Which do you trust more? (Grounding vs. GFCI) - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Old 02-10-2015, 09:38 PM   #21
MTW
Rewards Points: 10,216
Originally Posted by captkirk View Post
Gfci protect people grounding protects equipmemt.
Equipment grounding most certainly protects people.
The Following User Says Thank You to MTW For This Useful Post:
guest (02-10-2015)
Old 02-11-2015, 12:13 AM   #22
Rewards Points: 1,510
Old 02-11-2015, 12:27 AM   #23
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Gfci protection doesn't hurt but i don't believe it should be mandatory for everything. I added two garage door opener outlets last night., they were 11' high. I loaded them from the sprinkler gfci outlet. But really, what safety is gained here by having the door openers protected if they are grounded?
Old 02-11-2015, 04:00 AM   #24
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,354
Originally Posted by bobelectric View Post
Now that's working hot ! No Thanks.
The Following User Says Thank You to TOOL_5150 For This Useful Post:
The_kid (02-11-2015)
Old 02-11-2015, 08:06 AM   #25
Bababoee
captkirk's Avatar
Rewards Points: 2,030
Someone can easily get electrocuted by a fault that doesn't trip a breaker. You could have voltage going to ground and not trip a breaker.
I just had ceu class last week and the instructor asked a similar question. Although his argument was better than mine.
The breaker protects the wire the equipment ground protects the equipment and gfci protects people. Not saying that the equipment ground doesn't protect people in clearing any faults but it is very possible to still get electrocuted with it. And it goes back to your question, which do you trust more..?
Full time Bovine Scatologist.
Old 02-11-2015, 10:14 AM   #26
Rewards Points: 1,464
Equipment ground.
Old 02-11-2015, 10:35 AM   #27
Bababoee
captkirk's Avatar
If equipment ground is for life safety then why do we install GFCI s?
Old 02-11-2015, 01:35 PM   #28
Very Long Vacation
Rewards Points: 5,262
Nope, it protects people and property. A GFCI enhances an EGC or where it may fail to protect such as an appliance in water.
Old 02-11-2015, 01:40 PM   #29
Rewards Points: 119
Originally Posted by hardworkingstiff View Post
I think you missed my point. The only reason you need a GFCI is because you have a grounded system. Without a grounded system, the shock hazard drops tremendously. I believe that's the main reason they use isolated ground systems in operating rooms, to significantly reduce shock hazards.
If you don't have a grounded system, you really don't need a GFCI. It's not a choice of A over B, it's you need B because of A.
I believe ungrounded systems in operating rooms were mainly established to eliminate the chance of a spark of a ground fault causing an explosion. This used to be a huge problem long long ago. This of course doesn't help if there were a line-line fault, but according to data, ground faults are much more common than line-line faults.
Equipment grounds ensure the breaker will trip on ground fault assuming you have an effective ground fault current path back to the breaker. It's also going to take an average circuit breaker several cycles to trip that breaker, meaning that the full fault current is flowing on that circuit for maybe 50ms.
If I was part of that circuit, my body is going to experience all of that current. I don't want my body to ever be a ground fault path, but if it was, I would prefer that a GFCI be there to trip at 4-6mA rather than the circuit breaker letting through 50-100A best case scenario.
lannjenks is offline   Reply With Quote
The Following User Says Thank You to lannjenks For This Useful Post:
hardworkingstiff (02-11-2015)
Old 02-11-2015, 01:47 PM   #30
Very Long Vacation
3 main NEC reasons:
1. An EGC can break open and fail to protect. Thus, if an appliance frame became live it would sense a leakage going through a person or something else and disconnect the power.
2. Submerging something in water (most of the time anyway*). Water will not conduct enough power to trip a breaker, but can conduct power to a person. Such a scenario is a drill in a sink or bucket of water and a person reaches to in to grab it while feet on concrete or conductive surface.
