Had a "new" inspector last week. He said i had to put a 75amp or less breaker on my #2 SER feeder because he couldnt identify the lug temp rating?? Is he right?
I'm shakin it boss..I'm shakin it
Old 05-12-2013, 02:59 PM   #2
Rewards Points: 2,302
You know he is correct -- 110.14(C). I have never seen anyone get called on that. I don't know when the lugs became 75C but it seems like if the rating is 60C I begin to wonder if alum is even allowed on those lugs-- is there a rating for that.
I can't help it if I'm lucky
Lep (05-13-2013)
Old 05-12-2013, 03:03 PM   #3
Cletis's Avatar
Here is type i had in but a 90amp. I could just throw a 60 on til he leaves i guess. No markings for lug temp at all
Old 05-12-2013, 03:15 PM   #4
I was thinking main lugs on a panel-- yeah throw in a new breaker and you should be good.
Old 05-12-2013, 05:23 PM   #5
Service Call's Avatar
Rewards Points: 38
It's on the side
Service Call is online now   Reply With Quote
Old 05-12-2013, 11:33 PM   #6
Very Long Vacation
Rewards Points: 5,262
Ive been called out on it before but 75*C is ok for your breaker. Now code wise its a gray area whether you use the 60 or 75* column in the NEC.
Old 05-13-2013, 12:36 AM   #7
Rewards Points: 21,898
Pretty good percentage of the breakers I have ran into most are dual rated ( 60/75C ) so it will work but a gotcha is the rest of conductor that will fall either 60 or 75 C depending on how it ran.
SE and SER cable do come in two ratings so that part will have to be little more carefull with it.
Merci,
Marc
Old 05-13-2013, 06:31 AM   #8
Jesus Scott
electricmanscott's Avatar
Rewards Points: 232
There is more to the breaker selection for #2al ser and most installations I see are wrong. What code cycle are you on?
Old 05-13-2013, 09:10 AM   #9
child please.....
NolaTigaBait's Avatar
Rewards Points: 14
I use whichever one benefits me at the time....doesn't the 11 allow se on the 75 column?
REMOVED
Old 05-13-2013, 09:13 AM   #10
Rewards Points: 150
Yes, as long as it's not in contact with insulation.
AFAIK, it was only during the 2008 cycle that you had to use the 60 degree column.
highleg is offline   Reply With Quote
OCPD Sizing Helivice General Electrical Discussion 15 07-27-2012 07:27 PM
25 ocpd on #12 thhn Cletis General Electrical Discussion 20 01-10-2012 10:01 PM
When is an OCPD not an OCPD? Electron_Sam78 NEC Code Forum 25 08-24-2010 05:39 PM
2/0 - 100 OCPD Adapter Mike Guile Commercial Electrical Forum 9 02-28-2010 04:43 PM
Ocpd and hvac- need clarification SparksNY General Electrical Discussion 10 11-12-2007 10:36 PM