#12 AWG on 25 amp OPD - Electrician Talk - Professional Electrical Contractors Forum
Old 05-12-2010, 08:17 PM   #1
Les Voltage
Default #12 AWG on 25 amp OPD
I cant remember the reason I was able to use a 25 amp OCPD with #12 on a motor. I think it was because of the start up amps it pulled that made it use a 25 amp.
Any help? My boss told me today " There are no circumstances where #12 should be on any OCPD larger than 20 amps"
Would love to get a free lunch.
Old 05-12-2010, 08:19 PM   #2
child please.....
NolaTigaBait's Avatar
Rewards Points: 14
Yeah, for a motor you can size ocp at 250% of the flc.
Old 05-12-2010, 08:20 PM   #3
Rewards Points: 6,421
Originally Posted by Voltech View Post
I cant remember the reason I was able to use a 25 amp OPD with #12 on a motor. I think it was because of the start up amps it pulled that made it use a 25 amp.
Any help? My boss told me today " There are no circumstances where #12 should be on any OPD larger than 20 amps"
Air conditioning equipment and motor loads are two instances where he is wrong.
Old 05-12-2010, 08:21 PM   #4
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
Tell your boss you would like a free lunch.
A/C branch circuits can be #12 THHN with 40 amp OCPD if the nameplate data says so.
Replies based on NEC 2014
Old 05-12-2010, 08:21 PM   #5
I should say, however, that if that #12 terminates at a receptacle outlet, your boss is right. If it goes to (certain) equipment directly, then he is wrong in certain cases.
Old 05-12-2010, 08:45 PM   #6
sparks134's Avatar
Tell your boss to look at table 240.4 G... Tell your boss buy you want
steak for lunch!!!
sparks134 is offline   Reply With Quote
Old 05-12-2010, 09:20 PM   #7
Rewards Points: 2,298
Table 310.16 shows that #12 wire is good for 25 amps at 75C. Thus using article 240.4(D & G) by the asterisk at the bottom of the table, we are not only allowed to use #12 with a 25 amp breaker but we can use #12 at 25 amps and use a 45 amp breaker.
I can't help it if I'm lucky
Old 05-12-2010, 09:25 PM   #8
Les Voltage
steak for lunch!!!
I wont hit him up for a steak, but I wont settle for fast food
He has an open policy in the shop. Prove him wrong and he will buy you lunch. Its a win win situation for him IMO
Old 05-13-2010, 01:54 AM   #9
JohnR's Avatar
Sounds like a pretty good boss to me. He hiring?
Signed out.
Old 05-13-2010, 06:00 AM   #10
Rewards Points: 976
Here is an example of a #12 on a 45 amp breaker.
A branch circuit to a 3 HP 230 V single phase motor; all parts are listed for 75 deg C.
(Hint; articles 240.6, 310.16, 430.22(A), tables 430.52, and 430.148)
  • Table 430.148 gives a 3HP motor a full load current of 17 amps
  • 430.22(A) requires conductors be sized at 125% of full load current
  • 17 x 125% = 21.25 amps
  • Table 310.16, #12 THHN 75 deg C column = 25 amps
  • Table 430.52 allows up to 250% for the inverse time breaker
  • 17 x 250% = 42.5 amps
  • 240.4 states we can go UP to the next STANDARD size breaker
  • 240.6 would let us go up to a 45 amp breaker
  • Answer 45 amp breaker.
Roger
Roger is offline   Reply With Quote
The Following User Says Thank You to Roger For This Useful Post:
Dennis Alwon (05-13-2010)
Old 05-13-2010, 07:17 AM   #11
Very nice Roger. I almost posted something similar along with my post above but I was too slack.
Roger (05-13-2010)
Old 05-14-2010, 07:13 AM   #12
Proud Navy Veteran
Greg's Avatar
Rewards Points: 592
The reason why you can a breaker larger than 20 on a 12 wire is because a motor circuit is the best protected circuit out there. You have overloads protecting the motor should the motor go into a fault condition, the O.L.'s will release before the breaker trips. This because of how they are sized according to code.
Memorial Day: All gave some but some gave all.
Take the time to tell a Veteran Thank You, You owe him/her at least that much. After all Freedom is not Free.
Old 05-15-2010, 12:00 AM   #13
Les Voltage