6 throws of the hand - Electrician Talk - Professional Electrical Contractors Forum
Old 10-05-2012, 02:32 PM   #1
Rewards Points: 180
Default 6 throws of the hand
I have a 1200 amp panel with 6 200 amp breakers and no main. I took one of the breakers out and added a 400 amp panel with a main next to it. Inspector said he might not pass it because someone could come along a put that 200 amp breaker back in. Sounds ridiculous to me
big vic is offline   Reply With Quote
Old 10-05-2012, 02:35 PM   #2
backstay's Avatar
Rewards Points: 296
Somebody would need to file for an inspection then and would get failed on it.
The Following 4 Users Say Thank You to backstay For This Useful Post:
BBQ (10-05-2012), Bbsound (10-05-2012), davis9 (10-05-2012), Hippie (10-05-2012)
Old 10-05-2012, 02:41 PM   #3
Going_Commando's Avatar
Rewards Points: 1,620
Exactly. The code isn't designed to include future intent. The AHJs aren't pre-crime, they are supposed to look at the installation, decide if it passes or not, and let the chips fall as they may.
Old 10-05-2012, 02:48 PM   #4
Rewards Points: 2,204
Inspector has no right to fail it based on "what if". It would be the next guys problem not yours. Good luck
I can't help it if I'm lucky
Old 10-05-2012, 03:10 PM   #5
Surge03's Avatar
Rewards Points: 290
Correct inspector can not fail what happens in the future,inspector sound ridiculous to me.Its like installing a dedicated 120 volt circuit for a microwave and the inspector failing it because some1 could tap into it in the future LOL.
Surge03 is offline   Reply With Quote
Old 10-05-2012, 03:40 PM   #6
erics37's Avatar
Rewards Points: 642
The above posts are all true, but what if you wind up being the guy that has to go in later when they want another breaker installed in the empty space?
Old 10-05-2012, 03:52 PM   #7
denny3992's Avatar
Rewards Points: 2,014
Then quote them to add a disco infront of the mb
denny3992 is offline   Reply With Quote
Old 10-05-2012, 04:22 PM   #8
inform them that the NEC does not allow it.
The NEC is the MINIMUM standard.
Bbsound is offline   Reply With Quote
Old 10-05-2012, 04:38 PM   #9
backstay's Avatar
Rewards Points: 296
Take an existing 200 and sub in another panel.
Old 10-05-2012, 05:10 PM   #10
Rewards Points: 504
I don't see the problem with someone coming back in and changing that new 400A back to 200A (other than it being a dumb ass thing to do). What does that have to do with the 6-hand rule? Still 6 main breakers.
The 200A breaker would likely niusance trip if it has a 400A fully loaded panel down stream, but that still has zero relationship to the 6-hand rule.
Old 10-05-2012, 05:15 PM   #11
BBQ
Salty Member
BBQ's Avatar
The spot where the 200 was is now empty, the inspector is worried someone might put it back for a total of seven breakers.
That said, the inspector is out of line but should be much more concerned with the size of the service conductors and the total calculated load.
Old 10-05-2012, 05:18 PM   #12
220/221's Avatar
Rewards Points: 4,274
I was once required to take the bus clip hardware out of a service section for the same reason. Someone else may reinstall a switch. I was going to point out that someone could easily put the hardware back in but I figured it was a good enough compromise and only took a few minutes.
The engineer missed it, the estimator missed it and I missed it on the installation but the inspector caught it.
Old 10-05-2012, 07:50 PM   #13
erics37's Avatar
Rewards Points: 642
It was a rhetorical question you guys
Old 10-05-2012, 07:59 PM   #14
cog
stuiec's Avatar
Rewards Points: 1,292
Just how is it that you are replying in a thread titled "6 Throws of the Hand" without a single reference to your.....er.........other hobby??
Old 10-05-2012, 08:07 PM   #15
erics37's Avatar
Rewards Points: 642
Because I do that so often it takes way more than 6 throws.
The Following User Says Thank You to erics37 For This Useful Post:
stuiec (10-05-2012)
Old 10-05-2012, 09:51 PM   #16
Very Long Vacation
Rewards Points: 5,262
As long as the load calcs are below 1200 and its still 6 throw there is absolutly nothing that is of concern.
Old 10-05-2012, 10:10 PM   #17
Rewards Points: 1,554
Can you not put the 200a breaker back in and take the feed
for the other distro thru it !
I know its overdoing it but then he can't complain about someone
using the vacant spaces.
Old 10-05-2012, 10:21 PM   #18
kbsparky's Avatar
Rewards Points: 1,000
Originally Posted by Going_Commando View Post
Exactly. The code isn't designed to include future intent.....
I disagree here. What about section 404.2(C) ??
The informational note clearly states that requirement is for (future) use ...
This is but one instance where the Code can and does try to predict future installation and requires modification today for may be tomorrow ...
-KB