Which do you trust more? (Grounding vs. GFCI) - Page 3 - Electrician Talk - Professional Electrical Contractors Forum
Old 02-12-2015, 10:15 PM   #41
MTW
Rewards Points: 677
Originally Posted by captkirk View Post
And like I said EGC is not life safety so what are we debating now
That simply is not true. The NEC (and common sense) mandates all metallic non-current carrying parts and paths be bonded by a low impedance path back to the source. The reason for that is so those parts do not become energized and therefore pose a risk to human life. A short circuit or ground fault to a metallic path will immediately open the OCPD, removing the hazard.
The Following 3 Users Say Thank You to MTW For This Useful Post:
dronai (02-14-2015), guest (02-13-2015), meadow (02-12-2015)
Old 02-13-2015, 09:55 PM   #42
Rewards Points: 211
If I was in a pool area I would sure as hell hope there was a gfci on it. Egc wouldn't do anything..
I was hit because I stuck a metal razor blade in it not because of water being present. But I agree it was done right being on the GFCI its just the GFCI failed.
yamatitan is offline   Reply With Quote
Old 02-13-2015, 10:20 PM   #43
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
In a growing plastic nation more and more items are becoming plastic and being manufactured with 2 wire supply cords. Grounding will do nothing to aid in shock intervention. As to grounding metal framed appliances, i think gfci protection is an absolute waste of money.
The Following User Says Thank You to Shockdoc For This Useful Post:
MTW (02-13-2015)
Old 02-13-2015, 10:35 PM   #44
Very Long Vacation
Rewards Points: 5,262
We should go Japanese, everything they have (well, almost everything) is double insulated and 2 prong. 100 volts to being safer.
MTW (02-13-2015)
Old 02-13-2015, 10:44 PM   #45
MTW
Rewards Points: 677
And no AFCI's either.
Old 02-14-2015, 12:11 AM   #46
Very Long Vacation
Old 02-14-2015, 04:42 AM   #47
Rewards Points: 1,464
And their Fried Rice is the best!
Old 02-14-2015, 04:56 AM   #48
You maybe felt a shock, but it may have been below 4-6 ma. required to trip a gfi. Did you go and push the test button after to verify a faulty device?
The Following User Says Thank You to bobelectric For This Useful Post:
hardworkingstiff (02-14-2015)
Old 02-14-2015, 10:39 AM   #49
Rewards Points: 206
I agree with this statement 100%. However, just to add to the confusion, I have a textbook that states explicitly grounding/bonding are for equipment protection and gfci's are for personnel protection.
newbi is offline   Reply With Quote
Old 02-14-2015, 10:46 AM   #50
Rewards Points: 14,714
Yes it will, but if you are in series with that for any reason, the breaker will not open and you will most likely die. That's what the GFCI is there to prevent.
The premise of the OP is inaccurate IMO because it's not a question of either/or.
Old 02-14-2015, 11:17 AM   #51
Bababoee
captkirk's Avatar
Rewards Points: 2,030
Equipment ground is to facilitate the opening of a breaker in the event of a short. It's very possible for a person to come between the short and the breaker. As it is very possible for a person to come between a fault and not tripping the breaker. I'm not sure what you guys don't get about that.? And I'm not saying that equipment grounds aren't importatnt. But if I was in a pool for instance I would hope it's on a gfci. As if it was just grounded and bonded you could still get k8lled. Oi yeh....we're is brian when you need him
Full time Bovine Scatologist.
Old 02-14-2015, 11:17 AM   #52
MTW
Rewards Points: 677
That textbook is wrong then.
Old 02-14-2015, 11:19 AM   #53
MTW
Rewards Points: 677
Many circuits do not contain GFCI protection, so I have no idea how this applies.
Yeah, whatever.
Old 02-14-2015, 11:20 AM   #54
MTW
Rewards Points: 677
Some situations call for an added level of protection, so the NEC requires GFCI's.
Yeah, because only Brian knows everything about electricity.
Old 02-14-2015, 11:24 AM   #55
Bababoee
captkirk's Avatar
I trust brian 1000 times more than you just like gfci in a pool over "EQUIPMENT" ground...lmao
Old 02-14-2015, 11:27 AM   #56
MTW
Rewards Points: 677
Old 02-14-2015, 12:20 PM   #57
Who is Brain?
Old 02-14-2015, 12:54 PM   #58
Very Long Vacation
I have a text book that say the ground rod is for to trip a breaker. Along with other questionable assumptions. Older text books were guilty of this.
The Following 2 Users Say Thank You to meadow For This Useful Post:
guest (02-14-2015), newbi (02-14-2015)
Old 02-14-2015, 01:00 PM   #59
Very Long Vacation
Please tell me how a person can come between the short and the breaker
Unless you are talking about a person opening up an appliance and putting there hand on a hot and the other on the frame... in that case you would be at fault for serving a live appliance, where not even a GFCI may protect you such as if you were to grab live and neutral at the same time.
Now if talking about dropping something into a pool, an EGC with a GFCI would 100% guarantee clearing where a GFCI only may not if the pool water was ungrounded.
GFCIs do not sense water. They sense an imbalance.
MTW (02-14-2015)
Old 02-14-2015, 01:16 PM   #60
Rewards Points: 206
Cool, my book is only a couple years old. I find it more beneficial to learn here on ET.
Trust your gut. 99cents Business, Marketing, and Sales 10 06-24-2014 09:00 AM
Trust your intuition... 99cents Business, Marketing, and Sales 6 07-03-2013 05:43 PM
Do you always trust your instincts? Magnettica General Electrical Discussion 38 07-08-2011 09:29 PM
Never trust a contractor Bob Badger Off Topic (Non Trade) 3 08-10-2010 01:49 PM
losing trust 3phase General Electrical Discussion 14 04-24-2008 08:42 PM