Buck Boost Transformer - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By Service Call
Old 09-27-2016, 01:02 PM   #1
Rewards Points: 32
Default Buck Boost Transformer
Can someone educate me on how to rate a Buck-Boost Transformer? I have a 15 amp 220 volt 1-phase machine fed with 208 volt. Customer wants full 220 volt. I initially rated the Buck-Boost Transformer for 3.3KVA ( IxE/1000). Supplier informed me that I only need a 1KVA maximum because I don't have to fully rate when the voltage only needs to boosted. I don't understand this.
2825mdh1 is offline   Reply With Quote
Old 09-27-2016, 01:12 PM   #2
Rewards Points: 21,896
It is very simple to change voltage on buck/boost transformer because both secondary and primary useally connected in series but there is few differnt style of connection for B/B .
The reason why it is small because the secondary side will do most of the work to just increase or decrease voltage by small steps .
and I want to give you a heads up make sure you follow the connection diagram very carefull because each one is differnt style of connection I know it can be a headache on that.
and what type of brand of B/B you will plan to use because I have quite few listing of connection diagrams so I cant post all of it until I know what brand you will use and myself and few other members can help you on that.
2825mdh1 (09-28-2016)
Old 09-27-2016, 05:21 PM   #3
Rewards Points: 26,512
230 V - 208 V = 22 V of boost. ( forget the talk about 220 V )
22 V x 15 A ( at full load, I presume ) = 330 VA
If the wire sizes are not too absurd, then even a 500 VA autoformer would be overkill.
Consult Ugly's for a suitable wiring diagram.
Old 09-27-2016, 06:06 PM   #4
Service Call's Avatar
Rewards Points: 32
The reason it's small is cause you're only concern is the current on the boosted voltage. Which is 12 volts boosted and 15 amps. So you can actually use only a .250 KVA.
This from Square D. Although depending on the load you may want to upsize i.e. motor load.
frenchelectrican likes this.
Service Call is online now   Reply With Quote
The Following User Says Thank You to Service Call For This Useful Post:
Old 09-27-2016, 08:38 PM   #5
Rewards Points: 3,106
The reason it can be small is because only the low voltage side of the transformer sees line current. The high voltage side sees only the small current needed to generate the low voltage side.
Old 09-28-2016, 10:55 AM   #6
Rewards Points: 32
I can see it now. Thank you to everyone who replied.
Can SDGE require my customer to pay for transformer Jeremy9 General Electrical Discussion 13 06-17-2018 11:51 PM
Open delta open wye transformer bank Lone Crapshooter Industrial Electrical Forum 15 09-15-2016 02:42 PM
Transformer install Arrow3030 NEC Code Forum 10 09-08-2016 04:15 PM
Transformer neutral bond sizing (paralleled secondary) haltonelectrician Canadian Electrical Forum 27 06-19-2016 07:21 PM
Transformer Bonding CES Services and Service Equipment 25 04-23-2016 12:54 AM