2hp motor over current - Electrician Talk - Professional Electrical Contractors Forum
Closed Thread
Old 04-13-2013, 02:24 PM   #1
xsryman's Avatar
Default 2hp motor over current
Is it normal for a motor to ever run at above its nameplate value. Its FLA is 5amps and across the line it is pulling 6.4-6.8. It keeps tripping out the drive that is running it. The motor is brand new btw.
xsryman is offline
Old 04-13-2013, 02:40 PM   #2
Awg-Dawg's Avatar
Rewards Points: 726
Originally Posted by xsryman View Post
Its FLA is 5amps and across the line it is pulling 6.4-6.8. The motor is brand new btw.
If seen where the wrong size pulley is put on, that could cause the amperage to be higher.
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline
Old 04-13-2013, 02:43 PM   #3
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
99.5% of the time high motor current is because of a stubborn connected mechanical load. What is this thing driving?
Always wear your gloves.
Big John is offline
shocksystems (03-07-2015)
Old 04-13-2013, 02:48 PM   #4
xsryman's Avatar
Its pumping milk out of a collection tank on a dairy. It has a pump connected to the cface
xsryman is offline
Old 04-13-2013, 02:58 PM   #5
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Is this a replacement for the same sized motor? Totally new installation? What changed?
Big John is offline
Old 04-13-2013, 03:16 PM   #6
xsryman's Avatar
Its was running on an old AC Tech drive that died. Replaced it with an ATV312 and it ran about 15hrs then tripped out on o.cf-(overcurrent fault). So after running in bypass across the line the motor spit out a spark and so it was replaced then put back on the drive and has ran fine for 4-5days. Now it is tripping on o.cf and even after resetting the vfd it goes right into o.cf fault upon start up. So the motor is back on bypass contact or but is pulling 6+ amps. Gotta be something upstream? Maybe needs a line reactor? Maybe just a detective drive?
xsryman is offline
Old 04-13-2013, 05:41 PM   #7
8V71's Avatar
Rewards Points: 2,900
My guess would be a mechanical issue also. Pump bearings could be starting to seize or something is restricting the product flow. If you can't find any obvious issues maybe the original motor was a bit undersized to begin with but the old drive could handle the current better or had less sensitive protection.
8V71 is offline
Old 04-13-2013, 05:46 PM   #8
Electron Flow Consultant
sparky970's Avatar
Rewards Points: 992
If you must keep it running until it's convenient to fix, more than likely the pump, you could close the discharge valve a little to bring the current down.
sparky970 is offline
Old 04-13-2013, 05:50 PM   #9
BBQ
Salty Member
BBQ's Avatar
As long as it is a centrifugal pump restricting the flow will reduce the current.
I agree.
BBQ is offline
The Following 2 Users Say Thank You to BBQ For This Useful Post:
micromind (04-13-2013), wdemos (04-13-2013)
Old 04-13-2013, 06:27 PM   #10
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Most likely scenario from this is that your load is changing, causing the original motor to go into overcurrent. It was put in bypass, and with no overload protection it ran to overheat and insulation failure. The replacement motor went in, and is now seeing the same overload condition, and will also eventually fail if run at that amperage.
The two big questions are: Is the original drive failure related? And what is causing the change in mechanical operation of the pump? I agree with other posters that restricting the pump volume should lower your pump current.
Why is this normally VFD driven if it can run across the line?
Big John is offline
Old 04-13-2013, 06:45 PM   #11
xsryman's Avatar
Speed regulation is needed to get the best cooling as the milk comes from the receiver tank and passes through the chiller. Its not a centrifugal pump so there are no bearings to wear. It has an impeller directly on the motor shaft. It can run across the line but it is not ideal. Only for bypass situations. There is another set up identical to this one right next to it that is pulling the proper amp draw. There is just something about this setup. Checked for phase imbalances at the I/p and o/p. Everything checks out. Just high amp draw at the output.
xsryman is offline
Old 04-13-2013, 06:56 PM   #12
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Can you post a model# or pictures? I'm having a hard time imagining this, and when I Google it I'm getting pictures of positive-displacement pumps, which are actually contrary to what we've said here and can't tolerate any discharge restriction.
Big John is offline
BBQ (04-14-2013)
Old 04-13-2013, 07:15 PM   #13
zap
tates1882's Avatar
Rewards Points: 1,076
What voltage? 1 or 3 phase? Is the fault contained to one phase or all three?
tates1882 is offline
Old 04-13-2013, 07:26 PM   #14
8V71's Avatar
I think it's still centrifugal but a specialized SS unit with no external pump bearing.
8V71 is offline
Old 04-13-2013, 07:31 PM   #15
To answer your original question, sometimes yes a motor can run over its nameplate rating depending on the motor service factor.
But not that high of a percentage as you are seeing.
The NEC is the MINIMUM standard.
Bbsound is offline
Old 04-13-2013, 08:08 PM   #16
Rewards Points: 3,126
2HP, 5 amps; it's either 208 or 240 3.
I'd also be willing to bet that all 3 phases are seeing overcurrent.
I agree with the others, it's not a motor issue, most likely mechanical.
If the impeller is connected directly to the shaft, it's most likely a centrifugal pump. Is the motor actually a C face or is it a J frame? Like 56J.
As noted, if it is indeed a centrifugal pump, restricting the discharge will lower the current. If it's just about any other type, restricting the discharge will cause the current to rise.
Are the suction and discharge pressures the same on both pumps? If so, look at mechanical issues. If not, then look at fluid issues.
micromind is offline
Old 04-13-2013, 08:18 PM   #17
xsryman's Avatar
It is 2hp 240v 3ph. I guess I will have to do some more mechanical investigation on Monday.
xsryman is offline
Old 04-13-2013, 08:19 PM   #18
xsryman's Avatar
Oh and its 56c. Not jet pump.
xsryman is offline
Old 04-13-2013, 08:31 PM   #19
If it's 56C, then more than likely there's a bearing in the pump casing. Probably only one, but most 56C pumps have a bearing, even though they are directly coupled to the shaft.
Old 04-13-2013, 09:24 PM   #20
zap
tates1882's Avatar
A Mis alignment when mounting the motor can produce ol fault. Also a restriction in the chiller plate could be the problem. Is it a plate exchanger or a tank chilling system?
Closed Thread
exam question: motor over-current protection stonewhite General Electrical Discussion 2 12-06-2012 11:58 PM
Motor current unbalance? tates1882 PLCs, VFDs, Motors and Controls 11 08-22-2012 09:39 PM
3 phase motor current readings farlsincharge PLCs, VFDs, Motors and Controls 13 02-24-2011 04:18 AM
How to calculate No load current and No load torque in DC Motor AMIanna General Electrical Discussion 3 05-21-2010 10:15 AM