I was installing a 100amp sub panel in a big ass basement and came across this; funny thing is, the house is probably 3-5 years old! They went to great lengths to run this from the neutral bar at the disco....needless to say I cut the #6 and dropped it into the new sub.
I'd rather be sleeping.
The Following User Says Thank You to BuzzKill For This Useful Post:
bdawg (01-25-2015)
Old 01-24-2015, 08:11 PM   #2
Rewards Points: 1,298
Was that the gas pipe bond?
Mich drew is offline   Reply With Quote
Old 01-24-2015, 08:15 PM   #3
BuzzKill's Avatar
I guess you could call it that...better would be the "illegal gas pipe bond" or the "suicide gas pipe bond".
Mich drew (01-24-2015)
Old 01-24-2015, 10:20 PM   #4
Retired Account
Rewards Points: 14,650
What makes it suicidal to an MBJ vs. a sub's G-bar Buzz? ~CS~
Bad Electrician (01-25-2015)
Old 01-24-2015, 10:22 PM   #5
Mr. Awesome
Rewards Points: 85
If there is flexible stainless gas lines in the home you need to bond the gas line here in Iowa. You might want to see if that is the reason next time you go cutting stuff. Personally if you did that in my house you would be getting called back to fix it.
knomore is offline   Reply With Quote
Old 01-24-2015, 10:51 PM   #6
Rewards Points: 1,464
Any job I do, the inspector aways checks out the grounding and bonding . I think you should have another look.
Old 01-24-2015, 11:32 PM   #7
Very Long Vacation
Rewards Points: 5,262
If any of that is corrugated gas tubing it needs to be bonded/grounded.
BTW, that duct work is
Old 01-25-2015, 12:22 AM   #8
Bad Electrician's Avatar
Rewards Points: 4,969
Gas pipes are bonded either intentionally or accidentally and hard to avoid. Ever appliance that uses gas also has an electrical connection with a EGC.
Old 01-25-2015, 12:42 PM   #9
Rewards Points: 101
When ever an existing gas line is extended using flexible gas line it must be bonded. I think you better put it back.
cc2kj is offline   Reply With Quote
Old 01-25-2015, 02:06 PM   #10
Rewards Points: 308
Pray tell, how was that one in the picture ''bonded'' when the pipe is clearly wrapped in insulating tape under the pipe clamp?
Libtard logic: It’s okay for people to LOOT in person, but not VOTE in person
Maximumbob (01-26-2015)
Old 01-25-2015, 02:32 PM   #11
BuzzKill's Avatar
oops.
yep, never saw any corrugated tubing so that's what made me jump at it, but that doesn't mean there is some where I can't see. I got more work there shortly, I'll fix it.
CADPoint (01-25-2015)
Old 01-25-2015, 02:35 PM   #12
RGH
RGH's Avatar
Rewards Points: 2,044
Mac your losing me here... Insulating tape?? Looks like black pipe here to me... I would check water heater main bond should be there vs bonding sub derived off main panel.
I rather be fishing......
RGH is offline   Reply With Quote
Old 01-25-2015, 02:43 PM   #13
Rewards Points: 308
Thought about that, my eyes and pictures here are not that great, that looked like plumbers pipe wrap to me at first. We rarely see black pipe used here.
Old 01-25-2015, 03:07 PM   #14
Ty Wrapp's Avatar
I don't see any duct work. I see insulation!
Ty Wrapp is offline   Reply With Quote
Old 01-25-2015, 03:26 PM   #15
RGH
RGH's Avatar
I see this stuff here all the time the cable guys are ground happy I think we need a few better pics . Gas is used everything up here in snow country. A ground wire is usually run from an appliance to the pipe if had flex pipe ( dryers) usually. But the main bond is usually at water heater
check this beauty out:-image-3478708196.jpg
Like this one I did😉
The Following User Says Thank You to RGH For This Useful Post:
Big Pickles (01-25-2015)
Old 01-25-2015, 03:32 PM   #16
BuzzKill's Avatar
I just recoil at gas bonds two inches from the valve.
Old 01-25-2015, 05:11 PM   #17
1.21gigawatts's Avatar
Rewards Points: 62
Why would you drop that bond into your sub ? Grounding and grounded conductors would run with your feeder. Its is neither in a detached building nor a seperatly derived system.
1.21gigawatts is offline   Reply With Quote
Old 01-25-2015, 05:35 PM   #18
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
There's nothing wrong with bonding a gas pipe from the ground bar in a sub panel.
Old 01-25-2015, 05:54 PM   #19
Rewards Points: 60
The gas bond is unnecessary if there is no CSST present and the equipment grounding conductor for the unit served will be the bond for the gas.
If you bond the pipe then IMO it is size to T250.122 . Going to a sub panel should be can be argued as to whether it is okay or not as there is no provisions that I know of that allows the ground bar in a panel to be used. To late for a proposal for 2017 but golly someone should put it in there
Art. 250.102 states that a bonding jumper shall be a wire, bus, screw, or similar suitable conductor.
Old 01-25-2015, 06:03 PM   #20
evil bastard
Rewards Points: 746
We're not talking about a bonding jumper.
Its a beauty Oakey Code Violation Discussion 5 12-16-2014 07:41 PM
ulta beauty flashover General Electrical Discussion 10 07-14-2013 01:14 PM
What a beauty hydro Services and Service Equipment 19 03-04-2013 12:00 PM
Little beauty frank Off Topic (Non Trade) 3 07-20-2010 01:32 PM
Found this beauty... running dummy Code Violation Discussion 30 06-22-2009 03:17 PM