Could someone please confirm my understanding of 3 phase generators power output. I'm in Australia so all calculations are in 240v
A 30kVA generator in total can provide a theoretical maximum of 30,000/240 = 125A which would be 41.6A per phase? Using a power factor or 0.8 we get a total of 125*0.8 = 100A or 33.3A per phase. So a 30kva generator is capable of running 3x32 amp distribution boxes? Cheers |
Join the #1 Electrician Forum Today - It's Totally Free! ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free! |
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task! |
Sponsored Links | |||
Advertisement |
#2 |
Rewards Points: 26,360
In the real world, the alternator is loaded by real loads.
Distribution boxes are NOT real loads. They are distribution nodes. You have to ask yourself: "What are the actual net loads to be served?" This calculation is termed a load-calc... what else? Set-up a spread sheet program and punch in the numbers. You'll want to look at actual Watts as well as keep an eye on Power Factor. ( If poor, the latter doesn't load up the alternator, but does figure in conductor sizing. ) Last edited by telsa; 11-08-2018 at 12:10 AM. |
#3 |
Thanks
So assuming unrealistic ideal loads I'm correct? Just after a sanity check that I'm not out by a factor of 3. |
Advertisement |
#4 |
German Spy
Rewards Points: 3,991
Huh?
I see nooothing, I was not here. I did not even get up this morning. |
#5 | ||
Rewards Points: 2,985
![]() Quote:
EDIT: I just realized I may be misreading this. Is the 240V L-L or L-N? Last edited by AK_sparky; 11-08-2018 at 01:47 PM. |
#6 |
German Spy
240v x 1.73 x 33.3a= @13KW
brian john likes this.
#7 |
Rewards Points: 1,750
30X1000/240x1.732= 72.23 amps
30X.8/x1000/240X1.723= 57.78 amps or somewhere close to that
Ah, but I was so much older then, I'm younger than that now Last edited by brian john; 11-08-2018 at 08:32 PM. |
Tags |
3 phase, generators, load calculation ![]() |
Thread Tools | |
Display Modes | |
Thread | Thread Starter | Forum | Replies | Last Post |
240v 3 phase corner grounded delta and 240v single phase loads | snadeau | Commercial Electrical Forum | 2 | 08-30-2018 08:28 PM |
Electrical Theory question.. phase balancing | Jmp2016 | General Electrical Discussion | 8 | 10-11-2017 01:40 PM |
Phase to Phase Voltage Wire to Phase to Neutral Load | killabeez87 | New Member Introductions | 7 | 02-24-2017 10:30 AM |
3 Phase / 1 Phase question | J91 | Commercial Electrical Forum | 16 | 10-23-2016 05:25 AM |
3 phase to single phase | te12co2w | PLCs, VFDs, Motors and Controls | 62 | 03-14-2016 11:47 AM |