I was talking with a lineman (which I am NOT!) about a service they had to do. One pole and there was a need for 120/208 for a building and next door was a resi service. He said he thought you could do it with only three cans, which I think to be true. But the POCO made them install 4 cans with the resi being dedicated just to that service.
Couldn't this be done in a typical 208Y if one of the unused taps were brought over for the 120/240 service as all the center taps would be bonded anyway?
A typical 120/208 service uses three tap cans (120-0-120) on the pole with only one tap and the center tap used leaving half the secondary unused on all three cans....each one only produces 120V, but would still have 240 available if the other tap was used?
I could see some possible balancing issues with maybe a larger can and two smaller is the 120/240 load were significant. Just having some good electrical discussion.
TWN
TheWireNut is offline   Reply With Quote
Old 06-26-2015, 08:08 PM   #2
Rewards Points: 26,838
A 208Y120 single phase Service uses a different meter socket than a 240/120 two leg Service.
Right there, that's a show stopper for the Poco.
All Poco's have found out that being too clever -- bites them back.
Old 06-26-2015, 08:35 PM   #3
Rewards Points: 265
We are talking about two separate services on two separate buildings. one with 120/208 three phase and one 120/240 single phase. Two meters.
TWN
Old 06-26-2015, 09:17 PM   #4
Rewards Points: 3,360
With typical pole-mount pots, there are 2 - 120 volt windings on the secondary. When the service is 120/240, they are connected in series with the common connection being the center bushing.
When the service is 120/208, they are connected in parallel and only 2 bushings are used, usually the two outside ones. The 3rd bushing (usually the center one) is not connected.
But I see what you're saying. If one of the pots were connected in series (120/240 and all 3 bushings used) then yes, that one would supply both single phase and one phase of the Y.
The problem is that pot could easily be grossly overloaded if both the single and 3 services were in use at the same time. Going to a larger pot would pose problems as well; the impedance would be different resulting in voltage imbalance in the 3 service, plus 1/3 of the pots capacity could never be utilized.
Plus, very few linemen would have even the slighest clue how to troubleshoot it if a problem ever arose..........lol. Let alone actually hook it up.
The Following 4 Users Say Thank You to micromind For This Useful Post:
JW Splicer (06-26-2015), Rollie73 (06-26-2015), tates1882 (06-26-2015), TheWireNut (06-27-2015)
Old 06-27-2015, 10:00 AM   #5
Barjack's Avatar
Rewards Points: 308
I'm really confused here.
Here is what I think I know:
In a wye system, one end of each secondary winding is connected to the one end of the other two, producing a common point, the neutral.
The "floating" ends of the wye are 208V L-L, and 120V L-N.
So, where would the 240V come from?
Are you saying there is an extra winding in each secondary, that is not being used in a wye configuration, and if connected in series with one of the legs it would produce 240V?
So, would one of the line phases in the wye system actually be the neutral in the 120/240 system, which would actually be 240V L-N on the wye with the extra winding?
Apologies if this makes no sense.
Barjack is offline   Reply With Quote
Old 06-27-2015, 11:13 AM   #6
In a typical pole-mount pot, there are two 120 volt windings. for a 120/240 service, they are connected in series. The point of connection becomes a center tap and it is connected to the center bushing.
For a 120/208 service, the windings are connected in parallel. Since there are only 2 wires, only 2 bushings are used.
If one of the pots on a 120/208 service is connected in series, both 120 (for the Y service) and 120/240 (for the single phase service) exist. The other 2 pots are connected 120 for the other 2 legs of the Y.
Old 06-27-2015, 12:08 PM   #7
Barjack's Avatar
Rewards Points: 308
120/208 3phase and 120/240 single with 3 cans-imageuploadedbyelectriciantalk.com1435421317.830396.jpg
If you can read my chicken scratch, would this be the correct wiring diagram?
Wouldn't this create a bonding problem as both neutral points would end up connected together?
Sent from my iPhone using electriciantalk.com
120/208 3phase and 120/240 single with 3 cans-imageuploadedbyelectriciantalk.com1435421082.668279.jpg
The Following User Says Thank You to Barjack For This Useful Post:
Old 06-27-2015, 12:32 PM   #8
professional redneck
Rewards Points: 187
almost this, the center top of the single phase would be the same as the neutral of the 3 phase
metalpats is offline   Reply With Quote
The Following User Says Thank You to metalpats For This Useful Post:
Barjack (06-27-2015)
Old 06-27-2015, 12:46 PM   #9
Barjack's Avatar
Rewards Points: 308
120/208 3phase and 120/240 single with 3 cans-imageuploadedbyelectriciantalk.com1435423548.771141.jpg
So, this then?
Old 06-27-2015, 01:06 PM   #10
Originally Posted by Barjack View Post
Attachment 58122
So, this then?
That's it!!!
This connection would work, but the 240 pot will either be overloaded or not used to its capacity.
The Following 2 Users Say Thank You to micromind For This Useful Post:
Barjack (06-27-2015), TheWireNut (06-27-2015)
Old 06-27-2015, 01:12 PM   #11
Barjack's Avatar
Rewards Points: 308
Originally Posted by micromind View Post
That's it!!!
I had no idea those pole transformers had double windings in them.
Thanks for the help!
micromind (06-27-2015)
Old 06-27-2015, 08:21 PM   #12
Very Long Vacation
Rewards Points: 5,262
This thread:
http://www.electriciantalk.com/f2/24...25/#post912964
The Following 2 Users Say Thank You to meadow For This Useful Post:
Barjack (06-27-2015), micromind (06-27-2015)
Old 06-27-2015, 08:23 PM   #13
Very Long Vacation
Yup! They parallel them to het 120 volts in a 3 phase bank, series for 120/240. That way both are covered. See above post for diagram.
Old 06-27-2015, 10:12 PM   #14
Rewards Points: 265
This is exactly why I asked on here! Thanks guys. I was always under the impression that they only used half of the secondary, but they actually parallel them for full capacity. The POCO around here used the center tap for the common or neutral and the other tap is unused. If I could figure out how to post pics on here I certainly would!
TWN
The Following 2 Users Say Thank You to TheWireNut For This Useful Post:
meadow (06-27-2015), micromind (06-27-2015)
Old 06-27-2015, 11:25 PM   #15
When paralleled, any 2 bushings will work. Around here, they use the outside 2 and the center one is not connected.
Old 06-27-2015, 11:48 PM   #16
Very Long Vacation
Double bushing can? They normally pic the center around here because single bushing cans are required to have a ground (can) strap to the neutral bushing.
Old 06-28-2015, 01:05 AM   #17
That's interesting; around here, all 3 bushings are isolated and whatever one is to be grounded is done so by connecting the neutral to both the pole ground and the primary neutral/ground.
120/208 1-ph load in 120/240 environment mikewillnot Commercial Electrical Forum 21 06-08-2015 06:15 AM
240, 4 wire to 120/208 jgs8919 Services and Service Equipment 14 02-04-2014 12:34 PM
120/208/240/480? dietdrkelp General Electrical Discussion 18 10-01-2013 10:36 AM
480/277, 240/120, 208/120 in same bldg THARMON NEC Code Forum 10 03-22-2010 09:28 PM
120/240 high leg to 120/208? deadshort52 General Electrical Discussion 3 01-08-2009 08:52 PM