240V single phase circuit with unequal length leads - Electrician Talk - Professional Electrical Contractors Forum
Closed Thread
Old 02-18-2015, 06:35 AM   #1
Default 240V single phase circuit with unequal length leads
Hello all
I am wiring an invertor-type mini-split AC system in a residence requiring a 240v 15a breaker.
Due to the topography of the house, running an additional circuit from the breaker would pose some difficulty and substantially increase the cost of the install.
I have 2 existing 120v 20a single phase circuits supplying outlets in the area (not in the same conduit) and am interested in removing the breakers from these 2 circuits and replacing them with a double pole 240v 15a circuit breaker (with common trip) and tapping these for use with the minisplit. The neutrals for each circuit are tied in to the same block at the service entrance breaker box and there are no sub-panels.
1) My understanding is that a multipole breaker with common trip will allow full rated amperage through any pole as long as combined amperage from all poles does not exceed rated amperage. i.e. in this case if 1 pole was pulling 0 amps the other pole can pull the full 15 amps without the breaker cutting the circuit.
Is this correct?
2) I know that magnetic interactions between oppositely phased leads within the same conduit act to decrease heat buildup. This would not be the case here. However, I would be de-rating my circuit.
Will this be a problem?
3) I estimate that the wire runs for each of the 2 circuits are approximately 50-75 feet long but are unequal length.
Will unequal length leads cause phase shifting problems?
4) Last but not least, is this expressly prohibited by the NEC?
Thanks in advance for any and all input!
aubreyj is offline
Old 02-18-2015, 06:52 AM   #2
Barjack's Avatar
Rewards Points: 280
What has your electrician said?
Barjack is offline
Old 02-18-2015, 06:53 AM   #3
Very Long Vacation
Rewards Points: 5,262
IBTL
If this is in conduit there is no way to fish 2 extra 14 guage wires?
meadow is offline
Old 02-18-2015, 07:13 AM   #4
Rewards Points: 1,830
Dennis Alwon is online now
Closed Thread
480V - 3 phase circuit - Split into 3 single phase feeds justonespark NEC Code Forum 2 11-13-2014 05:52 PM
Single & Three Phase Motor Loads on Three Phase Circuit josefbartos NEC Code Forum 4 09-05-2010 02:31 PM
Voltage Reading on a single phase 120Vac Circuit rarivera General Electrical Discussion 3 08-04-2010 06:18 PM
no voltage between legs of a 230v single phase circuit brandonmcginnis Residential Electrical Forum 9 02-14-2010 05:26 PM
Grounded 240V single phase zgozvrm General Electrical Discussion 5 06-20-2009 05:27 AM