#3 feeding 1/0 Voltage drop for entire run? - Electrician Talk - Professional Electrical Contractors Forum
Old 11-05-2012, 06:17 AM   #1
Aegis's Avatar
Rewards Points: 1,732
Default #3 feeding 1/0 Voltage drop for entire run?
I have a 100A service. In the gutter/splitter I have #3s as the feed. This splitter feeds a 100A panel and a 100A disconnect. In the 100A Disconnect I'm using 1/0 for derating and voltage drop. So basically I have 10ft of #3 feeding 1/0. I've heard some say the entire run should be the same but the way I'm looking at it is I'm keeping what I'm getting into the 100A disconnect. Thoughts?
Aegis is offline   Reply With Quote
Old 11-05-2012, 06:34 AM   #2
Rewards Points: 14,714
After reading your post 3 times, I think maybe, if I understand what you are saying, I agree. I reserve the right to change my mind as details are explained.
Old 11-05-2012, 06:38 AM   #3
butcher733's Avatar
Rewards Points: 798
whats on the load side of the disconnect and how far away is it? It must be pretty far to go three sizes up. I think your good as far as the NEC is concerned.
I'll take therapists for $400.
butcher733 is offline   Reply With Quote
Old 11-05-2012, 06:47 AM   #4
Aegis's Avatar
The 100A disco is feeding a panel that's 200ft away and I'm calculating for 80A. There's also some temp derating going on but to my understanding doesn't stack on top of the voltage drop calculation.
Old 11-05-2012, 06:55 AM   #5
k_buz's Avatar
Does the CEC limit voltage drop?
k_buz is offline   Reply With Quote
Old 11-05-2012, 06:56 AM   #6
Hippie's Avatar
Rewards Points: 570
1/0 seems a little large for the load/distance. However there is nothing wrong with upsizing just the long portion of the run, its done all the time
Hippie is offline   Reply With Quote
Old 11-05-2012, 07:00 AM   #7
Rewards Points: 1,224
You just add the two voltage drops together to get the total. I get 0.4 volt drop on the 10' of #3 with an 80 amp load and 3.5 volts on the 200' of 1/0.
Old 11-05-2012, 07:30 AM   #8
mbednarik's Avatar
Rewards Points: 1,126
don't forget to upsize your EGC also.
The Following User Says Thank You to mbednarik For This Useful Post:
Aegis (11-05-2012)
Old 11-05-2012, 07:47 AM   #9
Rewards Points: 1,000
I think it would look better if you brought the 1/0 to whatever termination point it needs to go without splicing but I think its legal either way.
I did one for the dept of transportation where they specified #8 copper for a 15amp circuit which seemed big except the homerun was over 1200 feet (120 volts).
if i'm not mistaken, z*i=voltage drop
200ft x 2 = 400ft
z = .13 per 1000 ft (table 9), .00013/ft
400ft * .00013 z/ft = .052 z
.052 z * 80 amps = 4.16 v voltage drop
uconduit is offline   Reply With Quote
Old 11-05-2012, 09:28 AM   #10
Aegis's Avatar
Not sure what you mean.
Old 11-05-2012, 09:34 AM   #11
Aegis's Avatar
200ft x 2 = 400ft
I got something similar to what Don got, close to 3.5v. I've used table D3 in the past and also this website
http://www.csgnetwork.com/voltagedropcalc.html
single service drop feeding two meter sockets skunkyganja General Electrical Discussion 13 08-09-2011 09:23 PM
single service drop feeding two meter sockets skunkyganja General Electrical Discussion 11 08-09-2011 11:32 AM
Voltage drop under load on A leg/voltage rise on B leg Fowlerfellow General Electrical Discussion 17 06-03-2011 01:42 PM
Voltage Drop Zparme General Electrical Discussion 9 04-06-2011 06:08 AM
Voltage Drop john salyards General Electrical Discussion 3 02-17-2008 04:43 PM