Current Transformer - Electrician Talk - Professional Electrical Contractors Forum
Like Tree9Likes
  • 4 Post By MDShunk
  • 3 Post By frenchelectrican
  • 1 Post By gpop
  • 1 Post By micromind
Old 08-21-2018, 04:19 PM   #1
Rewards Points: 193
Default Current Transformer
What happens to a 10A current transformer that has 60 amps passing through it??
czars is offline   Reply With Quote
Old 08-21-2018, 04:27 PM   #2
Rewards Points: 6,421
Depends on brand and model. They'll either perform above rated expectations, run hot, or burn out. Quite often, all three, and in that order.
Old 08-21-2018, 04:38 PM   #3
Rewards Points: 21,896
I am on same page as MDshunk posted it will be one of the three but how long the overload will last .,, most case with serious overload it will either overheat or burnout some will survie pretty good but the calberation may be off wonkers some.
and one warning with current transformer never open any connection when you have load on current transformer otherwise it will self destruction it.
Old 08-21-2018, 08:20 PM   #4
Rewards Points: 1,778
I would worry less about a ct than i would worry about what its connect to.
I have a few setups that far exceed the ct ratings but we use a shorting relay to protect the controls until the motor has started.
joebanana likes this.
Old 08-22-2018, 08:51 PM   #5
Rewards Points: 3,104
Depending on its design, it will most likely saturate the core and the secondary current will no longer be in proportion to the primary.
frenchelectrican likes this.
Ground Current brian john General Electrical Discussion 13 05-22-2018 11:46 AM
Y Delta woes chicken steve NEC Code Forum 58 04-03-2018 06:52 PM
Current transformer orientation? bill39 General Electrical Discussion 9 07-07-2016 02:37 PM
CT's (Current Transformer) grounding magmash PLCs, VFDs, Motors and Controls 5 01-19-2016 09:59 PM