Delta Supply and star generator - Electrician Talk - Professional Electrical Contractors Forum
Like Tree8Likes
  • 1 Post By frenchelectrican
  • 3 Post By micromind
  • 2 Post By micromind
  • 1 Post By brian john
Old 03-25-2018, 08:08 PM   #1
Rewards Points: 34
Default Delta Supply and star generator
Hello everyone,
I am relatively new to this field of electrical design. In my current assignment I am working on the upgrade of some old water treatment plants with new equipment. The supply coming to one of the site is delta connected (verified from local hydro). In my design I am using a transfer switch and plan to connect a backup diesel generator to it.
My question is
(1)Does it matter if generator is star connected?
(2)Other new loads would include a pump, few heaters and a SPD. Does delta supply affect them?
(3)Do I need to contact hydro and ask them to upgrade the supply to a star? since generator is already purchased.
Any help in this regard is much appreciated. Please explain in detail since I am newbie.
-haiderster
haiderster is offline   Reply With Quote
Old 03-25-2018, 08:12 PM   #2
fertilizer distrubuter
Ultrafault's Avatar
Rewards Points: 554
what grounding configuration do you have on your delta supply?
Sent from my SM-N910P using Tapatalk
Ultrafault is offline   Reply With Quote
Old 03-25-2018, 08:27 PM   #3
Rewards Points: 3,560
How many leads does the generator have, reconfigure it if possible.
Old 03-25-2018, 08:56 PM   #4
Rewards Points: 21,898
What size the generator it is set up what ya plan to get it? ( if you know the model number if possible )
What voltage and conferation it is on the uility side it is now ? and please make a note which type of grounding on delta system that will make the differnce on that.
The reason why I ask due myself and couple other guys posted a very good point on the system.
there are few generators that can be reconnection on the spot. and genrally it cheaper to change connection on the generator than try to redo the uility side that will really eat up time and money.
Old 03-25-2018, 09:31 PM   #5
Rewards Points: 34
It is a Generac 60kW SD060 generator.
At the utility side it is 600V delta and I suspect it is ungrounded as I saw ground fault detection panel with 3 lights.
For generator leads ...I am not so sure if there are 12 or less...I have to ask the supplier.
-haiderster
Old 03-25-2018, 11:29 PM   #6
Rewards Points: 1,230
-haiderster
I believe its 12
bostonPedro is offline   Reply With Quote
Old 03-26-2018, 03:19 AM   #7
-haiderster
Originally Posted by bostonPedro View Post
I believe its 12
If it was wired for 480Y277 or 208Y120 then yes it is common to find 12 lead but for straight 600 volts I think it come in either 6 or 12 lead.
micromind likes this.
Old 03-26-2018, 10:33 AM   #8
Rewards Points: 3,432
If the 600 volt ∆ has 3 lights, it is not grounded. The 3 lights are a ground fault detector.
Provided that no ground fault is present (all 3 lights glow dimly), using a 347/600 star gen will work. The system doesn't care about voltage to ground, only phase to phase.
Since it sounds like a pretty simple system, before making the actual connection, de-energize the system and megger each phase to ensure that no ground faults exist. Also megger each load that is not directly connected to the main system.
Before you merger the system, you'll need to disconnect the ground fault lights.
Old 03-26-2018, 10:46 AM   #9
Bird dog's Avatar
Rewards Points: 582
For the NEC, wouldn't you also have to make the system a corner grounded delta? (The OP is from Canada--CEC would apply)
Old 03-26-2018, 11:53 AM   #10
Yes and no depending on the ground fault detection system is.
But if the exsting ground fault detector is working you can use it as it is., however if you plan to remove the ground fault detector system then you have to corner grounded it.
Old 03-26-2018, 12:53 PM   #11
Rewards Points: 2,302
Where I work we have a transfer switch that one source is wye and the other is delta. It works OK but when checking phasing there is always a larger than normal difference between similar phases. (NA-EA, NB-EB, NC-EC). Thank goodness we had a engineer with us when we were checking it out. He did some quick calculations and said our connections were OK.
From that experience I would label the transfer switch that one source is wye and the other source is delta and that there is a voltage difference between similar phases.
LC
Old 03-26-2018, 06:09 PM   #12
If there are no ground faults and the ground detector is working properly, you'll measure 347 from each phase to ground with a DMM. If the meter is low impedance, it'll affect the readings.
The 2 systems will operate the same even though one is high impedance grounded and the other is solidly grounded.
It's a bit different when a ground fault exists......the utility system will give an indication while the gen, being solidly grounded will trip a breaker, blow a fuse or blow something else up.
I believe it'd be code compliant if both the utility and the gens grounding systems are compliant since only one can supply the load at any given moment.
Old 03-26-2018, 08:50 PM   #13
BUT, Would an In-Phase Monitor on an ATS would function?
Old 03-26-2018, 10:08 PM   #14
As far as I know, the in-phase monitor in a transfer switch looks at phase to phase voltages. I've never seen one that uses phase to neutral.
That doesn't mean they don't exist, it's just that I've never seen one.
Old 03-26-2018, 10:12 PM   #15
Brian John .,, typically most Inphase monitor useally read phase to phase but few models do read phase to neutral ( depending on the spec and the customer request. )
Old 04-12-2018, 01:23 AM   #16
Rewards Points: 34
thanks everyone for the replies, ...just to summarize
- can I connect a Y generator to a transfer switch with a delta ungrounded supply connected to the other side (yes/No?) Please note I have VFD as the main load 1X25HP
-Any special consideration about the generator grounding and how would it effect during fault condition. Do I leave the neutral floating or bond it to frame. Do I provide a grounding electrode at the generator? I still need to bring the bonding conductor to the service panel to ground it there right?
-Can I use 4 pole transfer switch and treat generator as a separately derived system? Any problem with this configuration?
-Do I need to install ground fault indication lights at the main service breaker as per the code?