208Vac to 120Vac Industrial Control transformer? - Electrician Talk - Professional Electrical Contractors Forum
Old 02-07-2015, 07:52 PM   #1
Rewards Points: 6
Default 208Vac to 120Vac Industrial Control transformer?
Hello, I've got a question about an 'Industrial Control Transformer'.
There's an elevator which is fed from a 120/208Vac panel, with a 60 amp 3 phase disconnect in between. The 3 phases come in and feed the motor circuit. From the top of that circuit, two lines tap off and go to 2 - 1.6A fuses and then to the 0.15kVA - 208Vac to 120Vac 'Industrial Control Transformer'. (which is single phase)
Anyone have an idea why on earth the installers didn't just bring a 15amp line to neutral circuit from the panel to the 1.6amp fuses to feed the control circuit? Is it an elevator code situation where the entire system must be able to be de-energized with one disconnect? That's all I can really think of.
unlucky.break is offline   Reply With Quote
Old 02-07-2015, 08:06 PM   #2
Rewards Points: 1,298
Yes, the disconnect shuts off everything so you don't have to find a breaker to also shut off if you pulled in a separate 120 ckt.
Mich drew is offline   Reply With Quote
The Following User Says Thank You to Mich drew For This Useful Post:
glen1971 (02-13-2015)
Old 02-12-2015, 01:38 PM   #3
Rewards Points: 6
Thank you for confirming my suspicions Mich.
Old 02-12-2015, 02:32 PM   #4
Rewards Points: 2,080
they just didn't run a 4 wire cable, they could have run the 60 amp with a neutral then 1 leg go to a control fuse, no need for separate 120v circuit.
oliquir is online now   Reply With Quote
Old 02-12-2015, 03:07 PM   #5
just the cowboy's Avatar
Rewards Points: 148
Default Maybe 240 volt also
The elevator may have dual voltage ratings 480 volt or 240 volt, then they would need the xformer so they probilaly build them all the same.
Old 02-12-2015, 03:11 PM   #6
Rewards Points: 1,004
xpertpc is offline   Reply With Quote
Old 02-12-2015, 08:53 PM   #7
Rewards Points: 1,464
We can only bring power to the elevator room and the Otis guys take it from there. Usually 480 3 and a 120 fusible disconnect for cab lights.
The Following 2 Users Say Thank You to bobelectric For This Useful Post:
glen1971 (02-13-2015), Shockdoc (02-13-2015)
Old 02-13-2015, 01:44 PM   #8
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
On my end they want a second 120 volt circuit ran through the disconnect for service gfci receptacles in machine room and shaft.
Best U.S. City for Entry into Field of Industrial Control Systems. theForce PLCs, VFDs, Motors and Controls 6 06-10-2014 11:44 PM
Convert UPS Output Power Jack from 208vAC to 120vAC Question newbDan General Electrical Discussion 5 07-30-2013 06:59 PM
Industrial Control Work Chat42 New Member Introductions 10 05-14-2012 06:40 PM
Insurance for doing industrial control work. Sparkee Business, Marketing, and Sales 6 07-20-2011 11:33 PM
Industrial Control Panels - Installation michelebacocchia NEC Code Forum 16 08-26-2010 10:25 AM