Dual Voltage Generator KVA & Amperage question - Electrician Talk - Professional Electrical Contractors Forum
Like Tree6Likes
  • 1 Post By B-Nabs
  • 1 Post By micromind
  • 1 Post By robg3987
  • 1 Post By Bird dog
  • 2 Post By Bird dog
Old 03-26-2019, 08:07 PM   #1
Rewards Points: 14
Default Dual Voltage Generator KVA & Amperage question
Hello,
I have a 480V/240V 125Kva 3 phase generator that I have a question about the available Kva's and subsequent amperage available at the 2 available voltages.
The stator windings consist of 6 sets ( 12 leads) connected in a series Y configuration. So 2 windings in series for A phase, 2 for B, 2 for C.
Each phase has a connection available mid point for the 240 V selection.
The generator is rated at 125 Kva @ 480V.
I am trying to verify the available max Kva and amperage for each voltage (480 & 240) .
By my calculations, @ 480V, I should have approx 150A.
However (this is where I might be unclear) at the 240V (mid point of the 2 series windings),, I should still be getting 150A through the winds (as they are in series, but now only 240 V, so now therefore don't I have only 62.5 Kva ( 150 A @ 240V) ???
Its not what I observed when I load bank tested it.
robg3987 is offline   Reply With Quote
Old 03-26-2019, 08:34 PM   #2
Bird dog's Avatar
Rewards Points: 942
What does the nameplate say?
Old 03-26-2019, 08:47 PM   #3
Watt Pusher
B-Nabs's Avatar
Rewards Points: 474
Wouldn't you parallel the windings for 240V operation? So you'd still have 150A per winding, but that would result in 300A per phase, so still the same KVA.
Old 03-26-2019, 09:22 PM   #4
Rewards Points: 14
exactly what I posted ( 125 Kva at 480 Volts)
Old 03-26-2019, 09:32 PM   #5
Rewards Points: 14
yes,, that is what I had expected to do, but we were told by the supplier that it would achieve the same KVa output in that configuration (non-parralled configuration).
I was wondering if I had something wrong in my theoretical predictions.
The other possibility is that the supplier is full of BS and running it like that will ultimately lead to burning out the winding.
I'm just making sure I haven't misunderstood the theory and my calculations
Old 03-27-2019, 01:09 AM   #6
Rewards Points: 3,118
Winding heat is dependent on amps; no part of any winding can be loaded beyond its amp rating.
KVA is amps and volts.
In your case, if you get power from the 240 point only, the gen becomes 62.5 KVA.
You are correct in that each winding can produce 150 amps, at 480 this will be 125 KVA. At 240, it'll be 62.5 KVA.
You can also use any combination of 240 and 480 loads provided no part of any winding produces more than 150 amps.
Be careful with the 240 here, it's not 120/240, it's 138/240 because it's connected Y.
Old 03-27-2019, 06:45 AM   #7
Rewards Points: 1,254
If that's the case I'd picture something like this in the connections (in the low voltage configuration, would 1 be bonded to 4-5-6?)
https://www.electrical-contractor.net/theory/3ym04.gif
Southeast Power (03-27-2019)
Old 03-27-2019, 07:11 AM   #8
Southeast Power's Avatar
Rewards Points: 8,702
Im concerned with the OP asking about 240 volts.
OP, are you concerned with the KW rating if the 3 phase generator is used single phase 120/240?
Old 03-27-2019, 09:18 AM   #9
Rewards Points: 14
Yes! thanks for the vindication on what I was trying to explain to my management & supplier.
I also didn't mention the 138/240 V result in my post, but I'm very happy that you noticed that outcome because that is exactly what we observed in our field test. In this generator configuration we have also attempted to provide some convenience receptacles (120V GFCI and 240 V) but then realized the 138V output !!
So again,, thank you for following this through to the same conclusion that I arrived at. That makes me feel relieved that I wasn't going nuts when they told me it could be done!
Old 03-27-2019, 12:58 PM   #10
Bird dog's Avatar
Rewards Points: 942
So, if you have a 480v genset, all you need is a 480v delta/208-120v xfmr?
https://www.platt.com/platt-electric...SubCatID=10980
glen1971 likes this.
Old 03-27-2019, 01:23 PM   #11
Rewards Points: 14
Yup,, that is what I had suggested also to solve the additional problem. But they don't seem to be interested nor heeding the technical advice provided. The main output would have to be turned down to around 415 volts to ensure there was 120 v available to the convenience receptacles. At 414 volts it becomes pretty much useless to any other motor loads connected.
So yes I agree the ideal solution was proposed as a xfr to handle the secondary loads at proper voltage.
The point I am at now, is to go to back to the actual manufacturer (Cummins) and get them to tell me what these windings are rated at. Then I can state my findings on the rated capacities and the configuration, if they want to exceed the ratings,,, then I can't do anything more.
Old 03-27-2019, 01:46 PM   #12
Bird dog's Avatar
Rewards Points: 942
Present to Cummins your whole problem. They may say we do not recommend that, you can't do that or give you an acceptable option (do this or buy this kit).
Cummins may laugh at you & say buy a genset wth a 208/120v output.
glen1971 and Kevin_Essiambre like this.
Old 03-27-2019, 03:09 PM   #13
Rewards Points: 14
Default Dual Voltage Generator KsuggestVA & Amperage question
Lol,,,good point Bird Dog!
I appreciate all the input and suggestions.
Just waiting now for a call back from Cummins....
Old 03-27-2019, 10:39 PM   #14
Rewards Points: 14
well, we heard back from the rep and they agreed with my assessment of reduced Kva at 240V (62.5 Kva).
All they would commit to in am email statement was ",,, with mid point tap of the series Y winding configuration the Kva rating would have to be de-rated from the 480V selection,,".
Now at least I have corroborated technical feedback, in addition to all of your feedback to support me.
Now if they want to override the ratings and damage it,, my conscious is clear that I did my due diligence.
Thank you all for your stellar input and advise.
Cheers!
Rob
VA Low Voltage Question fayt Commercial Electrical Forum 9 04-11-2018 11:08 PM
Voltage Fluctuation Mr.Awesome PLCs, VFDs, Motors and Controls 45 03-20-2017 01:40 AM
Amperage question CuriousGeorge87 General Electrical Discussion 11 01-21-2017 12:22 AM
Chasing that voltage ~48~ Residential Electrical Forum 15 07-28-2016 01:26 AM
Cec voltage drop question Rick9999 General Electrical Discussion 7 05-15-2016 04:35 PM