Is AC home run feeder or branch circuit? - Electrician Talk - Professional Electrical Contractors Forum
Old 01-22-2015, 06:25 AM   #1
Rewards Points: 132
Default Is AC home run feeder or branch circuit?
Stupid random thought... If a feeder differs from a branch circuit in that it is between the main OCPD and downstream OCPD, would an AC condenser with its own disconnect be on a feeder?
I don't have a lot of experience wiring ACs but it seems like the disconnect is just a breaker, right?
dielectricunion is offline   Reply With Quote
Old 01-22-2015, 06:31 AM   #2
Very Long Vacation
Rewards Points: 5,262
The disconnect is a disconnect, but even with an OCPD its function is still a disconnect... ok thinking about this you make a really valid question
Old 01-22-2015, 06:52 AM   #3
Rewards Points: 14,714
If the disconnect has OCP (not one of those breakers that does not have OCP), then by definition, the circuit from the panel to the disconnect is a feeder.
The Following 4 Users Say Thank You to hardworkingstiff For This Useful Post:
Awg-Dawg (01-22-2015), chicken steve (01-22-2015), pete87 (01-22-2015), Pharon (01-22-2015)
Old 01-22-2015, 07:08 AM   #4
Retired Account
Rewards Points: 14,650
From art 100>, it would appear your AC may qualify as 'Branch Circuit, Individual' Dielectric...
Feeder. All circuit conductors between the service equip-
ment, the source of a separately derived system, or other
power supply source and the final branch-circuit overcur-
rent device.
Branch Circuit. The circuit conductors between the final
overcurrent device protecting the circuit and the outlet(s).
Branch Circuit, Appliance. A branch circuit that supplies
energy to one or more outlets to which appliances are to be
connected and that has no permanently connected lumi-
naires that are not a part of an appliance.
Branch Circuit, General-Purpose. A branch circuit that
supplies two or more receptacles or outlets for lighting and
appliances.
Branch Circuit, Individual. A branch circuit that supplies
only one utilization equipment.
Branch Circuit, Multiwire. A branch circuit that consists
of two or more ungrounded conductors that have a voltage
between them, and a grounded conductor that has equal
voltage between it and each ungrounded conductor of the
circuit and that is connected to the neutral or grounded
conductor of the system.
The Following 3 Users Say Thank You to chicken steve For This Useful Post:
51360 (01-22-2015), meadow (01-22-2015), Pharon (01-22-2015)
Old 01-22-2015, 07:12 AM   #5
Rewards Points: 64
Yes, I wote a proposal for this because it makes no sense that a circuit to an a/c is a feeder in one case and a branch circuit in another. We'll see what they say.
When I brought this up at our yearly state meeting in Raleigh the cmp member agreed that technically it was a feeder when overcurrent protective device is installed in the disconnect but it should be treated as a branch circuit. That, of course , is his opinion. I happen to agree
Old 01-22-2015, 11:53 AM   #6
What is different if the conductor from the panel to disconnect is a "feeder" vs a "branch circuit"?
Old 01-22-2015, 01:36 PM   #7
Rewards Points: 1,464
Charlie said it well but I thought a feeder fed another panel and a branch circuit came from a panel to an outlet or other point of use like an a/c unit.
Old 01-22-2015, 01:40 PM   #8
Rewards Points: 190
"a feeder fed another panel"
Kinda true, but what defines a panel? An AC disconnect with an OCPD is essentially a 2 space panel.
Stumped is offline   Reply With Quote
The Following User Says Thank You to Stumped For This Useful Post:
hardworkingstiff (01-22-2015)
Old 01-22-2015, 04:38 PM   #9
I don't agree on that one. I would call that a service disconnect fed by a branch circuit.
Old 01-22-2015, 04:40 PM   #10
Pharon's Avatar
Rewards Points: 866
It's not a panel, but if it's fused it is the "final branch-circuit overcurrent device." That makes it a feeder by the Article 100 definition CS posted above.
Pharon is offline   Reply With Quote
The Following User Says Thank You to Pharon For This Useful Post:
Old 01-22-2015, 08:00 PM   #11
Ok, I can see that but not at the residential level. If I run a 480 volt circuit to a 3 Ø 60 amp disconnect and fuse down for a compressor, I'd call that circuit a feeder. Same,but different.
Old 01-22-2015, 08:08 PM   #12
Pharon's Avatar
Rewards Points: 866
Which would you call a feeder? From the panel to the fused disconnect or from the disconnect to the compressor? The first is a feeder, the latter is a branch circuit. The definitions are the same for commercial and residential.
Old 01-22-2015, 08:11 PM   #13
Rewards Points: 190
If it's got an OCPD in it, it's more than just a disconnect.
Would you agree with this:
If I take a 12-2 and run it to a junction box and splice 2 other 12-2 cables onto it, it's a branch circuit.
If I then replace that junction box with a 2-space panel or an AC disconnect with an OCPD, that 12-2 now becomes a feeder.
Emergency standby generator feeder branch circuit to another building MEC NEC Code Forum 15 09-19-2013 06:07 AM
can a feeder tap be a branch circuit wire? unsaint32 NEC Code Forum 2 10-22-2012 09:27 PM
feeder/ branch circuit sparky=t General Electrical Discussion 5 09-14-2012 03:49 PM
Branch circuit conductors/ feeder in same conduit oramac406 NEC Code Forum 1 02-21-2011 04:22 PM
Feeder or Branch Circuit Electron_Sam78 NEC Code Forum 12 08-25-2010 11:33 AM