Old 03-26-2013, 04:10 PM   #1
Curtlee's Avatar
Default Do I need a bonding bushing?
I have an outdoor 200amp 1 phase nema 3r meter, disconnect, then intersect panel. Which ones do I need to put bonding bushings? Also, I know the meter does not need to be grounded anymore, so if I take the grounding electrode straight in the bottom of disc, do I need attach it to the bonding bushing?
Curtlee is offline   Reply With Quote
Old 03-26-2013, 04:15 PM   #2
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
You can bring it to the bushing first and have it continuous. Or, you can use a jumper from the grounding bus to bushing. Either way meets the code minimum.
Replies based on NEC 2014
Old 03-26-2013, 04:56 PM   #3
220/221's Avatar
Rewards Points: 4,330
The metallic nipple that contains the unfused service conductors needs to be bonded.
That's my take on it anyway.
220/221 is online now   Reply With Quote
The Following 2 Users Say Thank You to 220/221 For This Useful Post:
BBQ (03-26-2013), Semi-Ret Electrician (03-26-2013)
Old 03-26-2013, 05:35 PM   #4
Rewards Points: 2,316
I don't know what a meter disconnect then intersect panel means.
The bonding bushings need to be used on the line side of the first disconnect means or in the meter. The grounding electrode conductor can be run to the first disconnect but you do still need to bond the bonding bushing with a bonding jumper sized to T. 250.66
I can't help it if I'm lucky
Old 03-26-2013, 05:46 PM   #5
Retired Account
Rewards Points: 14,650
If this is a meter/main combo incorporating an MBJ , there are no service conductors past it
If you wish to make the GEC onto a G-bushing,ask the poco, it may not be acceptable , as many require a solid (not metal casing of meter) bond bettween the two
Old 03-26-2013, 10:41 PM   #6
Does anyone know a code reference for this?
Kramsof is offline   Reply With Quote
Old 03-26-2013, 11:44 PM   #7
Rewards Points: 434
Do you only need a Bonding bushing when you have a concentric knockout?
JHFWIC is offline   Reply With Quote
Old 03-26-2013, 11:54 PM   #8
Semi-Ret Electrician's Avatar
Rewards Points: 486
(B) Method of Bonding at the Service. Bonding jumpers meeting the requirements of this article shall be used around impaired connections, such as reducing washers or oversized, concentric, or eccentric knockouts. Standard locknuts or bushings shall not be the only means for the bonding required by this section but shall be permitted to be installed to make a mechanical connection of the raceway(s).
Changed From 2008
250.92(B): Revised to clarify the limitation on the use of standard locknuts for bonding at service equipment.
Standard locknuts, sealing locknuts, and metal bushings are not acceptable as the sole means for bonding a raceway or cable to an enclosure on the line side of the service disconnecting means regardless of the type of or condition of the knockout.
Old 03-27-2013, 12:36 AM   #9
Cletis's Avatar
Rewards Points: 2,050
Dis not Dat
I'm shakin it boss..I'm shakin it
The Following User Says Thank You to Cletis For This Useful Post:
toolaholic (03-27-2013)
Old 03-27-2013, 01:06 AM   #10
Cletis's Avatar
These are ok. I have ton's of new/old ones for sale if interested
Old 03-27-2013, 01:17 AM   #11
Rewards Points: 990
Use PVC
cdslotz is offline   Reply With Quote
Old 03-27-2013, 01:39 AM   #12
220/221's Avatar
Service conductor nipples or concentric KO's over 250V to ground.
The Following User Says Thank You to 220/221 For This Useful Post:
BBQ (03-27-2013)
Old 03-27-2013, 02:46 AM   #13
Very Long Vacation
Rewards Points: 5,262
Yes, any side is ok, just make sure its bonded with a thick enough jumper. Think at least normal water bond size.
Old 03-27-2013, 11:01 AM   #14
toolaholic
Rewards Points: 250
Originally Posted by cletis View Post
these are ok. I have ton's of new/old ones for sale if interested
wrong finger !
toolaholic is offline   Reply With Quote
Plastic Bushing Use. Prometheus NEC Code Forum 21 10-23-2012 09:34 PM
Grounding Bushing 360max NEC Code Forum 10 06-25-2012 04:23 AM
Insulating Bushing 300.4(F) swimmer NEC Code Forum 10 01-02-2012 05:23 PM
Bonding lock nut vs grounding bushing nitro71 NEC Code Forum 1 04-25-2011 05:34 PM
bonding bushing flip250r General Electrical Discussion 11 03-30-2011 03:25 PM