Having a brain spasm, code not close by. We have 9 ccc in a pipe #10 and If I recall correctly we can derate from 40amp. This would put it at .70 X 40=28 amps. Can we still go with the 30 amp breaker because of the next size higher even though the adjustments puts us at 28 amps? Can't recall all the rules for this. Not sure how the inspector would see this install.
The other pipes got at least 12 ccc. So # 8 is being used because I am sure that it jumps to .50 reduction.
brother is offline   Reply With Quote
Old 02-16-2015, 01:30 PM   #2
Rewards Points: 1,830
Yes #10 is good for 40 amps at 90C so with 70% you would be good at 28 amps. As long as the calculated load is not greater than 28 amps then you can use a 30 amp overcurrent protective device per 240.4(B)
12 current carrying conductor would require 50% reduction so 8 awg at 90C is 55 amps-- brings you to 27.5 at 50%. Next size applies again
Old 02-16-2015, 01:34 PM   #3
Rewards Points: 70
In Canada we must use 75 degrees on everything except meter sockets
dave91 is offline   Reply With Quote
Old 02-16-2015, 01:52 PM   #4
We must use 75C also but we can use 90C for derating. I believe you can also.
As long as the final overcurrent protective device is not greater than the weakest link- usually 75C you are okay.
If you use nm then you must use the 60 C rating in the NEC
The Following 2 Users Say Thank You to Dennis Alwon For This Useful Post:
51360 (02-16-2015), daveEM (02-16-2015)
Old 02-16-2015, 01:52 PM   #5
Rewards Points: 2,080
in canada for derating we can use 90C column but must not exceed 75
C column for final ampacity similar to nec
oliquir is online now   Reply With Quote
Old 02-16-2015, 02:23 PM   #6
Light Bender
eddy current's Avatar
Rewards Points: 7,830
Can you quote the rule in the cec that says that?
51360 (02-16-2015)
Old 02-16-2015, 02:44 PM   #7
That was my understanding but you will have to help with the code section.
Old 02-16-2015, 02:45 PM   #8
Rewards Points: 70
If we take rule 4-006 (1) into consideration we would use 75 degrees and we would only use 90 degrees if we use subrule (2)
Old 02-16-2015, 03:14 PM   #9
Rewards Points: 70
Google " BC module Derating " it says to derate using 90 degrees
The Following User Says Thank You to dave91 For This Useful Post:
sparky970 (02-17-2015)
Old 02-16-2015, 04:30 PM   #10
Rewards Points: 588
Thanks. co worker says apparently we cannot upsize because they are receptacles. is this true? Can't recall of the top of my head.
Wire Ampacity Derating. Terminal temp rating vs Wire temp Rating Carultch NEC Code Forum 6 05-14-2013 12:36 AM
ampacity AFOREMA1 NEC Code Forum 2 05-10-2011 01:24 PM
Derating feeder ampacity in sunshine Shorty Circuit Commercial Electrical Forum 13 04-01-2011 09:32 PM
ampacity yetti NEC Code Forum 17 02-28-2011 03:43 AM
Ampacity Derating switchleg Residential Electrical Forum 35 11-23-2009 11:20 PM