Im not an electrican (yet) so dont rip me a new one for not totally grasping this.
It is the outlets after the open neutral but before the split that causes the problems. Devices plugged into these outlets will backfeed the voltage from both phases onto the neutral back to the point where it has been accidently opened. It can now overvoltage/undervoltage beyond the split and the devices plugged into those outlets can contribute to the problem as well.
I understand now that a neutral opening at the outlets on either leg after the split would not cause the voltage imbalance.
But just to clarify after reading the above explanation, In the case of a neutral breaking prior to the spilt,
Devices plugged into these outlets......
This makes it sound like only loads plugged in prior to the split cause the voltage imbalance on the other 2 legs of the MWBC.
However, I assumed that If the neutral breaks prior to the split, (even if there are NO outlets/loads plugged in prior to the split), then each leg after the split now will have the voltage imbalance between each other.
In other words, if the neutral opens prior to the split, my TV and Lightbulbs after the split are toast.....
Again, I am a minor and a student... please be kind.
soe is offline   Reply With Quote
Old 11-24-2013, 09:12 AM   #22
RIP 1959-2015
HARRY304E's Avatar
Rewards Points: 1,344
That's right they're toast,so that's why we pig tail it to the receptacles .
Old 11-24-2013, 11:01 AM   #23
8V71's Avatar
Rewards Points: 2,900
Loads after the split also have an effect but only if the break is before the split.
Yes
Yes
8V71 is offline   Reply With Quote
The Following User Says Thank You to 8V71 For This Useful Post:
soe (11-24-2013)
Old 11-24-2013, 12:27 PM   #24
soe
Rewards Points: 55
8V71 - Thank you very much. That is exactly what I was unclear about.
TO summarize what I 'think' I have gathered from your reply.... in my crude drawing below......
A break in the neutral at the yellow X, will NOT send unbalanced 240 over L1 and L2 unless there was a load at outlet 1 (prior to break).
Remove outlet #1 from equation completely... breaking the neutral now... both L1 and L2 circuits would be dead, not turn them into a 240 ciruit together.
THat is why we pigtail that outlet #1.... and even if that pigtail connetion failed (say the X break is the pigtail), then both L1 and L2 circuits would be dead (no overvoltage situation).
Thanks for your patience with me... let me know if my reasoning is correct.
Happy Thanksgiving.
Old 11-24-2013, 12:30 PM   #25
I own stock in FotoMat!
Rewards Points: 6,520
Happy Thanksgiving.
Opening the neutral at the yellow x WILL cause an imbalance, but only to the loads to the left of it.
Old 11-24-2013, 12:39 PM   #26
8V71's Avatar
Ahhh...you beat me to a diagram.
This image isn't near as nice as my horsey pictures but it may help. The blue things are supposed to be resistors (loads in the outlets) or even springs if you want to look at it in a mechanical sense.
Depending on how many loads (or springs) that are on each phase, it can make the neutral float anywhere in between the two phases which gives you the overvoltage/undervoltage problem between the neutral and each phase.
If the loads (springs) were perfectly matched between phases the neutral would stay in the center and you would never know that there is a problem even though the neutral is open.
Old 11-24-2013, 12:43 PM   #27
8V71's Avatar
I'm getting confused now. I think I have been giving you wrong information.
Edit: No, I'm sorry everything is back on track. Like 480 said, there will be an unbalanced situation with the yellow X broken. I also took a sentence out of my diagram that was incorrect.
Old 11-24-2013, 12:50 PM   #28
8V71's Avatar
deleted
Old 11-24-2013, 01:05 PM   #29
soe
Rewards Points: 55
Then my reasoning failed.
If you break the neutral at the X in my diagram, then all outlets (ABC) on L1 and L2 will see the unbalanced 240 depending on loads.
Everything relies on the integrity of the pigtail connection at outlet 1.
If you opened the neutral at X with power off to only one leg then the other leg would be dead, not a complete circuit. If open the neutral at x with power on to both legs, then you will get the over/under voltage situation on both L1 and L2.
If your still reading... I apologize for the jumble.
Old 11-24-2013, 01:32 PM   #30
Cletis's Avatar
Rewards Points: 2,050
Just think of it as an MLM. You do something wrong it F's everyone in your upline not your downline
I'm shakin it boss..I'm shakin it
Old 11-24-2013, 01:33 PM   #31
Cletis's Avatar
Old 11-24-2013, 01:41 PM   #32
8V71's Avatar
My fault, I gave you wrong information in post 23. It should be correct now.
Old 11-24-2013, 03:28 PM   #33
soe
Rewards Points: 55
I understand completely now....
Was it ever an acceptable practice to use a device to feed the neutrals thru?
When did the current pigtail rule come into effect?
Is it common to see an outlet wired this way in the field / on service calls?
Old 11-24-2013, 06:05 PM   #34
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Originally Posted by drumnut08 View Post
. Yes , because you're not counting on the continuity of the device as a feed through . It's an unbroken conductor and the circuit integrity I still intact on device replacement , or that's what I think anyway , lol ?
Until an idiot cuts the old device from the box and uses just wraps the wires on the new device. I loop em right thru, it's a time saving thing.
Tragically Stupid Basic Three Phase Question ErnieG General Electrical Discussion 27 03-24-2013 10:44 PM
Basic 3 Phase Question Deep Cover General Electrical Discussion 11 01-11-2013 08:06 AM
Basic Service Drop Question wattsup20 Services and Service Equipment 5 11-09-2010 06:12 PM
Question on Basic Overload Setting msoucy General Electrical Discussion 5 06-24-2009 07:33 PM
A basic dumb question hot and neutral reversed on a cord Golden Arc General Electrical Discussion 36 04-03-2009 08:56 AM