Compliant or not - Electrician Talk - Professional Electrical Contractors Forum
Old 02-28-2013, 05:22 PM   #1
Rewards Points: 510
Default Compliant or not
I'm having trouble with inspector telling me my one line diagram is incorrect and can not install transfer switch in this manner. Please take a look and no need to look at wire sizes or pipe sizes that is ok. He is telling me that the 400 Amp TS can not be used?
Gamit is offline   Reply With Quote
Old 02-28-2013, 05:25 PM   #2
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
400 amp main breaker ATS ? If so your panels need overcurrent protection( main breaker panels)
Old 02-28-2013, 05:26 PM   #3
Chris Kennedy's Avatar
Rewards Points: 2,000
Oops, 240.21.
The Following User Says Thank You to Chris Kennedy For This Useful Post:
wildleg (02-28-2013)
Old 02-28-2013, 05:30 PM   #4
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 1,038
I think maybe he thinks you need a 400A main disco (in front of the trough or at each supply), which is what I would probably do, but as far as I can tell, if the load calc is correct it should be fine (3 mains) (as long as the tap rules are followed) (I am assuming there is not 400A fusing in your ATS -that would be something I haven't seen)
Old 02-28-2013, 05:32 PM   #5
Rewards Points: 510
Yes the panels are main breakers and the TS will have a 400 Amp breaker in it as well. He is telling me that I need a 350 Amp breaker
Old 02-28-2013, 05:35 PM   #6
wildleg's Avatar
Originally Posted by Chris Kennedy View Post
Oops, 240.21.
ah, that makes sense - the tap conductors don't have overcurrent protection.
thanks
Old 02-28-2013, 05:36 PM   #7
Coffee drinking member
Wirenuting's Avatar
Rewards Points: 7,592
I don't see any isolation to the ATS.
Supply, Main distribution then you feed the ATS.
ATS only feeds necessary loads. Load shed option if needed and approved.
Old 02-28-2013, 05:40 PM   #8
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
What' feeding it? parrallel 4/0 als? They had me drop fusing to 350 on a 400 amp for that reason.I see you have 350 cu after the meter, He could be basing it on the 320 pan if not the latteral size. I take it it is not residential.
Old 02-28-2013, 05:40 PM   #9
Rewards Points: 510
thanks
Tap conductors are less then 10 feet long
Old 02-28-2013, 05:42 PM   #10
Rest In Peace
aftershockews's Avatar
Rewards Points: 7,003
I am not going to turn my head 90 degrees to the right to read that schematic.
aftershockews is offline   Reply With Quote
The Following User Says Thank You to aftershockews For This Useful Post:
Wirenuting (02-28-2013)
Old 02-28-2013, 05:44 PM   #11
Wirenuting's Avatar
Is this kind of what he wants to see in a 1 line format?
Old 02-28-2013, 05:44 PM   #12
ET rocks
3xdad's Avatar
Rewards Points: 2,174
Even at 350, those feeders would be overfused, so how does the tap rule come into play here?
Too soon, Black Dog... way too soon...Rock on buddy.
3xdad is offline   Reply With Quote
Old 02-28-2013, 05:48 PM   #13
240.4(B)
I agree with the inspector, 350A max.
Old 02-28-2013, 05:48 PM   #14
Rewards Points: 510
Over current protection is coming from main breaker panels and TS is serving as disco.
Old 02-28-2013, 05:58 PM   #15
wildleg's Avatar
I agree, the trough conductors should be 400s if they are going to be tapped
Old 02-28-2013, 06:02 PM   #16
ET rocks
3xdad's Avatar
i like the PV setup on the bottom left.
Old 02-28-2013, 06:06 PM   #17
The sun is dieing a slow death, why the happy face?
chicken steve (02-28-2013)
Old 02-28-2013, 06:09 PM   #18
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Gamit, Table 310.15 , 350 mcm is rated for 350 amps, 500 mcm would be the size wire used
Old 02-28-2013, 06:13 PM   #19
Rewards Points: 510
This is residential and the 350,s are should be fine considering the max possible load is 350 Amps.
Old 02-28-2013, 06:15 PM   #20
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
But the OCP is 400 and the wire needs to be sized to the main OCPD.
The Following User Says Thank You to Shockdoc For This Useful Post:
JohnR (02-28-2013)
Is this code compliant? Hexamexapex Residential Electrical Forum 11 02-26-2013 08:18 PM
Code compliant? Gamit General Electrical Discussion 9 02-22-2013 07:52 PM
Is this compliant? butcher733 General Electrical Discussion 6 12-24-2012 10:08 AM
Compliant? GEORGE D NEC Code Forum 12 11-16-2012 09:15 PM
Is this compliant? electures NEC Code Forum 10 06-27-2011 01:41 PM