8 AWG grounding conductor on Spa - Electrician Talk - Professional Electrical Contractors Forum
Like Tree4Likes
Old 06-18-2019, 07:03 AM   #1
WPNortheast's Avatar
Rewards Points: 168
Default 8 AWG grounding conductor on Spa
Hey everybody. I've got a spa install where the requirements are 50 amp 240 volt 4 wire with and 8 AWG grounding conductor required. How do you fellas skin a cat like this? My first thought was to run 2 2 2 4 scr to the main panel and put a 12 space main lug by the entrance to the crawl space. Then run sealtite with the necessary conductors from a 50 amp breaker in the Sub, to the outdoor GFCI disconnect. Then from the disconnect to the spa. Is this Overkill and is there an easier way? Or should I roll with this. Thanks everybody have a blessed day
WPNortheast is offline   Reply With Quote
Old 06-18-2019, 07:40 AM   #2
Sentimental Mental
CTshockhazard's Avatar
Rewards Points: 1,398
Default Sure it's 8?
I've seen them call for (the extra waste of cu) 6 AWG. I believe it's purely a listing thing for the actual connection in the tub.
I'm only kowtowing to their silly whim between the disco and the spa itself. 10 AWG is more than sufficient to clear a fault at 50A.
I have the attention span of a
Old 06-18-2019, 08:04 AM   #3
Rewards Points: 1,164
I usually just try to run pvc all the way. In most cases, we can do that thru a crawl space right to the spa disconnect.
HackWork likes this.
I can't help it if I'm lucky
Old 06-18-2019, 08:07 AM   #4
Rewards Points: 143
Yeah, PVC pipe is very easy to install the way it is partially flexible and can make sweeping bends around things.
Old 06-18-2019, 08:53 AM   #5
zac
Rewards Points: 814
I've had one call for #4 if over 75'.
zac is online now   Reply With Quote
Old 06-18-2019, 10:17 PM   #6
Rewards Points: 144
Feeders to a panel that supplies pool equipment or by extension a Hot Tub have to meet 680.25.A. No NM cable or SER. In other words a conduit system or MC cable. Also EGC has to be insulated. Then ask if the wiring method between the sub panel and the Hot Tub disconnect is a feeder or a branch circuit. A branch circuit that is installed indoors can be Cable.
Old 06-19-2019, 10:51 AM   #7
sbrn33's Avatar
Rewards Points: 3,232
99.9% of spas are portable so just run 6-3 NM.
Old 06-19-2019, 11:06 AM   #8
The op is saying that the specs are requiring a number 8 equipment grounding conductor. Not going to happen with NM unless you can find a 6/5 nm and eliminate the equipment grounding conductor and use one of the other conductors.
Old 06-19-2019, 11:18 AM   #9
sbrn33's Avatar
No he said requirements. I am assuming that he is talking NEC. The NEC does not require a #8 for a portable hot tub.
Old 06-19-2019, 11:19 AM   #10
sbrn33's Avatar
A hot tub is not a pool.
Signal1 likes this.
Old 06-19-2019, 02:24 PM   #11
The nec doesn't require the equipment grounding conductor to be larger than 250.122. But if the manufacturer states #8 then you need to use #8.
I don't think the op is talking about the equipotential bonding. At least that is not what I responded to...
Old 06-19-2019, 10:11 PM   #12
Rewards Points: 144
Read 680.42 then 680.25. 680.25 falls under part II of 680 so an outdoor Hot Tub is treated like a pool.
Old 06-20-2019, 11:13 AM   #13
Switched's Avatar
Rewards Points: 8,844
Pretty sure he's talking about a packaged spa unit, which does not get treated like a pool. 680 part II specifically says "Permanently Installed Pools". A packaged unit is considered portable and not permanent.
sbrn33 likes this.
The Following User Says Thank You to Switched For This Useful Post:
Dan the electricman (06-20-2019)
Old 06-20-2019, 05:05 PM   #14
Rewards Points: 144
680.42 talks about outdoor installations of Hot Tubs. They must conform to Provisions of Parts I and II of 680. Part II - 680.25 talks about feeders. So if a feeder is supplying a panel that feeds a Hot Tub, then the feeder needs to follow 680.25.A. The way the NEC 2014 Analysis book reads is that the exception for existing panels was removed. Very very important for anybody who wires a pool or Hot Tub from an " existing " sub-panel.
