6/2 mc what am i missing? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree18Likes
Old 07-08-2019, 12:01 PM   #1
WPNortheast's Avatar
Rewards Points: 168
Default 6/2 mc what am i missing?
Hey everybody I'm trying to figure out what's going on with this scenario. Only one out of four of my supply houses carry is 6 / 2 MC. The other three claim that it's very unusual to need. I need this cable for a 4 horsepower condenser on a walk-in cooler and a electric air curtain above an entry door. The air curtain has a 36 amp element and a 1.4 amp motor at 208 volts. The spec on the cooler condenser is MCA 45, MOP 50, RLA 23.4
Am I confused about something due to the large amount of residential that I do? I was thinking 6 gauge line conductors were in order... breakers are bolt on BR
WPNortheast is offline   Reply With Quote
Old 07-08-2019, 12:06 PM   #2
Rewards Points: 168
The condenser is single phase but it actually the air curtain is 3 phase. Still same conductor ampacity applies.
6/2 mc what am i missing?-20190708_120251_1562601968797.jpg
Old 07-08-2019, 12:23 PM   #3
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
AC90 (what we get in Canada instead of MC) either doesn't come in 6/2, or is exceedingly rare. I've always had to buy 6/3. I guess most applications for this wire size are either split single phase (120/240) or 3 phase, so manufacturers don't bother making a 2 conductor version.
Old 07-08-2019, 12:27 PM   #4
Rewards Points: 15,873
3/4" pvc. #6 wire. Forty five minutes and done.
Bird dog likes this.
Old 07-08-2019, 12:27 PM   #5
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
So are there two connections to be made or just one? It looks like just one, which would be 3 phase anyway, so 6/3 and a 3p 50A breaker is what you want.
99cents and CoolWill like this.
Old 07-08-2019, 12:39 PM   #6
CoolWill's Avatar
Rewards Points: 2,012
Problem solved. 6-3 is the answer.
I'm With Her! Hillary 2016
Old 07-08-2019, 12:57 PM   #7
Bird dog's Avatar
Rewards Points: 1,318
It sounds like it is two separate pieces of equipment which would require two separate ckts.
1) Air curtain with heater, #6 & 50amp breaker
2) Condenser, #6 & 50amp breaker
Flex into them with sealtight.
99cents and telsa like this.
Old 07-08-2019, 01:00 PM   #8
Bird dog's Avatar
If it's MC shouldn't it be 6-3 with ground?
Old 07-08-2019, 01:17 PM   #9
CoolWill's Avatar
I've never bought 6-3 that didn't have a ground.
electricguy and B-Nabs like this.
Old 07-08-2019, 01:34 PM   #10
Rewards Points: 168
Apparently i wasn't clear this is a matter of if due to the current required, is 6 truly necessary? I believe it is. To those who imagine any form of conduit with conductors would be easier than pulling an MC cable in the area I'm working, not a chance. PVC with THHN inside would take anybody at least half a day I don't care how sloppy it is. Even plastic seal tight with number six is inside would cost over double of what my one supplier cost for a cut of 6 / 2 MC. Thanks anyway though
Old 07-08-2019, 03:36 PM   #11
HertzHound's Avatar
Rewards Points: 648
If all the terminals are rated for 75c you could get away with #8 copper. I would just go with the 60c column and use #6
“Why say lot words when few words do trick”
Old 07-08-2019, 07:04 PM   #12
Rewards Points: 236
How are you using 6/2 for a 3 phase circuit?
Old 07-08-2019, 07:17 PM   #13
CoolWill's Avatar
Minimum circuit capacity is for both the single phase and 3-phase currents combined.
Old 07-08-2019, 08:21 PM   #14
Rewards Points: 168
The condenser is 1p. The air curtain is 3p. Come on
Old 07-08-2019, 08:54 PM   #15
Rewards Points: 168
Thanks everyone for the responses the answer was simple, once i got home and thought about it. 6/2 is rare because mc that size is for commercial and commercial wiring in that size is typically 3 phase...odd ball that the condenser is 1 phase.
Old 07-08-2019, 08:58 PM   #16
DashDingo's Avatar
Rewards Points: 14
Why wouldn’t 8 gauge work? Even at 125%.
MC is sized in the 75 column.
8/3 MC is common,
Three 8’s and a 10 ground baby.
DashDingo is offline   Reply With Quote
Old 07-08-2019, 09:26 PM   #17
Bird dog's Avatar
Could you cite a code reference for that please?
99cents likes this.
Old 07-08-2019, 09:32 PM   #18
Cow
Rewards Points: 4,532
330.80--->310.15
We use the 75 degree column for MC, same as THHN.
That would be getting #8 MC, not #6. This isn't 60 degree column Romex.
HackWork likes this.
Old 07-08-2019, 09:40 PM   #19
Watt Pusher
B-Nabs's Avatar
Rewards Points: 466
So is there another nameplate for a condenser you didn't post? The nameplate you posted shows a 3 phase heater (the bulk of the load) and a small single phase motor.
Old 07-08-2019, 09:45 PM   #20
DashDingo's Avatar
Rewards Points: 14
330.80