I'm trying to understand the following concept:
Example let's suppose I have a 2" raceway from a panel to a trough with hrs branching out of the trough. The 2" conduit is 3' long. Can I fill the 2" conduit to it max conductor capacity according to nec tables. Or does derating apply in this situation. If so why even have a conduit fill chart if you can only have max 3 ckts without derating. Someone please clarify.
Thanks
jayare813 is offline   Reply With Quote
Old 03-14-2014, 05:59 PM   #2
ponyboy's Avatar
Rewards Points: 709
Originally Posted by jayare813
I'm trying to understand the following concept: Example let's suppose I have a 2" raceway from a panel to a trough with hrs branching out of the trough. The 2" conduit is 3' long. Can I fill the 2" conduit to it max conductor capacity according to nec tables. Or does derating apply in this situation. If so why even have a conduit fill chart if you can only have max 3 ckts without derating. Someone please clarify. Thanks
Derating doesn't apply under 24".
Old 03-14-2014, 06:01 PM   #3
I own stock in FotoMat!
Rewards Points: 6,520
Raceway fill is merely a calculation of how many little circles you can put into a big circle.
Derating goes to how much heat an excessive number of little circles inside said big circle create, and now well the colored coating on the little circles can handle it.
Old 03-14-2014, 06:05 PM   #4
Awg-Dawg's Avatar
Rewards Points: 726
Nice!
A little too technical, but, nice.
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote
The Following User Says Thank You to Awg-Dawg For This Useful Post:
Pharon (03-14-2014)
Old 03-15-2014, 12:49 AM   #5
Rewards Points: 1,208
I'll give you an example that has meaning for me and maybe you will understand.
According to Table C.1 (9) 12 ga wires is max fill for 1/2" EMT. According to Table 310.15 90 degree 12 ga THHN/THHW max amp is 30A (not allowed to fuse over 20A). By Table 310.15(B)(2)(a) adjustment for more than 3 CCCs you multiply that 30A X .7 for the 9 CCCs which equal 21A and still good on a 20A fuse.
However if you go to 3/4" EMT the fill is (16) 12 ga wires (same insulation) which must be derated to 50% which equals 15A. No longer good on a 20A fuse.
With this 12 ga wire and 9 CCCs in 1/2" EMT six circuits can be run with single phase if all are shared neutrals (3X3).
Tiger is offline   Reply With Quote
Old 03-15-2014, 08:23 AM   #6
Rewards Points: 2,222
The derating does not affect this install but the fill is still pertinent. Look at Table 9 Note 4. You can only fill the nipple 60%
Neutral conductor to ground conductor measurements megw junky Residential Electrical Forum 7 04-08-2012 08:57 AM
derating your conductor if >3 of them. kaboler Code Violation Discussion 43 10-30-2011 02:23 PM
conductor derating on rooftops sunpower NEC Code Forum 25 07-15-2011 04:15 PM
grounding electrode conductor and grounded conductor nolabama Services and Service Equipment 6 01-12-2009 01:51 AM
Service conductor derating george nicholson Services and Service Equipment 2 04-22-2008 01:39 PM