* IF one had a fully insulated pool from ground and a 2 wire toaster was dropped in it with people swimming the GFCI would not trip. Ground your pool water folks
3. A damaged extension cord with exposed conductors. Should it end up in a puddle of water or a person was to grab the frayed cord the GFCI will most likely trip.
Reasons at the branch circuit level (though not required by the NEC directly)
1. Detecting dangerous wiring errors or faults. Any fault to ground such as romex pierced by a nail will trip differential (GFCI) protection, which is why 80% of AFCI have it but just set to a higher degree such as 30 or 50ma instead of 5.
Old 02-11-2015, 01:55 PM   #31
Bababoee
captkirk's Avatar
I've had several calls over the years in which people said they were getting shocked from certain appliances in their homes. Two things they all had in common were they all had egc and no gfci.
Old 02-11-2015, 02:00 PM   #32
Bababoee
captkirk's Avatar
And like I said EGC is not life safety so what are we debating now
Old 02-11-2015, 02:03 PM   #33
Very Long Vacation
What was did the issue end up being?
Old 02-11-2015, 02:19 PM   #34
[quote=meadow;1653137]3 main NEC reasons:
Debatable.
Old 02-11-2015, 02:29 PM   #35
Bababoee
captkirk's Avatar
One of them was a detached garage feeder with 2 cloth type conductors (rigid conduit as egc) feeding the outlets and lights in the garage the guy had a fridge that had current on the shell. Over the years the pipe corroded and the conductors fused to the pipe and was leaking current into the egc. If there was a gfci in the outlet it would have undoubtedly tripped but it was just a regular outlet.
The other one was much more serious. A metal pipe in a parking garage had corroded and the conductors leaked 277 volts into the ground. Didn't trip the breaker but when the maintenance guy went to change lamps he got the **** knocked out of him.
And I had an old window ac that had current on the shell. Defective unit and the breaker didn't trip.
I do a lot of service work so Ive seen a lot of **** over the years.
Old 02-11-2015, 02:32 PM   #36
Very Long Vacation
If the conduit was after a GFCI it would have.
The down side to breakers is that they fail to catch high resistance faults. What few will say is that short circuits will don't just happen, usually they start as a high resistance fault and progress until the leakage current trips the breaker.
Old 02-11-2015, 02:32 PM   #37
Very Long Vacation
[quote=bobelectric;1653297]
3 main NEC reasons:
Debatable.
The reason or the GFCI will trip?
Old 02-12-2015, 10:04 PM   #38
Rewards Points: 189
I dont put a lot of faith in GFCI's. I was doing a remodel on a pool that had old abandoned conduits stubbed up for pole lights and outlets on columns around the pool. In one column they had 3 3/4" pvc stubbed up. They all had duct tape which I figured a co worker had done previously to protect against debris during demo. I stuck my razor knife in one to cut the tape off the conduit and took a ride. Later found out that it was on a GFCI receptacle wired on the load side that was feeding a well pump someone had hacked into to add a receptacle on the column. All other circuits where in a dedicated sub panel for the pool that had been shut off. Ive had first hand experience of a GFCI failing to do its job.
yamatitan is offline   Reply With Quote
Old 02-12-2015, 11:06 PM   #39
Bababoee
captkirk's Avatar
If I was in a pool area I would sure as hell hope there was a gfci on it. Egc wouldn't do anything..
Old 02-12-2015, 11:10 PM   #40
Very Long Vacation
An EGC would help trip the GFCI if the pool was ungrounded.
Trust your gut. 99cents Business, Marketing, and Sales 10 06-24-2014 10:00 AM
Trust your intuition... 99cents Business, Marketing, and Sales 6 07-03-2013 06:43 PM
Do you always trust your instincts? Magnettica General Electrical Discussion 38 07-08-2011 10:29 PM
Never trust a contractor Bob Badger Off Topic (Non Trade) 3 08-10-2010 02:49 PM