Hypothetical question ,
If 480v shorted out in underground PVC, would the explosion be large enough to damage conduit unusable ?
mpcxl is offline   Reply With Quote
Old 03-17-2019, 08:43 PM   #2
Rewards Points: 16,462
For the Hypothetical answer .,,
all it depending on the AIC rating and size and numbers of conductors are involded in this mess.,, but my answer is oui it will if large enough a expolison.
and which type of OCPD you are using and if that faulted by uility side it will be much worst than load (customer side) fuse useally can clear the fault pretty quick but not always. but breakers that is depending on the setting.
Signal1 likes this.
Old 03-17-2019, 08:55 PM   #3
mpcxl's Avatar
Rewards Points: 54
#6 or 8 on load side of breaker but before fuse. It’s possible circuit is on a oversized breaker and uses fused over current protection to protect site lighting fixtures
All signs point to short/damaged circuit and damaged/broken pvc
Plan on cutting road , but just wondering if even possible to investigate further
Old 03-17-2019, 09:18 PM   #4
Okie .,, now this getting some good details coming out on this one.,,
first of all what size breaker did ya see it ?
what total load for this circuit and what type of luminaire it is running ?
Fuse size at the luminaire post ?
I know you mention 6 or 8 awg main conductor size but EGC what size it is ? I betcha it was #10 awg if that was the case you will know why real quick espcally with long run for parking lot luminaires.
how long the run it is ? ( in feet or meters )
The more info you posted the more easier we can give you the answer.
Old 03-17-2019, 09:35 PM   #5
mpcxl's Avatar
Rewards Points: 54
Don’t have any load calcs atm. Fuses are rated for 20A. Typical 400W MH ballast combo fixture
The egc was the same as conductors so #6 or 8. I think they’re #8. It’s the end of line for the run. So between light poles it’s ~100’.
I should add Ends of wires are charred and I cant get a fish through.
480v explosion damage underground PVC conduit-e1751427-4b04-4ac9-82ad-1e78ee44081b_1552872689904.jpg
480v explosion damage underground PVC conduit-a4288b57-6a79-4714-9cb4-81efee695ffa_1552872759965.jpg
Old 03-17-2019, 10:05 PM   #6
Band Member
emtnut's Avatar
Rewards Points: 420
We use 347V for lighting up here, and no... it doesn't explode.
If you had a short hot enough, it could melt the pvc and screw up your duct. But for the most part, if you can't remove the conductors or fish in new ones it's just because the duct is collapsed.
samgregger likes this.
Old 03-17-2019, 10:39 PM   #7
Rewards Points: 1,266
Had a 3 phase 480 WYE fault underground blew up a toilet (would have killed anyone on the can, knocked down 4 walls 3-drywall metal stud 1-cinderblock 25' tall.
SO YES
Shut the gym down for a month.
CoolWill likes this.
Old 03-17-2019, 10:59 PM   #8
Band Member
emtnut's Avatar
Rewards Points: 420
SO YES
All on #8 or #6 ??
Old 03-17-2019, 11:42 PM   #9
Originally Posted by emtnut View Post
All on #8 or #6 ??
3-sets of 750 kcmil al.
emtnut likes this.
Old 03-18-2019, 12:23 AM   #10
HertzHound's Avatar
Rewards Points: 238
Is it possible the conduit was damaged years ago. Maybe put a nick in the wire. Took all this time to finally blow. Probably had mud seaping in the whole time.
Old 03-18-2019, 06:04 AM   #11
Rewards Points: 694
The inside of the conduit will be sticky from the smoke and the conduit will have a real rough area where the wires burnt in the best scenario. In the worst the conduit will have collapsed.
Like hertzhound pointed out the wire burning up may have been the result of a failed conduit which would have made a re-pull impossible before the wire added to the problem.
I would give it my best shot to get a fish tape soaked in lube through the conduit then call it a day and consider replacing some if not all of the conduit. No one wants to cut up a road so i would probably dig up the conduit at the edge and see if the section under the road is usable.
Old 03-18-2019, 08:12 AM   #12
Rewards Points: 10,131
If they’re unfused service conductors in PVC conduit, you’re trenching.
brian john likes this.
Old 03-18-2019, 08:31 AM   #13
Rewards Points: 792
Possible yes...probable no...I pulled shorted out 15kV cables many times and pulled in new cables no problem.
Blow and Rod the conduit...
For parking lot lights i wouldn't think twice about just trying to pull new in the same conduit.
You could always just lay burnt conductors along conduit path and just dig that section you are worried about.
Tonedeaf is online now   Reply With Quote
Old 03-18-2019, 09:17 AM   #14
mpcxl's Avatar
Rewards Points: 54
Used a locator and fish tape. Found the break where the fish gets jammed up. Unfortunately, it’s rightunder the road.
Going to try a few more things, mainly vac to suck and blow, before we go ahead and cut road.
Old 03-18-2019, 11:44 AM   #15
Band Member
emtnut's Avatar
Rewards Points: 420
If you haven't already, try fishing from the other end ... sometimes you get lucky.
We've had 50/50 luck with hydrovac trucks too. But if their hose gets stuck, you just bought it !!
Old 03-18-2019, 11:45 AM   #16
Band Member
emtnut's Avatar
Rewards Points: 420
Yep, that would make the 'earth shattering ka-boom ! '
Old 03-18-2019, 01:43 PM   #17
Rewards Points: 412
lots of steamer trucks have cameras they can send down if the conduit is 1" or bigger.
mitch65 is offline   Reply With Quote
Old 03-18-2019, 05:17 PM   #18
Semper Fi
Southeast Power's Avatar
Rewards Points: 7,376
My guess is that something happend to the conduit and it injured the insulation.
Old 03-18-2019, 08:19 PM   #19
mpcxl's Avatar
Rewards Points: 54
Before and after. Charred pipe underground
480v explosion damage underground PVC conduit-5c24b82e-baa7-45c4-8381-4f3dc91aed5e_1552954659338.jpg
480v explosion damage underground PVC conduit-d58036ac-35ff-458b-bc8b-a3d7a03c310b_1552954680489.jpg
480v explosion damage underground PVC conduit-e3f63b0f-c0e7-405c-a2d4-0c2a275226c2_1552954717159.jpg
Old 03-18-2019, 08:54 PM   #20
CoolWill's Avatar
Rewards Points: 634
Welp.... Turns oit that electricians path asphalt better than road crews too. Is there anything we can't do?
I'm With Her! Hillary 2016
What type of wire do you use for underground conduit? NDC Canadian Electrical Forum 19 07-21-2018 07:05 PM
can anybody explain about what is" underground run"? mike883 Canadian Electrical Forum 5 09-27-2017 10:38 PM
Whats the most common wire for underground conduit? Canaduh Canadian Electrical Forum 12 07-27-2017 12:23 PM
Suspending security camera from conduit ElectMe NEC Code Forum 8 02-19-2017 04:20 PM
Underground Conduit: IMC or PVC? itiselectric General Electrical Discussion 16 03-14-2016 11:55 PM