Dimmer outputs voltage when turned off - Electrician Talk - Professional Electrical Contractors Forum
Old 12-05-2012, 03:12 PM   #1
Rewards Points: 149
Default Dimmer outputs voltage when turned off
I have a weird "problem". I installed dimmers (decora diva), and when they're turned off I get a voltage of 57.7V to ground. The light does shut off completely. When I turn it on, the light turns on, aswell as dims. It functions properly, just get a voltage when its turned off. It scared a carpenter on the jobsite .
jclarmo is offline   Reply With Quote
Old 12-05-2012, 04:00 PM   #2
EBFD6's Avatar
Rewards Points: 1,014
What are you using to measure this voltage with?
A digital multi-meter or similar high impedance tester?
Use a solenoid tester or low impedance DMM and see what you get.
EBFD6 is offline   Reply With Quote
Old 12-05-2012, 04:02 PM   #3
EBFD6's Avatar
Also, when you say it scared a carpenter, how do you mean?
Did he get bit, or did he just see your readings on the meter?
Just trying to determine if this is real or phantom voltage.
Old 12-05-2012, 04:11 PM   #4
IBEW L.U. 1852
Rollie73's Avatar
Rewards Points: 286
Phantom voltage. Probably using a high impedance DMM.
Old 12-05-2012, 04:11 PM   #5
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
It's leakage current through the triacs. It's normal on solid state dimmers.
-John
The Following 2 Users Say Thank You to Big John For This Useful Post:
EBFD6 (12-05-2012), svh19044 (12-05-2012)
Old 12-05-2012, 04:41 PM   #6
Rewards Points: 564
You will not read it with a Wiggy or an old Simpson meter, guaranteed.
nolabama (12-05-2012)
Old 12-05-2012, 05:12 PM   #7
Chris Kennedy's Avatar
Rewards Points: 2,000
-John
OP states Diva. In the off position they should be air gap open, no leakage.
Old 12-05-2012, 06:01 PM   #8
Rewards Points: 149
I was using a digital multimeter. The carpenter had a proximity voltage tester.
Old 12-05-2012, 08:21 PM   #9
mbednarik's Avatar
Rewards Points: 1,126
A diva has a backlight in it. There is a small lamp in parallel with the switch. When the switch is off it uses the load to complete the circuit. This is whatyou are reading. To test this shade the switch and install a fixture at the ceiling. In the off position the switch will be illuminated. Remove all of the lamps in the fixture and the illumination goes away.
The Following User Says Thank You to mbednarik For This Useful Post:
jclarmo (12-06-2012)
AC and DC voltage coming from purp/gray 0-10v dimming outputs??? wfaren Lighting Design 5 08-13-2012 07:56 PM
I need low voltage ballast and dimmer nrp3 General Electrical Discussion 5 02-15-2012 05:33 PM
Magnetic low voltage potlights, incandescent dimmer Vintage Sounds General Electrical Discussion 14 06-18-2011 12:10 PM
Low voltage dimmer. jefft110 General Electrical Discussion 11 06-06-2011 11:08 PM
Found standard dimmer on low voltage transformer duckdodgers Lighting Design 4 12-28-2007 03:09 PM