11:00 PM   #6
The other thing I forgot to add to this.,,
It have to be 400 amp panelboard or larger and watch the bussbar tabs., you may have to swap the bussbar cross link fingers if they do have it there because some are rated at lower amparage.
AFAIK the VH series are rated at 42,000 AIC if I remember the numbers correct @ 240 volts Line to Line.