That the house I turned you on to?
"The problem isn't that Hillary Clinton lies. We all know she lies. The problem is that her supporters don't seem to care"
jbfan is offline   Reply With Quote
Old 01-25-2015, 06:15 PM   #22
Chairman of the Bored
BuzzKill's Avatar
Rewards Points: 2,540
Shhh.
I'd rather be sleeping.
Old 01-25-2015, 06:18 PM   #23
Big Pickles's Avatar
Have run from panel to gas line when all plastic water lines in and out.
Big Pickles is offline   Reply With Quote
Old 01-25-2015, 06:20 PM   #24
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Water lines have nothing to do with bonding a gas line.
Old 01-25-2015, 06:22 PM   #25
Rewards Points: 304
Are you saying you used the gas pipe for your grounding electrode, since the water lines were all plastic?
Libtard logic: It’s okay for people to LOOT in person, but not VOTE in person
BuzzKill (01-25-2015)
Old 01-25-2015, 07:42 PM   #26
1.21gigawatts's Avatar
Rewards Points: 62
Originally Posted by mcclary's electrical View Post
There's nothing wrong with bonding a gas pipe from the ground bar in a sub panel.
You missed my point, why would he put an existing #8cu that was inteneded for bonding a gasline from the main loadcenter into his new subpanel. It does nothing as the bonding/grounding is done with the subs feeder.
And as for bonding systems from a sub, what if the sub was 40a mcb with a #10 egc? You still going to run a #8bond to a sub and hope it handles a high fault current ?
1.21gigawatts is offline   Reply With Quote
Old 01-25-2015, 07:44 PM   #27
Rewards Points: 60
We're not talking about a bonding jumper.
What are we talking about. Gas pipe has to be bonded and tied to the rest of the system just like water pipe unless there is an equipment grounding conductor at the equipment with gas fuel.
Old 01-25-2015, 10:10 PM   #28
MHElectric's Avatar
Rewards Points: 46
This gas bonding is so friggin confusing. I don't think any of the inspectors here know whether to enforce it or not, and even less contractors know if it's needed.
So far, it hasn't been enforced in my area, BUT, I have seen some new construction homes done by out-of-towners where a bare copper has been run from the main panel to the gas meter.
The Following User Says Thank You to MHElectric For This Useful Post:
BuzzKill (01-26-2015)
Old 01-25-2015, 10:50 PM   #29
icdubois's Avatar
Rewards Points: 491
In our area the ahj don't want to gas line or meter to be bonded.
icdubois is offline   Reply With Quote
The Following User Says Thank You to icdubois For This Useful Post:
BuzzKill (01-28-2015)
Old 01-27-2015, 05:39 PM   #30
If there is CSST in the residence then the bond should not have been made there but on the feed (house)side of the meter extended to the main service grounding equipment. But either way I don't think I would have just cut it out.
freeball is offline   Reply With Quote
Old 01-27-2015, 05:41 PM   #31
evil bastard
Rewards Points: 746
Please prove that. I think you made it up.
Old 01-27-2015, 05:45 PM   #32
Rewards Points: 60
The gas code states the bond is to be made at the point where the gas pipe enters the building. Some take that to mean outside the house. NC just amended that rule to allow bonding anywhere
Old 01-27-2015, 05:47 PM   #33
Rewards Points: 60
Here is the section
G2411.1.1 (310.1.1) CSST. Corrugated stainless steel tubing
(CSST) gas piping systems shall be bonded to the electrical
service grounding electrode system at the point where
the gas service enters the building. The bonding jumper
shall be not smaller than 6AWGcopper wire or equivalent.
ibew415 (01-27-2015)
Old 01-27-2015, 05:53 PM   #34
thanx Dennis you beat me to it. I just did that a few months ago on a residence.
Old 01-27-2015, 06:41 PM   #35
evil bastard
Rewards Points: 746
It still doesn't say it must be landed in the service.
Old 01-27-2015, 06:51 PM   #36
Rewards Points: 60
No it says bonded to the electrical service grounding electrode system which is connected back to the service. You cannot take it to a sub panel. It either goes back to the service directly or ties to the GES
Old 01-27-2015, 07:02 PM   #37
Very Long Vacation
Rewards Points: 5,262
Do you have your PMs turned off? I cant send you messages regarding this.
Old 01-27-2015, 07:53 PM   #38
evil bastard
Rewards Points: 746
Please check definition of bonding jumper. I think you're wrong.
In my view, it is connected to the grounding electrode system. Through a bonding jumper . No where does it say it must land in the service, it simply days it must be electrically connected, which it would be, landed on the ground bar of a sub panel.
Old 01-27-2015, 07:53 PM   #39
evil bastard
Rewards Points: 746
I don't think so. I'm not sure how I can tell on my phone either
Old 01-27-2015, 08:03 PM   #40
Very Long Vacation
That's ok, phones are something else.
Its a beauty Oakey Code Violation Discussion 5 12-16-2014 07:41 PM
ulta beauty flashover General Electrical Discussion 10 07-14-2013 01:14 PM
What a beauty hydro Services and Service Equipment 19 03-04-2013 12:00 PM
Little beauty frank Off Topic (Non Trade) 3 07-20-2010 01:32 PM
Found this beauty... running dummy Code Violation Discussion 30 06-22-2009 03:17 PM