2 Ground bars in a panel - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree56Likes
Old 03-28-2019, 10:06 AM   #21
Rewards Points: 7,520
I’m confused. What’s the issue here?
Is there a requirement in the NEC that says the factory supplied terminals strips used to connect the bare bond wires need to be connected together with a conductor or a green coloured screw?
Big commercial panels will have many of these (ground strips) to install on both sides of the panel to land all the bare bond wires from all the many circuits.
Are you saying they need to be connected together with a conductor ? If so, what a ridiculous requirement that is.
brian john and glen1971 like this.
brian john (03-28-2019)
Old 03-28-2019, 10:12 AM   #22
Russian Bot
Helmut's Avatar
Rewards Points: 3,751
it's always been a requirement. In the above situation, the panel box is the conductor.
MCasey likes this.
Alright, Alright, Alright... I'll tell you what to do. Go that way, reeeeeeeeeally fast. If something gets in your way......turn.
Old 03-28-2019, 10:21 AM   #23
They are always connected to the panel box. And breaker panels are always metal.
When would a panel ever actually need a conductor connecting these?
Old 03-28-2019, 10:46 AM   #24
Russian Bot
Helmut's Avatar
I agree. Probably 99% of time anyway.
I've never seen a fiberglass panel board, but I would imagine they're out there somewhere for some application. It's the only time I could think of.
eddy current likes this.
Old 03-28-2019, 11:42 AM   #25
I’ve never seen a fibreglass panel, I doubt they exist. And if they did, the bonding terminals would be connected from the manufacturer I bet.
That’s why I’m confused with the question from the OP as it is not required with a metal breaker panel.
Old 03-28-2019, 11:52 AM   #26
Rewards Points: 421
Thatís why Iím confused with the question from the OP as it is not required with a metal breaker panel.
I am confused by most of this thread.
Old 03-28-2019, 12:27 PM   #27
Government Services
The confusing thing here is why would one would thnk you would need to connect the ground bars I the first place? Cannot recall even seeing this in the most intricate detailed job spec
MCasey is offline   Reply With Quote
Old 03-28-2019, 12:31 PM   #28
Rewards Points: 421
Yup, but people went with it which made it more confusing.
Maybe they were confusing connecting multiple neutral bars? Or in the case of a service panel, you can put neutrals on a ground bar if you connect it with a large enough busbar or conductor.
But for ground bars, just attach them to the panel.
brian john and eddy current like this.
Old 03-28-2019, 12:34 PM   #29
Rewards Points: 46
Iíve never seen a fibreglass panel, I doubt they exist. And if they did, the bonding terminals would be connected from the manufacturer I bet.
Apparently the OP has someone telling him that he must, or for some reason is wondering if it's necessary.
As far as fiberglass panels, they have existed. I have seen 1 Square D Trilliant panel, which are no longer being made.
Sent from my Moto Z (2) using Tapatalk
Old 03-28-2019, 01:57 PM   #30
Rewards Points: 1,494
In Europe, they are used extensively
Old 03-28-2019, 01:58 PM   #31
Originally Posted by Forge Boyz View Post
Apparently the OP has AN IDIOT INSPECTOR telling him that he must, or for some reason is wondering if it's necessary.
Fixed it for you.
Old 03-28-2019, 02:17 PM   #32
Rewards Points: 304
IER in Texas makes Seimens panels with fiberglass or stainless enclosures.
brian john likes this.
Old 03-28-2019, 07:10 PM   #33
Can't Remember
Rewards Points: 864
I think if it makes you feel better do it, but I'm hard pressed to believe its required.
Old 03-28-2019, 07:37 PM   #34
Rewards Points: 278
No,
Did it come from the manufacturer that way? NO
Did you install the ground bars? NO
I can guarantee the metal back box has more conducting surface area than a #6 AWG CU.
Common sense is leaving this trade in droves.
This.
And I was surprised I had to get to post #14 to see it.......
Old 03-28-2019, 10:40 PM   #35
Rewards Points: 6,843
Why do you need a Green bonding screw for a ground bar?
I do not think there is any reference to a green screw in the NEC.
Green to indicate a ground. Why are ground screws green on receptacles, and switches, ground pig tails, and other equipment? I didn't say "need", but it would be a clue as to whether it's meant as a bonded bus. My shop vac motor has a ground screw on the motor, even though there's no exposed metal anywhere on the unit. What's the purpose? And it is referenced in the NEC.
Old 03-28-2019, 11:09 PM   #36
Rewards Points: 1,171
The 2nd ground bar comes with the panel so you can take one out and resell it next time you install a cheap main lug aluminum bus panel
Old 03-29-2019, 04:24 AM   #37
Rewards Points: 421
What youíre saying is not based in reality.
Iíve never once seen a green screw in a ground bar on a panel. It just doesnít happen.
The only green screw is the one used as the main bonding jumper through the neutral bar.
Bird dog (03-29-2019)
Old 03-29-2019, 07:27 AM   #38
CoolWill's Avatar
Rewards Points: 2,012
What is all this? I step away for a few days and stuff like this happens.
Additional ground bars in a panel don't need a wire conductor to bond them. They are attached to the grounded metal can.
I'm With Her! Hillary 2016
Old 03-29-2019, 09:12 AM   #39
Rewards Points: 304
Originally Posted by joe-nwt View Post
This.
Welcome aboard @joe-nwt!
Enjoy your ride here.
Old 03-29-2019, 01:06 PM   #40
Rewards Points: 278
Green ground screws are for people in the DIYChatroom.com. Those people may also need help identifying a bonded bus.
HackWork likes this.
Out building independent ground NJMike Residential Electrical Forum 10 07-05-2018 08:09 AM
Panel ground w/Disconnect WronGun Residential Electrical Forum 3 11-26-2017 04:30 PM
Double panel design question. JohnJ65 Services and Service Equipment 23 07-07-2017 08:19 PM
How do you ground a panel? 99cents Canadian Electrical Forum 24 01-29-2017 10:11 PM
Old Breaker/Fuse Panel A Little Short General Electrical Discussion 18 10-11-2016 05:34 AM