Dist. Txf Short-Circuit : Stabilizing Winding - Electrician Talk - Professional Electrical Contractors Forum
Old 06-01-2014, 08:30 AM   #1
Unhappy Dist. Txf Short-Circuit : Stabilizing Winding
Hi All,
I am facing one critical matter where my energised (Vector group:ynYNd01) oil distribution transformer is down and basically the consultant and contractor disagreed with factory's view.
a) Factory made this transformer according to consultant spec, it was tested twice before energised.
b) Contractor used bear copper tape to earth it with our provided point at the bottom of the transformer and they also used another copper bear copper tape to earth the stabilizing winding point from the top of transformer (with both copper tape jointly touched on bottom and grounded. But the top stabilizing earth bar was touched with the side body of the transformer. The burn mark was showing at the point from stabilizing bar touched the body of txf.
c) We open up and lift the winding and saw some burn point from the bottom of the stabilizing winding which also burn the bottom structure steel of the transformer. Is already out of shape and touched the structure steel.
d) Factory engineer explained that it was the wrong earthing mathod that stabilizing shall use insulated copper to earth and shall not touch the body earth bar. It's already touched the body earth bar and stabilizing non-insulated touched the transformer top body created big flow of current force to cause the internal stabilizing winding to curve and touch the internal winding structual steel to spark....
e) Contractor forgot to install our provided Oil Thermometer (with contact), which is totally weird... I am totally shocked! and we dont know is this overheated.
Now, the consultant disagreed our view. Please help to look into this and advice us are we wrong in the factory explaination?
joytuw is offline   Reply With Quote
Old 06-01-2014, 09:58 AM   #2
RIP 1959-2015
Black Dog's Avatar
Rewards Points: 180
Originally Posted by joytuw View Post
Hi All,
Hello.
You should have an electrical engineer look over your transformer so you can get the right advice.
Welcome to the forum.
Old 06-01-2014, 10:03 AM   #3
Hi Black dog,
Did have a lot engineers around when we open up the winding... any view?
Old 06-01-2014, 10:13 AM   #4
fertilizer distrubuter
Ultrafault's Avatar
Rewards Points: 554
Big John will hopefully be around to sort this out for you.
Ultrafault is offline   Reply With Quote
The Following User Says Thank You to Ultrafault For This Useful Post:
joytuw (06-01-2014)
Old 06-01-2014, 11:19 AM   #5
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Tertiary windings are a bit out of my league, but what you're describing doesn't make sense to me.
If you're solidly grounding your delta, all your earthing points are common, you're putting the ground strap at the same potential as your tank and everything else. Unless you had absolutely massive zero sequence current flow there should be no reason for a difference in potential between the top of the grounding point and the bottom and no reason for arcing.
Try asking the same question here,
a lot of those guys are actually transformer designers and would be better equipped to give you an answer.
Always wear your gloves.
The Following 3 Users Say Thank You to Big John For This Useful Post:
Black Dog (06-01-2014), dspiffy (06-01-2014), joytuw (06-02-2014)
Tags
transformer
short circuit protection dynahd98 NEC Code Forum 3 12-15-2013 01:18 PM
definition: short circuit stonewhite General Electrical Discussion 7 11-23-2012 09:32 PM
Short Circuit Power FullSail General Electrical Discussion 0 10-16-2012 03:15 AM
SHORT CIRCUIT FOR XFMR 33/6.6 kv m sleem NEC Code Forum 1 06-25-2012 02:44 AM
Short Circuit Current Lithium General Electrical Discussion 1 06-30-2009 06:08 PM