Originally Posted by Ultrafault View Post
My boss asked me a question, and I could not satisfactorily explain what would happen if you hooked a three phase transformer to a single phase supply. For the sake of this conversation we assumed the transformer would be delta 240 to wye 480 as the suggestion was for step up. I told him it would be horribly inefficent but to be honest I was only using supposition.
Could some of you guys enlighten me about the physics of this situation?
Could you use this setup as a single phase transformer?
What output could you expect at the secondary conductors?
Would a delta delta transformer provide you with different results?
If you connected 240V to H1 H3 , you would need to ground H2
The result on Wye or Delta would be the same, because the vectors are 180˚ apart. You would have 480V on X2 to X0 , and 240 on both X1 and X3 to X0
Although in Delta secondary you would have 480V on X1 to X3 and 240V on X2 to X1 and X3
Made a quick drawing to show it better.
The thing to remember is that the "wye" output is NOT a Y ... ie they are not 120˚ vectors, so they simply add up.
**edit** added dwg ... note, two H1's on primary ... one should be H3
micromind, TGGT and Ultrafault like this.
Old 06-12-2016, 12:10 PM   #22
Rewards Points: 3,932
Since it is a step up transformer, wouldn't the 240 vac go onto X1 and X3, and the 480 would be on the high side?
This might do in a bind, but I'm thinking the correct transformer should be installed as soon as possible....
emtnut likes this.
Old 06-12-2016, 12:18 PM   #23
Band Member
emtnut's Avatar
Yes, it should ! I was still on my first coffee
glen1971 likes this.
Old 06-12-2016, 12:35 PM   #24
Rewards Points: 3,052
The X windings on a 240∆ - 277/480Y transformer are 277 volts, not 480. 480 is derived from the Y connected 277 volt windings having 120 of phase shift.
emtnut likes this.
Old 06-12-2016, 12:47 PM   #25
Band Member
emtnut's Avatar
Yep !
So you would have 277V , and 138.5V for that tx .... think that's what you said in your earlier post
micromind (06-12-2016)
Step Up single phase transformer mr_electrician Services and Service Equipment 4 05-25-2016 06:29 AM
3 phase to single phase te12co2w PLCs, VFDs, Motors and Controls 62 03-14-2016 11:47 AM
220 single phase to 3 phase? TechieBecky Canadian Electrical Forum 16 02-19-2016 04:46 AM
3 phase panel (208) used for single phase (240)? CEC09 Canadian Electrical Forum 3 02-10-2016 03:35 AM
Can be both a three or single phase motor just the cowboy General Electrical Discussion 2 01-21-2016 11:36 AM