Default Conductor derating

I'm trying to understand the following concept:


Example let's suppose I have a 2" raceway from a panel to a trough with hrs branching out of the trough. The 2" conduit is 3' long. Can I fill the 2" conduit to it max conductor capacity according to nec tables. Or does derating apply in this situation. If so why even have a conduit fill chart if you can only have max 3 ckts without derating. Someone please clarify.

Thanks
jayare813 is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 03-14-2014, 06:59 PM   #2
Senior Member
 
ponyboy's Avatar
 
Join Date: Nov 2012
Location: parts unknown
Posts: 8,051
Rewards Points: 709
Default

Quote:
Originally Posted by jayare813
I'm trying to understand the following concept: Example let's suppose I have a 2" raceway from a panel to a trough with hrs branching out of the trough. The 2" conduit is 3' long. Can I fill the 2" conduit to it max conductor capacity according to nec tables. Or does derating apply in this situation. If so why even have a conduit fill chart if you can only have max 3 ckts without derating. Someone please clarify. Thanks
Derating doesn't apply under 24".
__________________
Too dumb for New York, too ugly for LA
ponyboy is offline   Reply With Quote
Old 03-14-2014, 07:01 PM   #3
I own stock in FotoMat!
 
480sparky's Avatar
 
Join Date: Sep 2007
Location: Cornpatch USA
Posts: 39,118
Rewards Points: 6,520
Default

Raceway fill is merely a calculation of how many little circles you can put into a big circle.

Derating goes to how much heat an excessive number of little circles inside said big circle create, and now well the colored coating on the little circles can handle it.
__________________
I'm 480Sparky, and I approved this message.
480sparky is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 03-14-2014, 07:05 PM   #4
Senior Member
 
Awg-Dawg's Avatar
 
Join Date: Jan 2007
Location: Dayton Ohio
Posts: 3,275
Rewards Points: 570
Default

Quote:
Originally Posted by 480sparky View Post
Raceway fill is merely a calculation of how many little circles you can put into a big circle.

Derating goes to how much heat an excessive number of little circles inside said big circle create, and now well the colored coating on the little circles can handle it.

Nice!

A little too technical, but, nice.
__________________
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote
The Following User Says Thank You to Awg-Dawg For This Useful Post:
Pharon (03-14-2014)
Old 03-15-2014, 01:49 AM   #5
Senior Member
 
Join Date: Jan 2008
Posts: 1,330
Rewards Points: 1,208
Default

I'll give you an example that has meaning for me and maybe you will understand.

According to Table C.1 (9) 12 ga wires is max fill for 1/2" EMT. According to Table 310.15 90 degree 12 ga THHN/THHW max amp is 30A (not allowed to fuse over 20A). By Table 310.15(B)(2)(a) adjustment for more than 3 CCCs you multiply that 30A X .7 for the 9 CCCs which equal 21A and still good on a 20A fuse.

However if you go to 3/4" EMT the fill is (16) 12 ga wires (same insulation) which must be derated to 50% which equals 15A. No longer good on a 20A fuse.

With this 12 ga wire and 9 CCCs in 1/2" EMT six circuits can be run with single phase if all are shared neutrals (3X3).
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Tiger is offline   Reply With Quote
Old 03-15-2014, 09:23 AM   #6
Moderator

 
Dennis Alwon's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 21,201
Rewards Points: 1,398
Default

The derating does not affect this install but the fill is still pertinent. Look at Table 9 Note 4. You can only fill the nipple 60%
Dennis Alwon is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Neutral conductor to ground conductor measurements megw junky Residential Electrical Forum 7 04-08-2012 09:57 AM
derating your conductor if >3 of them. kaboler Code Violation Discussion 43 10-30-2011 03:23 PM
conductor derating on rooftops sunpower NEC Code Forum 25 07-15-2011 05:15 PM
grounding electrode conductor and grounded conductor nolabama Services and Service Equipment 6 01-12-2009 02:51 AM
Service conductor derating george nicholson Services and Service Equipment 2 04-22-2008 02:39 PM


All times are GMT -4. The time now is 10:52 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com