Hi guys,
While buying a disconnect switch today for a 240vac system i saw on the specification that the max amp is like 20 while the same switch on 600vac is 60amp and was wondering why ? isn't like the total watt that matter only ?
My product was a Eaton disconnect Heavy-duty non fusible 3 poles amp rated 60amps
DH362UGK
Thanks
martindag is offline   Reply With Quote
Old 03-07-2016, 01:13 PM   #2
Rewards Points: 15,269
You're sure your spec doesn't call for a minimum of 20 amp? That's a normal, everyday disconnect switch. You're good to go. Disconnect switches aren't rated in watts.
If your spec is for a fused disconnect I could understand a maximum of 20 amps.
martindag (03-07-2016)
Old 03-07-2016, 01:58 PM   #3
martindag's Avatar
Rewards Points: 215
actualy the rating was for Max Horsepower for every volts, but still im trying to understand.
DH362UGK
Amp Rating: 60 amps
Max HP 3 phases
240vac = 20amps
480vac= 40amps
600vac= 60amps
Why at 240vac 3 phase this disconnect is limited to 20amps while on 600vac it can take 60amps ??
My unit is running on 208vac 20amp and was thinking of buying a normal one 30 amp rated but this part about the Horsepower and voltage confuse me.
Old 03-07-2016, 02:31 PM   #4
Rewards Points: 434
Originally Posted by martindag View Post
DH362UGK
Amp Rating: 60 amps
Max HP 3 phases
240vac = 20amps
480vac= 40amps
600vac= 60amps
You are reading this wrong. Look at the top of that column, those numbers are for the HP rating, not the amp rating.
Max HP 3 phases
240vac = 20HP
480vac= 40HP
600vac= 60HP
(BTW, my catalog shows the max HP at 480V as 50HP, not 40)
The Following 2 Users Say Thank You to JRaef For This Useful Post:
Bad Electrician (03-07-2016), martindag (03-07-2016)
Old 03-07-2016, 02:37 PM   #5
martindag's Avatar
Rewards Points: 215
ohhhh ok i get it now! , my bad i thought this was amp, thanks !
so to resume is the disconnect is rated 600vac 60amp MAX
no matter which voltage AC or Amp as long has it under the max rating it's fine (i saw DC is a little different)
and the HP is something else.
Old 03-07-2016, 02:44 PM   #6
Rewards Points: 434
Why at 240vac 3 phase this disconnect is limited to 20HP while on 600vac it can take 60HP ??
FIFY
Voltage goes down, current for the same HP goes up.
20HP @ 230V = 54 FLA
40HP @460V = 52 FLA
50HP @ 460V = 65 FLA
60HP at 575V = 62 FLA
Now how they can get away with a 60A switch being OK for running a motor with an FLA over 60A, or even AT 60A, I have no idea. The NEC clearly says a disconnect must be rated for 115% of the motor FLA.
But this is a NON-FUSED switch, meaning you cannot use it in a circuit that does not have another OCPD up stream. So maybe they are thinking they can use a "fudge factor" on their FLC rating because something else in the circuit will have to deal with overloads. So if they tested it with UL for 50HP @ 460V and it passes, then it's legit.
If you look at the fusible version of the same switch, the HP listings are lower by one size.
That's something you would have to ask them. Their data sheet doesn't mention 208V. 20HP @ 208V is 59.5A FLA so if you ask me, they ALREADY took that leap in listing it for motor FLAs over 60A, ergo I would think that the 20HP 208V would be fine. But an AHJ may want to see it in writing.
InPhase277 and Ultrafault like this.
The Following 3 Users Say Thank You to JRaef For This Useful Post:
Bad Electrician (03-07-2016), martindag (03-07-2016), Ultrafault (03-07-2016)
Old 03-07-2016, 03:20 PM   #7
martindag's Avatar
Rewards Points: 215
Thanks alot very informative !
Old 03-07-2016, 04:14 PM   #8
Bad Electrician's Avatar
Rewards Points: 4,969
You should see how big his head is to hold all that brain power. This is one wise individual.
We are lucky to have him as a member
I was born with a plastic spoon in my mouth.
The Following 3 Users Say Thank You to Bad Electrician For This Useful Post:
Rollie73 (03-07-2016), theJcK (03-07-2016)
Old 03-07-2016, 06:35 PM   #9
Rewards Points: 434
Almost everything I know I attained by making mistakes...
My favorite saying:
"Note to self; DON'T do that again!"
readydave8 and emtnut like this.
transfer switch for generator blacknpurplejs General Electrical Discussion 2 02-21-2016 09:17 PM
light switch near shower huntingflower Canadian Electrical Forum 4 02-17-2016 07:09 AM
Rangehood operation by remote switch katwalatapan Canadian Electrical Forum 4 01-29-2016 01:37 PM
115 VAC disconnect - should I break both hot & neutral? Paul Kraemer General Electrical Discussion 11 01-22-2016 10:21 PM
Oil Burner Switch Spark Master Residential Electrical Forum 8 01-10-2016 11:48 AM