Installed a Murray 30 amp 2 pole GFI for a hot tub about 5 years ago .This hot tub required a neutral connection....customer had been using the test button to shut hot tub down for periodic servicing(which was probably less frequent than Murray recommends testing the "test" button).customer says the test button no longer trips the breaker.If I were to test this breaker for ground fault interruption, I would first check all of the line side potential voltages(phase to phase ,phase to neutral and phase to ground) I would probably then check each load phase with a load to ground.I would expect the breaker to trip. I read somewhere(assuming it was a typo) that you would test the line side to ground for ground fault interruption. That made no sense to me.I think I'll ultimitly tell the customer to change the breaker for liability/safety even if it's just the physical test button that is non functional. any thoughts?
drums5 is offline   Reply With Quote
Old 04-14-2012, 05:22 PM   #2
I own stock in FotoMat!
Rewards Points: 6,520
The only acceptable method to test a GFCI is to use the built-in test button. If it fails to open the breaker, it's time to replace it.
The Following 4 Users Say Thank You to 480sparky For This Useful Post:
drums5 (04-15-2012), Pete m. (04-16-2012), sbrn33 (04-15-2012), SparkYZ (04-16-2012)
Old 04-14-2012, 06:20 PM   #3
BBQ
Salty Member
BBQ's Avatar
The test button fails to trip a 5 year old GFCI.
Hmmm what should I do?
drums5 (04-16-2012)
Old 04-14-2012, 06:27 PM   #4
PM Cletis.
Start a poll.
The Following 3 Users Say Thank You to 480sparky For This Useful Post:
BBQ (04-14-2012), drums5 (04-16-2012), HIVOLT (04-14-2012)
Old 04-14-2012, 06:32 PM   #5
BBQ
Salty Member
BBQ's Avatar
PM Cletis.
Start a poll.
LOL, seems like the 'in' thing to do.
Old 04-15-2012, 06:52 PM   #6
aDudeInPhx's Avatar
Rewards Points: 268
You would test the LOAD side to ground & it should trip the GFI.
aDudeInPhx is offline   Reply With Quote
Old 04-15-2012, 06:53 PM   #7
Rewards Points: 6,421
Which adds no information of value to the troubleshooting process. If the test button doesn't work, it's time to replace the breaker. There's nothing you need to know beyond that.
The Following 5 Users Say Thank You to MDShunk For This Useful Post:
BBQ (04-15-2012), frenchelectrican (04-17-2012), oldtimer (04-15-2012), Pete m. (04-16-2012), Restoration (04-15-2012)
Old 04-15-2012, 06:55 PM   #8
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Invent your own contraption using a momentary pushbutton and 100 watt bulb.
The Following User Says Thank You to Shockdoc For This Useful Post:
drums5 (04-16-2012)
Old 04-15-2012, 07:24 PM   #9
aDudeInPhx's Avatar
Rewards Points: 268
I agree, it's time to replace the breaker- but in general it's helpful to know that testing load to ground vs line to ground should trip a gfi, no?
Old 04-15-2012, 07:26 PM   #10
It should, but if it fails for some reason, you've unnecessarily exposed yourself to a hazard. It's a dumb idea.
drums5 (04-16-2012)
Old 04-15-2012, 07:38 PM   #11
aDudeInPhx's Avatar
Rewards Points: 268
I agree that it isn't part of the troubleshooting process.
The Following User Says Thank You to aDudeInPhx For This Useful Post:
drums5 (04-16-2012)
Old 04-15-2012, 07:38 PM   #12
sbrn33's Avatar
Rewards Points: 3,516
I would replace the breaker, why take a chance. I would also charge $1750 to replace it. Plus my dispatch fee.
The Following 2 Users Say Thank You to sbrn33 For This Useful Post:
aDudeInPhx (04-15-2012), drums5 (04-16-2012)
Old 04-15-2012, 08:24 PM   #13
aDudeInPhx's Avatar
Rewards Points: 268
You would be holding a voltage tester in your hand at that time wouldn't you?
drums5 (04-16-2012)
Old 04-15-2012, 10:48 PM   #14
Default Safety first
No question about changing the breaker. Don't know what i was thinking in regards to safety and liability. Thanks for the wake up call.In regards to that website i mentioned testing a gfi breaker line to ground is still incorrect...no?
Old 04-16-2012, 08:14 AM   #15
Rewards Points: 1,224
Yes, the breaker needs to be replaced, but I don't see any more hazard using a voltage tester to test the operation of a GFCI than I see in using that same voltage tester to check for voltage. This assumes that your voltage testing device pulls enough current to cause the GFCI to trip. You do need voltage rated gloves to use the voltage tester in either case.
drums5 (04-16-2012)
Old 04-16-2012, 04:18 PM   #16
A wiggy from line hot to ground will trip a GFCI. Safe and effective. (The flow is MUCH greater than the 4-6ma standard though so it does NOT tell you if the GFCI trips within allowable tolerance. That is what the test button is for.)
As for the OP, your main issue is training the customer to shut the breaker off the right way.
Oh, wait, on second thought if they keep calling you to change it out when it fails let them have at it and rake in the cash.
The Following User Says Thank You to guest For This Useful Post:
drums5 (04-16-2012)
Tags
gfi breaker, gfi test button, hot tub gfi breaker
Temporarily replacing 4-pole transfer switch with 3-pole erics37 General Electrical Discussion 34 03-04-2012 11:57 PM
PLC Counter Reset Problem dronai PLCs, VFDs, Motors and Controls 10 10-30-2011 01:23 AM
power flex 4 reset? Calectrical PLCs, VFDs, Motors and Controls 1 11-21-2010 01:13 AM
Vista 50P reset? MDShunk Structured Wiring 11 03-25-2010 12:58 AM
It worked before I reset it jwjrw General Electrical Discussion 7 02-17-2010 01:52 PM