buck boost - Electrician Talk - Professional Electrical Contractors Forum
Old 07-01-2014, 10:23 PM   #1
flashover's Avatar
Rewards Points: 121
Default buck boost
I dont understand something about an installment we are doing.
There is a refrigerated trailer we temped out for 208 3ph.
Something happen causing compressor to shut down, no tripped breaker, no blown fuse. But while reading voltage at the disco i read 196v.
We are now installing buck boost transformers to adjust for undervoltage to get the 208 at the disco, and compressor.
2 transformers in parallel for each of the 2 refrigerated trailers.
I dont understand how this works because the nameplate on the transformer say 120/208v primary, 12/24v secondary.
The wiring schematic says "boost"
Does this thing boost the voltage to 208, or am i gonna get 24 volts on the secondary?
flashover is offline   Reply With Quote
Old 07-01-2014, 10:27 PM   #2
IBEW MEMBER
Rewards Points: 254
So adjusting the taps is not a option?
fistofbolts is offline   Reply With Quote
Old 07-01-2014, 10:44 PM   #3
Rewards Points: 2,950
Yes, the nameplate is misleading. Just find the wiring schematic that matches your scenario and you will be fine. Call the tech support number if you have any questions. I have had good luck doing that when I wasn't sure about how many xfmrs to use and in what configuration to get what I wanted.
Old 07-01-2014, 11:10 PM   #4
Rewards Points: 3,032
These transformers have isolated windings; the primary is not internally connected to the secondary.
In your case, you are connecting the two isolated windings in series. This will add the secondary voltage to the primary.
You can also reverse the polarity of the secondary and it will subtract the secondary from the primary.
These transformers will seem small for the load they carry, this is because the load current appears on the secondary, not the primary.
You can compute the formulas if you want, but in the vast majority of cases, if the load does not exceed the capacity of the secondary, you're good.
Old 07-02-2014, 12:19 AM   #5
Electron Pathway Engineer
The_Modifier's Avatar
Rewards Points: 246
Nicely said, couldn't have put it better myself.
The_Modifier is online now   Reply With Quote
The Following User Says Thank You to The_Modifier For This Useful Post:
micromind (07-02-2014)
Old 07-02-2014, 09:10 PM   #6
Rewards Points: 1,498
Your clearly not understanding the concept of buck / boost !
Yes you will get 24v at the secondary BUT this is in series with
mains supply, so you can increase the voltage by 24v or decrease the voltage by 24v depending on the polarity of the 24v winding.
I suggest that you read up on how the buck / boost system works.
The Following User Says Thank You to dmxtothemax For This Useful Post:
Bad Electrician (07-02-2014)
Old 07-02-2014, 09:26 PM   #7
Bad Electrician's Avatar
Rewards Points: 4,969
http://www.solahevidutysales.com/buc...ansformers.htm
A decent site for a quick primer for the OP and PDF's for selecting the correct rating transformer
Buck n boost LegacyofTroy General Electrical Discussion 17 08-08-2013 08:59 AM
Buck boost TXR Surge03 General Electrical Discussion 26 07-24-2013 04:08 AM
buck boost garfield General Electrical Discussion 38 05-11-2012 09:32 AM
another buck boost TxElectrician General Electrical Discussion 7 04-16-2012 11:56 PM
Buck-Boost; Need Help!! Joe Momma General Electrical Discussion 13 05-19-2009 08:48 PM