Old 06-20-2019, 07:53 PM   #15
Rewards Points: 168
200 amp main lug fed from meter main, has breaker for spa gfci disconnect, which also has breaker.
You really think its a code violation for that cable feeding the 200 amp main lug to be SER? Absolute nonsense
Old 06-20-2019, 10:07 PM   #16
HertzHound's Avatar
Rewards Points: 602
I think what he means is that in the past it was common to install a sub panel and get an inspection. A week latter add the pool or hot tub off of the sub panel. This was how it was done to avoid having the insulated ground run to the sub panel.
If the sub panel was existing, it was allowed to not have the insulated ground. Some inspectors would allow you pull a separate permit for the panel if they saw that you missed the insulated ground. Later they would come back and inspect the pool.
kb1jb1 likes this.
Why say lot words when few words do trick
The Following User Says Thank You to HertzHound For This Useful Post:
kb1jb1 (06-20-2019)
Old 06-20-2019, 11:12 PM   #17
Rewards Points: 144
Do people here read the current NEC and the Analysis book? I am talking about panels that feed pool equipment. I also recommend the IEAI book, " One and Two Family Dwelling Electrical Systems." It has many explanations, examples, and pictures. The IAEI certifies many electrical inspectors and this is their reference book. I am only quoting what the books say. If I follow the written guidelines, then I should not get blamed for when things go wrong. The expression, " going by the book.".
Old 06-21-2019, 04:57 AM   #18
Rewards Points: 168
Your right from my reading the nec. Wow what a shocker thanks. I’m glad I’ve only installed the SER, I’m going to replace it with copper in LFNC at 2.20 a foot. :-/ safety 1st
Old 06-21-2019, 07:34 AM   #19
Rewards Points: 143
I've never heard of this Analysis book.
What happens in the situation of an outside service disconnect feeding an inside main panel with SER cable? They can't install a pool in their house without changing that cable feeding their entire house?
Old 06-21-2019, 08:20 AM   #20
Sentimental Mental
Default OP is on 2017 NEC
Here's the current:
2017 NEC
680.14 Corrosive Environment.
(A) General. Areas where pool sanitation chemicals are
stored, as well as areas with circulation pumps, automatic chlorinators,
filters, open areas under decks adjacent to or abutting
the pool structure, and similar locations shall be considered to
be a corrosive environment. The air in such areas shall be
considered to be laden with acid, chlorine, and bromine
vapors, or any combination of acid, chlorine, or bromine
vapors, and any liquids or condensation in those areas shall be
considered to be laden with acids, chlorine, and bromine
vapors.
(B) Wiring Methods. Wiring methods in the areas described
in 680.14(A) shall be listed and identified for use in such areas.
Rigid metal conduit, intermediate metal conduit, rigid polyvinyl
chloride conduit, and reinforced thermosetting resin
conduit shall be considered to be resistant to the corrosive
environment specified in 680.14(A).
680.25 Feeders. These provisions shall apply to any feeder on
the supply side of panelboards supplying branch circuits for
pool equipment covered in Part II of this article and on the
load side of the service equipment or the source of a separately
derived system.
(A) Feeders. Where feeders are installed in corrosive environments
as described in 680.14, the wiring method of that
portion of the feeder shall be as required in 680.14(B) or shall
be liquidtight flexible nonmetallic conduit. Wiring methods
installed in corrosive environments as described in 680.14 shall
contain an insulated copper equipment grounding conductor
sized in accordance with Table 250.122, but not smaller than
12 AWG.
Where installed in noncorrosive environments, feeders shall
comply with the general requirements in Chapter 3.
(B) Aluminum Conduit. Aluminum conduit shall not be
permitted in the pool area where subject to corrosion.
680.42 Outdoor Installations. A spa or hot tub installed
outdoors shall comply with the provisions of Parts I and II of
this article, except as permitted in 680.42(A) and (B), that
would otherwise apply to pools installed outdoors.
(C) Interior Wiring to Outdoor Installations. In the interior
of a dwelling unit or in the interior of another building or
structure associated with a dwelling unit, any of the wiring
methods recognized or permitted in Chapter 3 of this Code
shall be permitted
to be used for the connection to motor
disconnecting means and the motor, heating, and control loads
that are part of a self-contained spa or hot tub or a packaged
spa or hot tub equipment assembly. Wiring to an underwater
luminaire shall comply with 680.23 or 680.33.