Available Fault Current - Electrician Talk - Professional Electrical Contractors Forum
Like Tree4Likes
  • 1 Post By FaultCurrent
  • 2 Post By micromind
  • 1 Post By telsa
Old 09-25-2017, 08:59 AM   #1
Rewards Points: 14
Default Available Fault Current
Need help ASAP. With the situation in south Florida, FLP NOT able to compute a AFC letter and I need to build a commercial service quick. My question: I'm building a small 3ph service for irrigation. Feed from open Delta two transformer system. I'm going to compute the primary at infinite since FPL is on hurricane duty. How do I input the transformer data since the 3ph two transformer delta system nameplates are 1ph 120/240. Oh yes, if you are not familure with AFC calcs please don't answer. And don't need any advise on building the service. Thanks in advance
pfactor2 is offline   Reply With Quote
Old 09-25-2017, 10:45 AM   #2
FaultCurrent's Avatar
Rewards Points: 931
Most utilities use the infinite bus as the basis for the primary FC. Since you say you have an open delta setup - many utilities use this rule - Open Delta services have maximum fault currents equal to or less than single-phase services with the same transformer size and voltage. Use the single-phase table and the larger of the two transformers to identify the maximum secondary fault current.
This table works well. Answers are close enough.
This is the one I have bookmarked, I'm sure there are others:
http://www.ed3online.org/files/Const...012-06-05).pdf
brian john likes this.
Old 09-25-2017, 11:12 AM   #3
Rewards Points: 3,434
With an open ∆, each transformers contribution is independent of the other because they are connected to each other at only one end, not both. Therefore, the maximum available fault current will be the larger of the 2 transformers.
Divide the impedance by the full-load current and you'll have fault current.
Example, suppose the largest transformer is 50KVA, 240 volts and the impedance is 5.2%
50,000 240 = 208. 208 .052 = 4000 amps.
brian john and telsa like this.
Old 09-25-2017, 03:57 PM   #4
Rewards Points: 26,920
This stuff is also to be found in Ugly's.
Pages 58-61.
All of the formulas are right there.
can anyone explain what is neutral grounding devces and its using? mike883 General Electrical Discussion 11 08-11-2017 01:35 AM
Fault current Dash Dingo General Electrical Discussion 4 07-25-2017 11:53 PM
Fault Current Protective device 6KA/10KA johnegan General Electrical Discussion 0 09-21-2016 04:38 AM
Converting Fault Current Into Calories Lone Crapshooter Workplace Safety 4 04-17-2016 07:33 PM
Average Primary Fault Current RePhase277 General Electrical Discussion 21 02-10-2016 07:26 AM