AC Troubleshooter - Electrician Talk - Professional Electrical Contractors Forum
Old 08-10-2014, 10:04 PM   #1
dronai's Avatar
Rewards Points: 4,571
Default AC Troubleshooter
Had a customer needing AC repair which I gave to my friend. Turns out to be a nightmare intermittent low voltage control problem. The original board was burned, and had an oversized 10A fuse in it. Installed a new board, and it would blow the 5A fuses every 4-5 hrs.
Long story short, the original LV wire to the compressor had the problem. He replaced the wire, but told me the original wire on the contactor coil was using only one wire from the board, and the other side of the coil was from the metal frame ??? Using the metal as a neutral, but the voltage is only 24V from a different source ??? Odd how that even worked ?
dronai is online now   Reply With Quote
Old 08-10-2014, 10:08 PM   #2
Bad Electrician's Avatar
Rewards Points: 4,969
If the transformer had a grounded secondary and one side of the board was connected to the ungrounded conductor the other side of the board was grounded, it would work.
The Following 2 Users Say Thank You to Bad Electrician For This Useful Post:
dronai (08-10-2014), guest (08-10-2014)
Old 08-10-2014, 10:12 PM   #3
dronai's Avatar
AC voltage though and at a different voltage So the secondary of the LV transformer would not be grounded right ? So how could it get back to it's source ?
Old 08-10-2014, 10:57 PM   #4
It had to be grounded either intentionally or accidentally.
The Following User Says Thank You to Bad Electrician For This Useful Post:
dronai (08-10-2014)
Old 08-10-2014, 11:05 PM   #5
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
You know that single conductor circuit can't work, so follow your instincts. Get an ohmmeter and start ringing out paths to ground. If they're using the equipment frame as a return that complete circuit has to be there somewhere.
Is one side of the secondary hard grounded?
Always wear your gloves.
The Following 2 Users Say Thank You to Big John For This Useful Post:
Bad Electrician (08-10-2014), dronai (08-10-2014)
Old 08-10-2014, 11:12 PM   #6
dronai's Avatar
YeahBad, has to be grounded. I didn't think those really small control transformers were internally grounded on the secondary is all.
Big John, We finished yesterday, I was just pondering
Old 08-11-2014, 12:03 AM   #7
8V71's Avatar
Rewards Points: 2,900
They aren't internally grounded. Someone had to jump one lead to ground.
8V71 is offline   Reply With Quote
The Following User Says Thank You to 8V71 For This Useful Post:
dronai (08-11-2014)
Old 08-11-2014, 12:10 AM   #8
8V71's Avatar
Like if they grounded the conductor at the transformer in the air handler the path would be to the main panel and then out to the condensing unit. It could/would also travel through the copper refrigerant lines between both units.
Old 08-11-2014, 12:15 AM   #9
dronai's Avatar
I bet the trick of using the metal frame is a last ditch effort when you lose all but one conductor in your control wires to the compressor. Over 150' away, it was a real PIA to run. We just ran a temporary across the roofs of these condos to test if this was the problem.
Old 08-11-2014, 12:58 AM   #10
Circumcised Member
idontknow's Avatar
Rewards Points: 250
Carrier, Rheem and their associated brands have grounded secondaries on their control transformers in the air handlers.
idontknow is offline   Reply With Quote
The Following 4 Users Say Thank You to idontknow For This Useful Post:
Big John (08-11-2014), Bonnette13 (08-12-2014), dronai (08-11-2014), mgraw (08-11-2014)